Quote:
Originally posted by murray13

No a RMS AC meter will only be accurate with a pure sine wave. The more inductive the load the more it will be off. ie the wave form looks less and less like a sine wave.
No, a "True RMS" meter ideally is unaffected by distortion. (There are practical limits with regard to the range of frequencies over which an actual meter will be accurate.)

An inductive load does not distort the shape of the waveform, it only shifts the phase of the current with respect to the voltage.