04-16-2005, 12:45 AM | #26 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
Ok so I have to say that (a) BillA's CPVC flanges with rubber gaskets work well (b) the Yokogawa flowmeter that Brucoman donated seems to produce reasonable results (c) the LCD on this thing is HORRIBLE. It has like a 5 degree range where I can read it and otherwise no joy. I'll get this thing reporting 4-20 mA ASAP. If all goes according to plan I'll have a new test loop set up tomorrow that logs dP and dT (wb) via Labview and I'll just eyeball the flowrate with the LCD readout on the flowmeter. Before I do that though I'm going to do a full range comparison of the readings of the GPI and the Yokogawa.
__________________
Getting paid like a biker with the best crank... -MF DOOM |
04-17-2005, 11:17 AM | #27 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
A little progress
The lcd output on the Yokogawa is in L/min so I used 3.875 L/gallon as the conversion for the GPI's output. It looks like the readings are pretty closely correlated over the entire range but not dead on. No big surprise I guess.
__________________
Getting paid like a biker with the best crank... -MF DOOM |
04-18-2005, 09:45 AM | #28 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
looks good, I'd put more credence in the AdMag
(and were it my data I'd probably 'adjust' the paddlewheel figures) |
04-18-2005, 10:20 AM | #29 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
I am planning to just let the socketA data stay as it is and then retest a few of the blocks that are still commercially available with the new setup. I'll probably spend the next few weeks just doing flow resistance testing of all those Socket A blocks and GPU blocks and radiators and the like to really get proficient with the dP xmitter and with the methodology and with Labview.
__________________
Getting paid like a biker with the best crank... -MF DOOM |
04-26-2005, 02:31 PM | #30 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
A bit of an update
Over the weekend I only got one day to really work on testing-related stuff. I have been testing out equipment as I get the chance, and as of Friday my testing room was a complete nightmare. A tangled mess of wires and hose and equipment just stacked everywhere with no real rhyme or reason. So rather than continuing down that path, I did some thinking about how I could arrange the space to make more efficient use of the test instruments and my work area. Here's how it looked before I started rearranging things (but after cleaning a bit):
The SocketA test system is on the left, and the old test loop was on that table in the center of the page. The PC under the desk runs Labview and the MAX6655 software for data collection and there's a KVM for the mouse, kbd, and monitor. The big stack of instruments on the right of the page is an HP 3497A scanner, a 3478A DMM, and a Fluke 2190A RTD setup all controlled via GPIB. It was NOT convenient to adjust wires and mess with them. So I rearranged the setup like this: The backs of the instruments now face the table so it's much easier to run wires and probes from the equipment to the testing loop. The front of the instruments are all accessible from the other side of the shelf. I have the new flowmeter on the table and you can see the dP xmitter above on the ledge. The PC on the bottom shelf of the instrument rack is the new Socket 939 system for complete system testing; it'll go into action as soon as I get the new soldering station set up on the left. I will be adding UPSes for all of the instruments on that bottom shelf this weekend. I still have a few hours of cleaning and arranging to do, but the space is much more useful now. The drawback to all these instruments is the need for lots of space and constantly accessing them.
__________________
Getting paid like a biker with the best crank... -MF DOOM |
04-26-2005, 05:39 PM | #31 |
Cooling Neophyte
Join Date: Jul 2004
Location: FL
Posts: 83
|
good idea with the shelf regarding accessability. Is that s939 case an AMS gtower? Those are nice
__________________
|
04-26-2005, 05:47 PM | #32 |
Cooling Savant
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
|
does that mean your going to test GPU blocks soon?
__________________
"Great spirits have always encountered violent opposition from mediocre minds" - (Einstein) |
04-26-2005, 06:10 PM | #33 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
MH I have about 4 things going on at various stages of completion. The easiest for me to do is to try and generate some numbers for the modeling that Cathar and Les and Lolito_Fr were doing a while back. It's easiest because it uses all the old equipment and is separate from this new setup. The other easy thing to do is to begin collecting dP measurements on GPU and CPU blocks.
The other two things I'm doing are a little harder because they involve some rather drastic hardware mods. I have to pull the LM63 IC off this 9600XT and tap into the diode from that way and then calibrate it for GPU block testing. I also have to cut open my socket 939 socket and solder diode wires onto that 3000+. I've been sorta putting both those things off because I'm a big sissy. Yes that's an AMS Gtower case. Bruce has shipped me a full tower with dual 120mm holes cut in the top for complete system testing. I'm waiting on it to get here to start messing with that project (instead of retesting a bunch of blocks for socket 939 I'm going to try and get a nice complete system testing setup running).
__________________
Getting paid like a biker with the best crank... -MF DOOM |
04-26-2005, 06:21 PM | #34 |
Cooling Savant
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
|
sounds like not enough hours in a day...
only reason i'm asking about teh GPU test is cause I have a video card that wants to be watercooled again... the crystal orb is so loud in comparison now...hehehe
__________________
"Great spirits have always encountered violent opposition from mediocre minds" - (Einstein) |
06-16-2005, 09:47 AM | #35 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
ok this is probably one of the best threads I could update, right? Talcum kindly donated a DVM card for y 3497A and also wired it up as a six channel DVM with labview vis and everything! 2 channels convert current to voltage (handy for 4-20 mA output instruments). I got it mostly working last night; I still have an issue scanning those channels while monitoring mA reading from the dP xmitter with a separate DMM. Labview makes no sense to pH.
Tonight I'll cut a hole in the mobo tray of the GTower Server, clean up my testing room and install test system in that GTower case. Friday I plan to collect the first full set of data with the Labview setup just to verify it works as intended. Then I'll probably spend a week running baseline tests on all the instruments (no fun but crucial).
__________________
Getting paid like a biker with the best crank... -MF DOOM |
06-16-2005, 07:23 PM | #36 |
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
After getting my bench up and running I have come up with about 10 years worth of projects to test with it. Wish I spent the time and money on it 4 years ago.... I already have a bunch of stuff done. Just waiting on you guys to get things re-organized to post it. Headed to Florida monday untill the 1st so I am not in a hurry anyway. Man, got to order a lot of copper when I get back....
|
09-19-2005, 08:22 PM | #37 | ||
Cooling Neophyte
Join Date: Sep 2001
Location: High Altitude Lab
Posts: 94
|
Quote:
http://www.sciencedaily.com/releases...0917085551.htm Quote:
http://www.sciam.com/article.cfm?art...D883414B7F0000 how a "ghetto" DIY version may be possible I dont know not to derail the thread or anything
__________________
LurkyLoo |
||
09-19-2005, 08:52 PM | #38 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
Interesting links, Ice Czar. Do you have an opinion on UV sterilization?
|
09-20-2005, 01:01 AM | #39 |
Cooling Neophyte
Join Date: Sep 2001
Location: High Altitude Lab
Posts: 94
|
well I dont have a qualitative opinion
Im familiar with UV irradiation though but I did find that as a "new" development interesting especially in relation to this http://web.mit.edu/hmtl/www/papers/DHIR.pdf well that and a paper I read a summary of a few years back about sonic induced microbubbles in enhancing heat transfer back on topic looking at various Rosemount 1151 Pressure Transmitters I see all sort of "Smart Ranges" 5, 8, 9 what does that denote? a calibration range?
__________________
LurkyLoo Last edited by Ice Czar; 09-20-2005 at 02:43 AM. |
09-20-2005, 02:56 PM | #40 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
Got it.
Goto: http://www.rosemount.com/document/pds/1151.pdf and scroll down to page 16 for a list of the range codes. There's a reference to "smart ranges" on page 3. edit: see http://www.rosemount.com/products/pressure/m1151.html for more info. Last edited by bigben2k; 09-20-2005 at 03:02 PM. |
09-20-2005, 03:13 PM | #41 |
Cooling Neophyte
Join Date: Sep 2001
Location: High Altitude Lab
Posts: 94
|
aha
thankyou very much !!!
__________________
LurkyLoo |