Water Block Design / Construction Building your own block? Need info on designing one? Heres where to do it |
![]() |
Thread Tools |
![]() |
#51 | |
Cooling Savant
Join Date: Oct 2002
Location: MidWest USA
Posts: 176
|
![]() Quote:
peace. unloaded |
|
![]() |
![]() |
![]() |
#52 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
'most' wb tests are run at 70W, but the actual value does vary very slightly
- do note that it is the actual value, as recorded at each measurement point, that is used in all calculations related to those specific combinations here is a breakdown: - heater voltage is measured ~1/4" from the heater's coil from the voltage sensing leads used in the 4-wire setup from the regulated power supply - heater current is measured and corrected for the meter's 'burden' (fro a Keithley 195A this is 0.0148A with a measured current of 1.4224A, with this heater 49.462VDC applied measured with a Fluke 8842A) - the resultant Watts are then calculated and then reduced by 1.6% to 'correct' for the apparent secondary path losses (heat applied but not going through the wb) this value, to 5 sig figs, is the one used for all calcs relating to temps taken at that same moment note that my temps have only 4 sig figs, and this is further reduced by me to 3 sig figs for the "C/W" (or T/W if I'm looking at the bp temps) the absolute accuracy/uncertainty of the measurements depends on the stability of the measurand and the capability of the instrument, and an advantage to the continuing reduction in sig figs as the calculations progress is the effective elimination of propagation errors as I suspect Since87 can describe, this whole topic becomes complex very quickly; fortunately my measurand values are fairly large (ignoring the RTD resistance changes) |
![]() |
![]() |
![]() |
#53 |
Pro/Guru - Uber Mod
Join Date: Sep 2002
Location: Indiana
Posts: 834
|
![]()
Right, it doesn't matter whether the power into the die simulator is exactly at 70 Watts. It does matter that you know the power into the die simulator accurately at each data point.
(I'd skimmed through Bill's description of the die simulator setup and seen that he was doing it right to the nth degree. I hadn't remembered the details though.) |
![]() |
![]() |
![]() |
#54 |
Cooling Savant
Join Date: Feb 2002
Location: Oxford University, UK
Posts: 452
|
![]()
As I suspected.
BillA, have you any desire to put together a heat source based on the Hammer dimensions. I have a few ideas for Hammer waterblocks, and if I did build any of them, I'd definitely want to get them tested properly. 8-ball |
![]() |
![]() |
![]() |
#55 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
am now doing the initial parts of this
2 distinct elements, well - 3 perhaps the mounting geometry: no real biggie, put the studs where ever they need to be the clamping force: AMD is now 24lbf P4 is 100lbf Hammer is to be ~90 or 100lbf (?) this may be speced, have not looked the heat source size: this is a pissing contest, though to me (and others) it is quite clear see Joe Citarella's thoughts here, with which I, and others, do NOT agree at all my 'issue' is with the IHS heat spreading one can measure its thickness, go to Waterloo and plug in the values and that is it, ain't gonna get no more - in fact rather less due to the TIM joints so the upshot, per me, is that the actual/effective heat source is NOT going to be substantially larger than the CPU - the lateral heat dispersion will occur in the bp of the wb or hsf I'm thinking strongly of staying with my present 10x10mm die - also enables the direct comparability of data and why would a 'good' wb not be so on any CPU ? eh ? Hammer 'special' = marketing 'special' |
![]() |
![]() |
![]() |
#56 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
For a Cu Heatsink/Waterblock/IHS. Used Waterloo for thermal Resistance when change in Flux Channel . 1D sums for other resistance . Added up the resistances. Differences between "Purple Dotted" and "Blue Dotted" is what would expect to show in a "Joe Citarelli type" experiments* with Cu coolers and reducing Cooler Dimensions to fit IHS**. ![]() * http://www.overclockers.com/articles708/index02.asp ** Calculating for the reduced contact area without reduction in heasink base area involves an another "Spreading Resistance" calculation - cannot be bothered(confused enough as it is) |
|
![]() |
![]() |
![]() |
#57 |
Cooling Savant
Join Date: Oct 2002
Location: MidWest USA
Posts: 176
|
![]()
I didn't understand Joe's experiment or results. To start with the pages were linked backwards. Then on one of the temp tables, for one HSF the on die temp was lower than the IHS temp. I assume its from some kinda error (maybe not?). Anyway it confused me. And finally to eleminate/isolate cooling properties of the IHS, he hacked up the HSF rather than removing the IHS! WHatever he was trying to do, I sure couldn't follow him. Glad you guys mentioned it, I thought maybe it was just me 8)
peace. unloaded |
![]() |
![]() |
![]() |