View Full Version : Roscal does kits, hi and lo flow too
BillA
12-15-2004, 03:01 PM
in French http://www.cooling-masters.com/news.php?id=75
in googlese http://translate.google.com/translate?u=http%3A%2F%2Fwww.cooling-masters.com%2Fnews.php%3Fid%3D75&langpair=fr%7Cen&hl=en&ie=UTF-8&oe=UTF-8&prev=%2Flanguage_tools
would that all were so through, very nice job
nikhsub1
12-15-2004, 03:28 PM
Ooooh, do I see some Swiftech bling? Me likes!
9mmCensor
12-15-2004, 03:38 PM
black is beautiful :)
me wants black block and silver (or black as #2 choice) hold down plates.
lolito_fr
12-15-2004, 03:48 PM
yeah, MCW looks quite sexy in red/black :D
...a top-notch article for a quality kit.
HammerSandwich
12-16-2004, 09:55 AM
Wow! Despite the Googlese, that's the best WC article I've seen.
Interesting/curious. that MCR120 radiator's temperatures translate(according to BI Pros data (http://forums.procooling.com/vbb/showpost.php?p=131498&postcount=23) ) heat dumps of ~ 47w and ~ 88w for a system-modeler's heat inputs of ~83w(75+8) and ~123w(115+8).
57% and 72% respectively.
BillA
12-18-2004, 06:24 PM
we gonna hijack another thread ?
where should we put this BI stuff ?
It is your thread and Roscal is not averse to science.
BillA
12-18-2004, 07:19 PM
no 'claim' to thread,
my only concern is that everything becomes so scrambled
Les
my whole problem with the modeling bit, is one to conclude that the measured watts are hugely low ? or temperature compression ? some of both ?
- or that the model is disconnected ?
why I test
a disclaimer, conditions
#1 all data is preliminary, the procedure is still being defined (Roscal note, those curves will be re-stated)
#2 consider this rad data as a unique data set;
in terms of control, accuracy and repeatability it is considerably better than the 2 previous efforts
#3 rads connected in a uniform manner, laid flat, fan(s) pushing w/grille guard(s)
#4 fan intake positioned 3" below the horizontal discharge of the environmental chamber's air conditioning
#5 fan discharge isolated from intake with a 4" horizontal baffle at the rad discharge face (the rad body is exposed to the 'cool' intake air)
readers interested in rad test data need to read and consider this post
http://forums.procooling.com/vbb/showthread.php?t=11039
here is one so curious that I ran some addl points to confirm
http://www.thermal-management-testing.com/80diss.gif
this curve will shift when I re-do, the tail will rise, but even so
Etacovda
12-18-2004, 08:23 PM
Black + red a likely combination for the future, or is the blue going to be kept (ie, black overseas models...)
edit - read about the 'designer' series
lolito_fr
12-19-2004, 05:17 AM
Interesting/curious. that MCR120 radiator's temperatures translate(according to BI Pros data (http://forums.procooling.com/vbb/showpost.php?p=131498&postcount=23) ) heat dumps of ~ 47w and ~ 88w for a system-modeler's heat inputs of ~83w(75+8) and ~123w(115+8).
57% and 72% respectively.
Those pesky secondary losses....
...
readers interested in rad test data need to read and consider this post
http://forums.procooling.com/vbb/showthread.php?t=11039
here is one so curious that I ran some addl points to confirm
http://www.thermal-management-testing.com/80diss.gif
this curve will shift when I re-do, the tail will rise, but even so
The tail is a puzzle; if not measurement error(re. Incoherent) or frictional heat(would require dP=18+ m(H2O))
Has driven me to look(again) at flow-boiling ( "the bends", cavitation)
Only got as far as :
"For the dissolution of oxygen in water, O2(g) <--> O2(aq), the enthalpy change under standard conditions is (-11.7)-0 = -11.7 kJ/mole" (http://dwb.unl.edu/Teacher/NSF/C09/C09Links/www.chem.ualberta.ca/courses/plambeck/p101/p01182.htm)
O2(aq) possibly drops 0.83 mg/l per m(H2O) dP across radiator when no temperature change temperature.(Calculator (http://www.thermidaire.on.ca/do.html))
Looks a tortuous road, to retread after 45 years, to yield nothing .
Looks more like pHaestus's territory.
HammerSandwich
12-19-2004, 08:48 AM
Looks clear that the higher flow doesn't let the water spend enough time in the rad. <ducks>
BillA
12-19-2004, 10:46 AM
Looks clear that the higher flow doesn't let the water spend enough time in the rad. <ducks>
wheeeeee . . . .
lol
The tail is a puzzle; if not .......or frictional heat(would require dP=18+ m(H2O))...
http://www.jr001b4751.pwp.blueyonder.co.uk/roscal1.jpghttp://www.jr001b4751.pwp.blueyonder.co.uk/roscal2.jpg
BillA
12-19-2004, 12:17 PM
methinks you are illustrating my reservations re the connector dP being lumped into the rad's
much is experimental, the new setup has eliminated some of the tailoff
- enough to consider all such part of an experimental issue ?
no, not so confident as that
a comprehensive set of the BI rads' performance will clarify some things, still unfolding as I am redoing 10 days of work (rad testing is such fun)
Your "data presentation" includes the connector contribution.
So has be used or manipulated out.
- enough to consider all such part of an experimental issue ?
Yes.
BillA
12-19-2004, 12:41 PM
wrt the rad dP, yes; often for both sizes
would prefer them out but the result is an abstraction
we shall see
The tail is a puzzle; if not measurement error(re. Incoherent) or frictional heat(would require dP=18+ m(H2O))
Has driven me to look(again) at flow-boiling ( "the bends", cavitation)
Looks a tortuous road ..... to yield nothing .
Possibly larger than expected :
Just considering Nitrogen(" the bends"component) would tempt me to change the dP correction from ~ 0.16(LPM x m(H2O)) to ~ 0.17(LPM x m(H2O))
Envisage water-vapour(cavitation component) to be larger.
Oh woe.
Maybe "Thermal Effectiveness" should be used to describe a radiators performance.
Is suggested inDecember's CoolingZone (http://www.coolingzone.com/Guest/News/NL_DEC_2004/CZ/Effectiveness.html), by Zahed Sheikh, as "A Useful Measure of Cold Plate Performance".
This measure includes both the "Heat Dissipated"(my Wa) and the important(to my mind) coolant's temperature drop across the radiator(my (Twi -Two))
BillA
12-21-2004, 07:10 PM
I think I agree, let me dig a bit
Incoherent
01-03-2005, 06:01 AM
Maybe "Thermal Effectiveness" should be used to describe a radiators performance.
Is suggested inDecember's CoolingZone (http://www.coolingzone.com/Guest/News/NL_DEC_2004/CZ/Effectiveness.html), by Zahed Sheikh, as "A Useful Measure of Cold Plate Performance".
Les, this article is bugging the shit out of me. I am probably misinterpreting it, ...perhaps I need to drop the assumption that "more effective = better performance"... thats annoying.
Will think a bit.
BillA
01-03-2005, 09:22 AM
a mix-up in terms I believe
the article describes (as I recall it) systems effectiveness, and then tries to draw conclusions wrt components
(and what Les is suggesting - I'm on the fence aka rebuilding a part of the WCing test circuit)
- the pump heat/head loss thing recast slightly
Link posted to indicate that authoritative(?) thermal engineers were noting the importance of the coolant's exit temperatures.
Think, I still prefer a device to be characterized by (C/W)inlets or (C/W)wo-ai at given flow-rates(Q)
Where
C= dTwi -ai or C= dTwo-ai (Not LMTD or part LMTD)
W is the change in SENSIBLE Heat of the coolant= Bill's "Heat Dissipated" = My "Ww" (http://forums.procooling.com/vbb/showpost.php?p=131576&postcount=36) = dT(wi-wo)*Cw*Q
Think "Sensible Heat"of coolant maybe prefereable to Energy of coolant.
BillA
01-03-2005, 10:10 AM
indeed, sensible heat is what is being measured
my problems were caused by temp compression by excessive thermal capitance in the loop, specifically at the crosses
- replaced all with some (fabricated) plastic bits, and all is well again
(undocumented was the fact that I'd used plastic crosses when doing these tests, which I still have; bleh 5 days wasted in hunting the problem)
yes Les, "C" is now taken inlet to inlet (by me anyway)
BUT I have found that a single temp at the fan inlet is rather inadaquate, the error can easily exceed ±0.5°C
- of course this depends on the desired precision
Incoherent
01-03-2005, 12:50 PM
Link posted to indicate that authoritative(?) thermal engineers were noting the importance of the coolant's exit temperatures.
Think, I still prefer a device to be characterized by (C/W)inlets or (C/W)wo-ai at given flow-rates(Q)
I totally agree. The Win-Ain is intuitive, the Wout-Ain gives an instant feel for effectiveness.
The article is indeed about System level design decisions I guess. However I am having trouble figuring out which he is referring to with "Effectiveness", system or "cold plate".
When the effectiveness is large, the coolant entering the radiator will be hotter. The difference between Tout and Tamb will likewise be larger, meaning that more heat can be dissipated from the radiator to ambient. The system consequence is that the radiator be made smaller and cheaper, with lower pressure drop and lower fan noise.
I have trouble reading this and and not reacting... "! how many times does it have to be said, the temperature rise across the waterblock has nothing to do with waterblock effectiveness, efficiency, thermal resistance whatever, but ALL to do with the power being dissipated, the flowrate and the coolant fluid type...
Also, as the effectiveness increases, the temperature rise of the coolant increases. According to equation (2), a smaller flow rate is then needed for the given amount of heat absorption, Qactual. This will reduce the pressure drop in the entire loop.
With lower mass flow rates and pressure drop, a smaller, cheaper and more reliable pump may be used.
Edit: Apologies. My 2 year old posted this, which was an initial layout of my thoughts, not intended to be posted. Will leave it for now, is not too insulting I hope.
lolito_fr
01-03-2005, 01:38 PM
IMO, the author makes a bad start when applying Equation (1) to a waterblock:
Eps=Qactual/Qmax
...
the die is not a constant temperature source!!
Perhaps someone should email this guy!?
Equation (1) is OK.
"Efficiency = Qactual/Qmax" is a definition.
Subsequent logic, as far Equation(6), seems correct.
However that is as far as I go.
Incoherent
01-04-2005, 02:54 AM
the die is not a constant temperature source!!
It could be considered a constant power source.
I am still very puzzled. There is nothing wrong with the logic, the problem is the point.
I think he means that the components of the system should be selected to not exceed a given die temperature, but be spec'ed as cheap and reliable as possible whilst conforming to this criterion. A high performance low flow block helps achieve this at higher water temperatures - meaning a smaller rad, lower flow pump, quieter fan.
I don't like the way it is presented though. When the effectiveness is large, the coolant entering the radiator will be hotter... and Also, as the effectiveness increases, the temperature rise of the coolant increases. leaves one with the suspicion that either he doesn't know what he is talking about or the application doesn't apply to us. The "Effectiveness" is increasing because Q actual is increasing within the framework of constants (i.e. constant die temp) he has selected. Reality is not like that unless the waterblock was trying to cool a large mass.
It is possible that the reader's an idiot.
lolito_fr
01-04-2005, 05:34 AM
It could be considered a constant power source
Assuming that, isn't Qactual=Qmax? (neglecting secondary losses, as usual)
In which case, based on (1), (2) and (3) we end up with Tout=Tdie ???
(must admit to not having spent much time on the article, so perhaps this reader is also an idiot)
BillA
01-04-2005, 09:13 AM
I spoke with the author several years ago trying to get him to accept one of my (puerile) articles
he is not a WCing guy at all, but like most others in Thermal Mgmt have the assumption that they can cool anything
- and the results of this assumption can be seen in old Lytron products, the Hydrocool by Delphi, and others
but they can get it right also, Delphi in the G5 for Apple - the biggest WCing app to date
the only thing I extracted was that the author was arguing for downsizing the pump with adequate system performance,
not too useful for Swiftech in pursuit of performance per se (for the DIY market)
Incoherent
01-04-2005, 09:21 AM
Assuming that, isn't Qactual=Qmax? (neglecting secondary losses, as usual)
In which case, based on (1), (2) and (3) we end up with Tout=Tdie ???
(must admit to not having spent much time on the article, so perhaps this reader is also an idiot)
I think you are right if you take that approach. Meaning that Effectiveness is always 1.00!?
Unless die temp is fixed (a thermally superconducting block of infinite mass) and thus able to deliver whatever Q is defined by R and Tin...
It's annoying me.
The conclusion I draw is that Waterblocks are more effective at lower flowrates, despite the fact that their thermal resistance is better at higher flowrates... !!?
A high effectiveness cold plate has a high liquid exit temperature and requires less flow rate for the same required thermal resistance. As a result, the liquid pumping power is reduced and the size of the radiator can be much smaller.)
Perhaps sums up his approach. I believe exit temperature is a consequence of flowrate and heat transferred, not cold plate effectiveness. But to maintain a given die temperature, the flowrate can be reduced with a lower resistance waterblock.
And one thing he is spot on with, is that the radiator can be much smaller with this approach. That might actually be the point...
<a sudden glint of understanding>
...I'll have to think some more, this might actually be a rather large point....
BillA
01-04-2005, 09:30 AM
in his system the pump is the only heat source that is a variable, so downsizing it then permits downsizing the rad
this is useful info for larger sized systems (for one with little experience), but in WCing 'reasonable' pump choices do already consider the pump's heat input as a part of the selection process
- in any case it is moot for DIYs as they do not do WCing systems design, though they may bumble about at it
Incoherent
01-04-2005, 09:44 AM
in his system the pump is the only heat source that is a variable, so downsizing it then permits downsizing the rad
Am thinking more in terms of the "required radiator C/W" to maintain a given water temp at high versus low flowrates. A quick calculation surprised me, need to recheck my numbers.
I am definitely bumbling. :)
BillA
01-04-2005, 09:52 AM
"required radiator C/W"
that's gonna be shooting in the dark for sure as the rad C/W varies with both sides' flow rates, heat load, temp differential and I've no doubt missed several
this is why the 'real world' approach is to identify the rad as a limiting factor
-> then oversize the hell out of it (the DIY approach as the LOWEST CPU temp is the goal)
other systems can be designed to provide rather specific performance under defined conditions, in which case the rad and/or wb performance (size, cost) will be downsized to achieve a cost effective solution that is sufficient for the intended task
pHaestus
01-04-2005, 11:07 AM
Exactly
Very few DIYers are interested in IC temperatures of 10% less than maximum mfgr specified operating temp, but if you are optimizing a system commercially then that makes perfect sense. Cooler temps really are for bragging rights, and lab/industrial equipment rarely puts much premium on that (other than brand name of course).
lolito_fr
01-04-2005, 12:36 PM
Think I have clarified my mis-understanding:
Qmax is the theoretical limit, which would apply if Tout=Tdie.
For some reason I was thinking that Qmax was the actual die power disp.
doh!!
*sneaks in when nobody is looking*
Hmmm... read the linked article and the discussion on "effectiveness"...
Given two choices, I'll choose that Sheikh did a "ppj" at conveying the core of his thought.
*digests the article and gets heartburn*
hmmmmm.....
*gets a wicked gleam in his eye*
Well heck, I get it now....
*builds a pump flow control system slaved to the inlet temp of the radiator and die temp of processor*
*sets control loop to adjust flow rate to maintain rad inlet coolant temp = die temp*
*makes a kit with small pump, small rad, and his new super-duper control system*
*sells it as most "effective" water cooling kit on the market*
muhahahahahaahhahahaha
*casually drops a note of serious content on the floor*
Summary of what I think his "core thought" was :
A measure of the relative thermal efficiency of a test group of heat exchangers (be they cold plates, blocks, rads, etc.), which is directly proportional to the amount of energy removed from a system under an identical set of conditions, can be measured by the deltaT across the exchanger (given the identical test conditions). Given more efficient components, a specified deltaT between the heat source (CPU, GPU, mem, etc.) and the ambient environment might be obtainable with lower coolant flow (both air and liquid), which could lead to smaller size and less noise ($ maybe, maybe not...).
Comment1: *Optimal* efficiency is quite rarely, if ever, 1.
My other 2 cents: As shown by my mad scientist device created before a moment of lucidity overcame me, thermal efficiency alone, *as defined as he did*, accomplishes nothing (except maybe a core meltdown). Ultimately the desired goal is to maintain the lowest temperature at the energy source (in this case the component die temps) in the most efficient manner (different people apply different metrics to the equation... noise, $, size, etc., etc.) within a given set of constraints (although some place no constraints other than "is it possible"). That having been said, if one examines the dominate factors in the equations for fluidic heat exchangers, there is much to be said for velocity and turbulence, which come at a cost ;)
*kicks note into the corner under the end table and hopes nobody notices it*
*waves hi on the way out*
*skips off into the darkness of "lurk-dumb" again cackling madly*
...
Well heck, I get it now....
*builds a pump flow control system slaved to the inlet temp of the radiator and die temp of processor*
*sets control loop to adjust flow rate to maintain rad inlet coolant temp = die temp*
*makes a kit with small pump, small rad, and his new super-duper control system*
*sells it as most "effective" water cooling kit on the market*
Isn't that somewhat similar to what Apple did in the G5 with the monitoring software?
snowwie
02-06-2005, 06:48 PM
is the advantage to controlling fan speed analagous to controlling pump speed? is peak (12v) speed THAT noisy for the DDC? is 7v on the DDC that much quieter?
edit: is there another advantage to a pump speed controller that I am unaware of?
BillA
02-07-2005, 11:41 AM
the pump won't run @ 7V input
I see I hid that note too well...