04-18-2003, 11:53 AM | #52 | ||
Registered User
Join Date: Mar 2003
Location: Brooklyn, NY
Posts: 112
|
Quote:
Please correct my impression if it is wrong, but I get the impression that you think the radiator doesn't need to cool as much because the water temperature is lower. This, I'm afraid, is completely wrong. Yes, the water is cooler, but the rad has to cool more water for a given time period than with a slower flow rate. So the radiator really does have more energy to transfer. It must, as that is the only way to reduce the temperature of the CPU. Quote:
In a typical system, we have water, at a given temperature, going into the waterblock. The water is heated to a higher temperature and then goes to the radiator. There, it is cooled back to the starting temperature and the cycle begins again. When we increase flow, the starting water temperature is assumed to stay the same. This means that the increase to waterblock performance is based solely on increased flow. The performance of the radiator, however, will be affected by two factors. The fundamentals of heat transfer tell us that the water exiting the waterblock is now at a lower temperature. Since we are now starting with a lower temperature for the radiator, the performance is affected by increased flow, *and* decreased temperature. Since a temperature decrease will reduce performance, the benefit from increased flow will be countered. Yes, the radiator can now move heat faster, but the waterblock's performance increase is still bigger. The radiator will get more heat than its performance increase can account for. The bottom line is that the radiator is going to have to work harder. Furthermore, the decrease in radiator temperature means that the radiator/fan relationship is not quite as good as it used to be. This fact exacts another toll on the radiator. The result from these additional influences is that the radiator is walloped with lots of extra work. So, what happens to CPU temperature? If you have a good radiator that can rise to the challenge, and cool water down to the point it did before, then you will have a lower CPU temperature. However, if the radiator can't rise to the challenge and can't remove the heat, then it will leave the heat in the water. This will undo the flow benefit, and temperatures will rise to the point where there is once again balance between the heat taken from the CPU and the heat expelled by the radiator. This balance will occur at a higher CPU temperature. So we see that it all depends on the radiator. Anything you can do to help the radiator do its job better, will help you realize the benefit of increased flow. Pushing more air through, or changing the rad outright, may be required. If you had a good radiator to begin with, and you weren't using all of the radiator's cooling capacity, then increasing flow will drop your CPU temperature by putting that extra capacity to work. |
||
04-18-2003, 12:10 PM | #53 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
a minor clarification to Graystar's description
all rad 'capacity' is always utilized, its not as if there is ever unused capacity what is happening is that a rad has 2 efficiency curves the major one related to the air side flow rate the minor one being the liquid side flow rate (although this can be significantly manipulated) the two affect each other, so a shift in either to a 'point' of greater efficiency will result in increased cooling - but since the actual goal is the lowest possible coolant exit temp from the rad, which is in conflict with the optimization of the wb's performance needs (always max flow rate); the "theoretical" calculation of the optimum compromised flow rate is beyond anyone without actual performance curves for the relevant components |
04-18-2003, 01:04 PM | #54 | |
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
Quote:
|
|
04-18-2003, 01:49 PM | #55 |
Cooling Savant
Join Date: Apr 2003
Location: San Mateo, CA, USA, Earth
Posts: 433
|
Well... now that I know my calibration method and measuring method were off... I retract my temp statements.
Until I've been able to modify a CPU and do proper bath calibration and later measurement, I will not quote any more temps. I feel I owe Jaydee and BillA an apology in this area too. I came up with the proceedures I use all on my own and it shows, thanks for the info guyz...
__________________
MMZ>TimeLord "Oooooooooh... that's gonna leave a mark!" |
04-18-2003, 02:01 PM | #56 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
pHaestus is kinda 'out in front' with this stuff
although few wish to accept what he says |
04-18-2003, 02:11 PM | #57 |
Cooling Savant
Join Date: Oct 2002
Location: Boston
Posts: 238
|
Christ, I'm gone for a day and BillA manages to blow everyone's cerebral cortex. Let me get the paper towels.
Okay, BillA, I don't know exactly why you're getting the charts you're getting. Not saying you're violating any rules of physics, but your current explainations, if I'm reading them right, are. For your rad, the heat transfer coefficient of the air should not be adversely affected by improving the heat transfer coefficient of the water. They are completely independent phenomena. My first job when something goes against theory is to recheck everything. What sort of precision can you get by generating replicate data? What is the accuracy of your temperature measuring equipment? Your flow metering equipment? Your pressure metering equipment? What are your raw data so others can check your calculations? And, assuming you're correct on all this, what is really happening? Alchemy |
04-18-2003, 02:42 PM | #58 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
short answers (trying to get my main computer back up)
for sure my explanations are inept yes, air and water quite independent, and treated in the experiment's design as independant let me get my box back up and plot the new data (many problems with the old) but those bumps are quite real not so difficult really but in the other thread perhaps ? - Null-A Ben started another later |
04-18-2003, 03:04 PM | #59 | ||
Cooling Savant
Join Date: Feb 2002
Location: Oxford University, UK
Posts: 452
|
Quote:
That statement is WRONG. The processor has a given output of heat. Lets say 70W, for the sake of argument. If you had an infinitely efficient radiator, and an infinitely efficient waterblock, the processor would be at ambient temperature, BUT THERE WOULD STILL ONLY BE 70W BEING TRANSFERRED INTO THE WATER AND ONLY 70W TRANSFERRED INTO THE AIR BY THE RAD!!!!! This is the key principle to understand. If you don't understand this then there is no point in me carrying on. Quote:
The air temp is fixed - yes? The C/W ratio at a given cfm is fixed - yes? The heat load is fixed at 70W - yes? Then the fins of the rad WILL be at ambient temp + 70 x C/W (at the given CFM) For a 70W load this is the equilibrium position and will not change! This will not be affected by a change in flow rate, however, a change in flow rate will change the C/W ratio for heat going from the water to the fins. We have already established, that the fin temperature is dependent on the fixed heat load, the fixed ambient temp and the fixed efficiency, resulting from a fixed CFM. Lets call this Tf, for fin temperature. Now lets start with a given C/W for a given flow rate. The average water temperature in the radiator should be such that the temperature difference divided by the C/W is equal to 70. In other words, the average water temp in the rad needs to be; Tf + C/W x 70 Now lets improve the efficiency. An improved efficiency is a lower C/W ratio, agreed? So lets call this (C/W - D). D for difference. So now, the average water temp in the rad will have to be; Tf + (C/W - D) x 70 = (Tf + C/W x 70) - (D x 70) Can you now see that the average water temp from an improved efficiency is now lower than before by an amount (D x 70). Granted, D is small, probably of the order of 0.01. However 0.01 x 70 is of the order of 1 degree difference in average water temp throughout the loop. Now I will concede that the water temperature does not vary linearly as it passes through the rad, but I have taken the liberty of evaluating the temperature change removing 70W from a water flow at 6lpm. which is roughly 1.5 gpm. It turns out to be 0.16 degrees. We know therfore, that the average temperature of the water has a margin of error of 0.16 degrees. Dropping this by 1 degree will reduce the temperature of the water going into the block, which will in turn reduce the temperature of the cpu. Sorry the last bit's rushed, but I've run out of time. Any further questions or points you would like to disagree with, carry on. 8-ball
__________________
For those who believe that water needs to travel slowly through the radiator for optimum performance, read the following thread. READ ALL OF THIS!!!! |
||
04-18-2003, 03:09 PM | #60 | ||||||
Cooling Savant
Join Date: Oct 2002
Location: Boston
Posts: 238
|
Quote:
Quote:
Quote:
Quote:
Quote:
Quote:
Alchemy |
||||||
04-18-2003, 03:51 PM | #61 |
Cooling Savant
Join Date: Feb 2002
Location: Oxford University, UK
Posts: 452
|
I think I said pretty much the same thing as alchemy, which reassures me somewhat. I always worry on its only two people carrying out a debate. It can turn into a shouting mach pretty quickly.
Alchemy, does my post state anything which contrevenes any fundamental laws. I'm pretty sure it doesn't, unless I forget ny advanced thermodynamics course I did a couple of years ago. 8-ball
__________________
For those who believe that water needs to travel slowly through the radiator for optimum performance, read the following thread. READ ALL OF THIS!!!! |
04-18-2003, 03:55 PM | #62 | ||||||
Registered User
Join Date: Mar 2003
Location: Brooklyn, NY
Posts: 112
|
Quote:
Quote:
Quote:
Quote:
Quote:
Quote:
|
||||||
04-18-2003, 04:18 PM | #63 | |
Cooling Savant
Join Date: Jul 2002
Location: Toronto, Canada
Posts: 381
|
Quote:
__________________
Michael E. Robbins M.A.Sc. Candidate, University of Toronto 12.1 GHz of AMD's finest (17.7 GHz total) crunching proudly for the AMDMB.com Killer Frogs SETI BOINC: Dual Opteron 246s (Iwill DK8N) | XP2800+ (Shuttle SN41G2) | 3x XP2400+ (ASUS A7N266-vm) SETI BOINC: 2x P4 2.8E (ASUS P4R800-vm) | Crunching 24/7 |
|
04-18-2003, 05:29 PM | #64 | |
Registered User
Join Date: Mar 2003
Location: Brooklyn, NY
Posts: 112
|
Quote:
|
|
04-18-2003, 05:38 PM | #65 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
WRONG
you putting suction on the board traces ? re-try that one |
04-18-2003, 05:38 PM | #66 | ||
Cooling Savant
Join Date: Feb 2002
Location: Oxford University, UK
Posts: 452
|
Quote:
I will be the first to admit that there are effects which will alter the theoretical outcome, as with everything, but the theory still stands and is relatively accurate. As I say over and over, yes you do need to consider the whole system, but the only data we know is the flow rate, the efficiencies, the heat load and the ambient air temp. The only things we can directly control are the heat load, the ambient air temp and the flow rate. (air and water) The efficiencies are determined by the flow rates, which in turn determine the delta T required to shift the set heat load. THIS IS HOW IT WORKS. Consider this. There are equations for the rate at which the water cools in the rad, the rad temp relative to the ambient temp, the water temp relative to the rad temp, the waterblock temp relative to the water temp and the cpu temp relative to the waterblock temp. This is essentially a set of simultaneous equations which can be solved. However, the only temperature we know is the ambient air temp, so we MUST work backward from this. Is this clear. The thermodynamic principles I outlined earlier are correct. Quote:
By increasing the flow rate, have we mysteriously added more water? The only concept you need to grasp is that watercooling is all about different components/mediums reaching equilibrium temperatures relative to the only defined temp, the ambient air, such that the differences in temps with the corresponding heat transfer coefficients result in the treansfer of the defined heat load. Changing variables such as flow rate air or water, will increase the heat transfer coefficients, thus reducing the temperature differences. Note this doesn't take into account heat from the pump, though differnt pumps may produce the same flow with different heat input. This is one of those real world factors that is hard to control. but hey, lets get the basics sorted first. 8-ball
__________________
For those who believe that water needs to travel slowly through the radiator for optimum performance, read the following thread. READ ALL OF THIS!!!! |
||
04-18-2003, 05:43 PM | #67 | |
Cooling Savant
Join Date: Feb 2002
Location: Oxford University, UK
Posts: 452
|
Quote:
The last statement here is false. The cpu puts out a fixed heat load for a given frequency. This does not change! The cpu temp is reduced by increasing the efficiencies....... Oh god, someone please shoot me. I can't go on like this! Over at Bit-Tech, they have a nice head banging against a wall smilie. This would be appropriate. 8-ball
__________________
For those who believe that water needs to travel slowly through the radiator for optimum performance, read the following thread. READ ALL OF THIS!!!! |
|
04-18-2003, 05:44 PM | #68 | |
Registered User
Join Date: Mar 2003
Location: Brooklyn, NY
Posts: 112
|
Quote:
|
|
04-18-2003, 05:47 PM | #69 |
Cooling Savant
Join Date: Feb 2002
Location: Oxford University, UK
Posts: 452
|
We have the "70W" going in and "70W" going out of the same volume of water. IE all of the water in the system.
I think much of your problem comes from considering each molecule of water. Overcomplicated and always likely to end in trouble. 8-ball
__________________
For those who believe that water needs to travel slowly through the radiator for optimum performance, read the following thread. READ ALL OF THIS!!!! |
04-18-2003, 05:52 PM | #70 | |
Cooling Neophyte
Join Date: Jan 2003
Location: OR/CA/NY
Posts: 81
|
Quote:
If not, grab a couple of books, put toghether a solid understanding of the most basic aspects of thermodynamics (fluid dynamics is rough), then reread this thread. Other people are trying to help you get an accurate understanding of what is happening, and you keep providing spurious counterexamples. |
|
04-18-2003, 06:40 PM | #71 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
I must recant
it is now very clear Graystar knows the words, but not the principles sorry all Graystar - stop posting 'till you sort it out (you will come out better so) |
04-18-2003, 06:50 PM | #72 | |
Cooling Savant
Join Date: Feb 2002
Location: Oxford University, UK
Posts: 452
|
Quote:
Hey what can I say, I'm a scientist. I'm not ashamed of that. Damnit, where's the blushing smilie gone?!? 8-ball PS, I tried to PM you earlier, but your mailbox was full. Do you not check them anymore?
__________________
For those who believe that water needs to travel slowly through the radiator for optimum performance, read the following thread. READ ALL OF THIS!!!! |
|
04-18-2003, 06:54 PM | #73 |
Cooling Savant
Join Date: May 2002
Location: Da UP
Posts: 517
|
Smoking???? This guy's hooked up straight to the IV man. I want to know if he does tarrot cards and palm reading on the side Oh wait, I think I just reached equalibrium, now if I could only down more beer than I piss.....
|
04-18-2003, 06:56 PM | #74 | |
Cooling Neophyte
Join Date: Jan 2003
Location: OR/CA/NY
Posts: 81
|
Quote:
|
|
04-18-2003, 07:12 PM | #75 |
Cooling Savant
Join Date: Feb 2002
Location: Oxford University, UK
Posts: 452
|
stop it, your making me laugh too loud, and everyon else in the flat is asleep.
8-ball
__________________
For those who believe that water needs to travel slowly through the radiator for optimum performance, read the following thread. READ ALL OF THIS!!!! |