A little status report;
.....One exception is the flow rate calculation at higher flows, it uses the water in-out delta T and ......
|
Maybe should include dP*Q correction for calculating flow rate from Heat Flux
Only ~ 1.5w here but......
Heat Dump =HeatFlux + KPa*LPM/60
LPM=HeatFlux/(69.77*dT - Kpa/60)......(Cp=4186 J/KgC) Think 60 is rigorous but not checked)
Dunno what it does to your queried "dp correction?= -0.05"