Unread 08-27-2002, 08:31 PM   #176
phiber
Cooling Neophyte
 
Join Date: Aug 2002
Location: NYC
Posts: 6
Default

Quote:
Originally posted by Joe
You know something, I am done with you on this forum... you are an annoyance and provide little if any accurate info. And then you go and start laughing at people cause they dont want to deal with a HVAC system AFTER YOU BLEW YOURS UP.

Get a life, and Get out of here.

*banned*
Thx man...
i was quite miffed after he said that....
phiber is offline   Reply With Quote
Unread 08-27-2002, 09:45 PM   #177
bowman1964
Cooling Savant
 
bowman1964's Avatar
 
Join Date: Jul 2002
Location: virginia usa
Posts: 126
Default

well ok guys let me try to shed some real life info hands on i should say of converting a (lets say r12 to r134).now i have been buying and installing changeover systems ever since there was the new kid r134a out.now the compressors i have sold over the years( last 12 years i say) are made 134a but can easily be changed over with no problem to r12.we most of the time take the compressor and turn upside down and warm the unit alowing all the oil as possable to drain for a hour or so.now r12 doesnt like pag oil very well(r134oil)but it will with stand a small amount of mixing.now putting r134 in a r12 sysyem is the same way but the pag oil mixes alot easyer.pag oil is designed to allow for a small amount of mixing with minerial oil.now i sell orings for these systems and i will tell you there is no differance in the orings.
now i see you already know that removing water from the system with a good vacuum is a must.......but allowing a vacuum to stay on a system for too long will break down the oil in the system doing alot more harm than good.i usally run it for about 1 hour on a small system. 8 hours would be on a very large system.we service on the highway 18 wheelers people call them,,,road tractors .600hp diesels that haul everthing well all use everyday.these systems use 2.5 to 3 lbs of r134a.and we only vacuum them for a couple of hours at the most.these systems are 10 times the size of the systems we are building for a pc.i know alot of guys in here are very smart people and can read the specs on anything.but real the world sometimes is a little differant.i am not guesing or reading some elses stuff i have done it myself.i guess going on 20 years now.but i am not to old too learn.........that is why i come in here. one of the best forums on the internet and i am proud to be part of this fourm
__________________
xp2800barton@2712 226x12 dual bank 2x256 twinmos pc3200 8RDA epox full mods.vdd,vdimm,vcore.
custom r502 cooled unit.CPU running @-18C GPU -21C Chipset -20c
only one like it.in one case.
custom r502 cooling unit

3D2001SE 21315

3DMARK03 6659
bowman1964 is offline   Reply With Quote
Unread 08-28-2002, 12:13 AM   #178
SonixOS
Cooling Savant
 
SonixOS's Avatar
 
Join Date: Mar 2002
Location: Silver Spring, MD
Posts: 282
Default

bowman, u think i should invest in switching to R502? Where could I get an expansion valve and an accumulator?
__________________
-sonix-
=======================
Antec SX830
Abit KR7A-133
MSI Geforce3 Ti200 VT128
TV-IN and TV-OUT
Sound Blaster Audigy
Linksys LNE100 V2.0
Toshiba DVD Drive 40x/16x
IBM Deskstar 60GXP 60gig
Watercooled
http://www.sonixnet.tk
=======================
SonixOS is offline   Reply With Quote
Unread 08-28-2002, 06:52 AM   #179
bowman1964
Cooling Savant
 
bowman1964's Avatar
 
Join Date: Jul 2002
Location: virginia usa
Posts: 126
Default

well to be honest r502 is nice but really too much for what you get.too much cost involved.i dont even use it.we specialize in moble ac units which usaually use r12...r134a...r22.
now r22 will get very cold.boiling point is -40f @ 0 psi.mine will run down to -60f but i had it running in a hard vacuum.all depends on what you what to do.now the accumulator you will need to make for a small system like yours i havent heard of anyone using on on a small system.I made one but found it didnt do me any good.on a pc you are running under a load 100% of the time.not meaning the cpu is loaded 100% but that you are making heat all the time so the compressor needs to run full time.i have tried cycling the compressor on and off and there is no way the compressor can come back on and catch up to the heat load.to be honest on mine if i cut the compressor off for one minute i have to wait about 1 hour before i can restart it because the liquid runs back in the compressor after i cut it off.now if i didnt have mine cooling so low in the temps this wouldnt be a problem but running a xp2100 @2150 mhz @ -42c takes alot from a cooling system.i would stay with a capillary tube system no expanson vavle.the expansion vavle would not work as well on a small system.and all we use at work uses a expansion vavle so i would use it if i thought it would work better.
__________________
xp2800barton@2712 226x12 dual bank 2x256 twinmos pc3200 8RDA epox full mods.vdd,vdimm,vcore.
custom r502 cooled unit.CPU running @-18C GPU -21C Chipset -20c
only one like it.in one case.
custom r502 cooling unit

3D2001SE 21315

3DMARK03 6659
bowman1964 is offline   Reply With Quote
Unread 08-28-2002, 07:43 AM   #180
Brians256
Pro/Staff
 
Brians256's Avatar
 
Join Date: Oct 2001
Location: Klamath Falls, OR
Posts: 1,439
Default

Thanks bowman! My info is second hand and from fuzzy memory on the conversion stuff. So, real experience is exactly what we needed to really answer the question.
Brians256 is offline   Reply With Quote
Unread 08-28-2002, 01:51 PM   #181
SonixOS
Cooling Savant
 
SonixOS's Avatar
 
Join Date: Mar 2002
Location: Silver Spring, MD
Posts: 282
Default

bowman, i am running a water chiller and NOT direct on die evaporator. I am really worried all the liquid is gonna kill the compressor too soon.
__________________
-sonix-
=======================
Antec SX830
Abit KR7A-133
MSI Geforce3 Ti200 VT128
TV-IN and TV-OUT
Sound Blaster Audigy
Linksys LNE100 V2.0
Toshiba DVD Drive 40x/16x
IBM Deskstar 60GXP 60gig
Watercooled
http://www.sonixnet.tk
=======================
SonixOS is offline   Reply With Quote
Unread 08-28-2002, 02:05 PM   #182
bowman1964
Cooling Savant
 
bowman1964's Avatar
 
Join Date: Jul 2002
Location: virginia usa
Posts: 126
Default

WELL IF YOU HAVE LIQUID ENTERING THE COMPRESSOR NOW, YOU HAVE TO FIX IT SOON.2 THINGS TO DO ,EASYEST IS TO REMOVE SOME FREON UNTILL IT STOPS,DOWNSIDE TO THIS IF YOU DONT HAVE ENOUGHT AREA IN THE EVAP. YOU WILL GO FROM COOLING WITH LIQUID ENTERING THE COMPRESSOT TO NO COOLING AT ALL.SECOND AND THE BEST THING TO DO IS TO ADD 10 FT OR SO TO THE EVAPORATER TUBING.THIS WELL GIVE THE FREON ADDED TIME TO BOIL OFF INTO A GAS.OR IF YOU ARE USING SOMETHING THAT YOU ARE UNABLE TO ADD MORE TUBING TO.TRY TWO THINGS. GET YOURSELF A WATER PIPE HEATER THE ONES LIKE YOU WRAP AROUND WATER PIPES TOP KEEP THEM FROM FREEZING,AND WRAP THE RETURN LINE TO THE COMPRESSOR THIS WILL GIVE YOU ENOUGHT EXTRA HEAT TO BOIL OFF THE LIQUID BEFORE IT MAKES IT TO THE COMPRESSOR
(SOUNDS CRAZY BUT IT WILL WORK WITHOUT BREAKING THE SYSTEM DOWN.SECOND THING IS TO WRAP 10 FT AROUND THE COMPRESSOR ITSELF AND HAVE THE RETURN LINE GO AROUND THE COMPRESSOR BEFORE IT GOES INTO THE COMPRESSOR.THIS WILL MAKE SURE YOU GET ALL THE FREON BOILED OFF AND HELP COIL THE COMPRESSOR.
I HOPE THIS HELPS
__________________
xp2800barton@2712 226x12 dual bank 2x256 twinmos pc3200 8RDA epox full mods.vdd,vdimm,vcore.
custom r502 cooled unit.CPU running @-18C GPU -21C Chipset -20c
only one like it.in one case.
custom r502 cooling unit

3D2001SE 21315

3DMARK03 6659
bowman1964 is offline   Reply With Quote
Unread 08-28-2002, 02:29 PM   #183
SonixOS
Cooling Savant
 
SonixOS's Avatar
 
Join Date: Mar 2002
Location: Silver Spring, MD
Posts: 282
Default

u got a picture of that heater ur talkin about for the pipes. R you talkin about just regular insulation or a heater?
__________________
-sonix-
=======================
Antec SX830
Abit KR7A-133
MSI Geforce3 Ti200 VT128
TV-IN and TV-OUT
Sound Blaster Audigy
Linksys LNE100 V2.0
Toshiba DVD Drive 40x/16x
IBM Deskstar 60GXP 60gig
Watercooled
http://www.sonixnet.tk
=======================
SonixOS is offline   Reply With Quote
Unread 08-28-2002, 02:32 PM   #184
aenigma
Immature Title Goes Here
 
Join Date: Aug 2002
Location: Washington
Posts: 81
Default

Quote:
Originally posted by SonixOS
u got a picture of that heater ur talkin about for the pipes. R you talkin about just regular insulation or a heater?
It is a pipe heater,keeps pipes from freezing in the winter.I have seen them at bi-mart.
aenigma is offline   Reply With Quote
Unread 08-28-2002, 08:34 PM   #185
bowman1964
Cooling Savant
 
bowman1964's Avatar
 
Join Date: Jul 2002
Location: virginia usa
Posts: 126
Default

yes that is what i was talking about aenigma, thanks.

you can find the heat wrap at most home depots and such.
__________________
xp2800barton@2712 226x12 dual bank 2x256 twinmos pc3200 8RDA epox full mods.vdd,vdimm,vcore.
custom r502 cooled unit.CPU running @-18C GPU -21C Chipset -20c
only one like it.in one case.
custom r502 cooling unit

3D2001SE 21315

3DMARK03 6659
bowman1964 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 12:33 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...