View Single Post
Unread 05-28-2004, 06:40 AM   #96
wijdeveld
Cooling Neophyte
 
Join Date: May 2004
Location: Netherlands
Posts: 29
Default

O.K. it's done!

For easy of comparison I HAVE EXAGGERATED THE TIM LAYER IN THE CALCULATIONS!!! It’s now 0.25 mm instead of 0.025 mm

Contour plot:
- Just for illustrating the isolines from the CPU/die to the cooling medium in a 2-D slice (scale = 10 x 10 mm)
- Don't mind the concentration scale in the contour plot, I haven't calibrated the calculation on a temperature scale here.

x-y plot:
- All three TIM compound have the same results (within 0,1 oC) and plot as one line

So, what you can see in the x-y plot (which is temperature corrected) is that the TIM compound doesn't matter (I’ve tried goop, AS3 and pure copper conductivity), it's the heat flux across the solid/solid boundary that's limiting. I've also done a calculation without TIM layer (direct HS to copper block contact); this improves the delta T with ~10% (-1.1 oC for the CPU/die).
So, my hypothesis right now is that:
1) the exact compound composition doesn’t matter that much
2) ensuring a perfect contact between solid interfaces is the most important aspect of a good TIM
3) even in a perfect fit situation TIM adds ~10% to the deltaT (+1.1 oC on a total of +14 oC)

I’ll try to evaluate the thickness of the TIM layer on the slope later on.

[EDIT] I've applied a fairly low load: 60 watt
Attached Images
File Type: png 2D-profile.png (6.8 KB, 22 views)
File Type: png delta_T.png (6.0 KB, 18 views)
wijdeveld is offline   Reply With Quote