Default Common pump P-Q Curves (graph inside)

I was bored this am, and decided to search the web and dig up P-Q curves for the most common wcer pumps used/sold today. I got the curves from the following places:

Hydor L20 and L30: http://www.cooltechnica.com/images/H...30_PQ_Data.pdf
Eheim pumps: http://forums.procooling.com/vbb/att...=&postid=44918
Sicce Idra: http://www.sicce.co.uk/Idragra.gif
Via Aqua 1300: http://www.wcaquatics.com/cgi-bin/it...aqua_pump.html

A note: The Via Aqua 1300 numbers as reported in their table do NOT result in a normal P-Q curve. I suspect that the max head of the the 1300 is much closer to 5 feet than to 6, and that the numbers are not exactly correct. I'used the P-Q curve provided on that page rather than the numbers in the table. It lists max flow of 400 GPH rather than the 370 reported by other vendors.

Another note: I just read representative points off the graphs and then used them to make a crude P-Q curve of my own. They obviously may be off by a few %.

Anyway, here goes:
Attached Images
File Type: jpg pumpcompare2.jpg (59.6 KB, 1562 views)
pHaestus is offline   Reply With Quote
Unread 11-27-2002, 12:05 PM   #2
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

An addendum:

Some of these pumps (Sicce, Via Aqua, Hydor) are typically used submerged but also will work inline. I do not know the exact conditions of the testing; I just reproduced the curves on a single graph.
pHaestus is offline   Reply With Quote
Unread 11-27-2002, 12:27 PM   #3
g.l.amour
Cooling Savant
 
g.l.amour's Avatar
 
Join Date: Mar 2002
Location: on da case
Posts: 933
Default

another one for in the WC encyclopdedia
__________________
yo soy un tiburón
g.l.amour is offline   Reply With Quote
Unread 11-27-2002, 12:54 PM   #4
Albigger
Cooling Savant
 
Join Date: Sep 2002
Location: ohio
Posts: 140
Default

nice work, a definate asset. have you been able to find any P-Q curves of the Danner Mag drive pumps? (specifically model 7)? I only found some rough numbers, from which BigBen made a small graph in another thread somewhere.

I was just wondering if you happen to come across any, because I couldn't find that information anywhere else
Albigger is offline   Reply With Quote
Unread 11-27-2002, 04:02 PM   #5
FRAGN'STIEN
Cooling Savant
 
FRAGN'STIEN's Avatar
 
Join Date: May 2002
Location: Rathdrum, ID
Posts: 380
Default

Some great info pHaestus, thanks, but shouldn't it read:

flow (GPH) instead of flow(GPM)?

I don't know about anyone else, but my Ehiem 1048 will not produce 9600 GPH
__________________
**This space for rent**
FRAGN'STIEN is offline   Reply With Quote
Unread 11-27-2002, 04:35 PM   #6
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

yes it's true. Should read GPH not GPM. I set everything up in Excel so I could also do SI; then didn't pay enough attention to the units in graph. I don't think I can edit that graph as I added it as an attachment. I'll make a new graph and attach again shortly.

Still haven't found Danner numbers yet.
pHaestus is offline   Reply With Quote
Unread 11-27-2002, 05:07 PM   #7
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default Two birds with one stone

Found Danner info here:

http://www.dannermfg.com/hamptonwate...its/pumps.html

And added the 250gph (Mag2) and 350GPH (Mag3) to list.

It's getting pretty busy now...
Attached Images
File Type: jpg pumpcomparbig.jpg (60.1 KB, 1316 views)
pHaestus is offline   Reply With Quote
Unread 11-27-2002, 05:16 PM   #8
bigdawginva
Cooling Savant
 
Join Date: Oct 2002
Location: VA
Posts: 104
Default

Awesome work. Had no idea the Danner's faired so well. Perhaps an intersecting wattage line as well.

Great work and thank you!
bigdawginva is offline   Reply With Quote
Unread 11-27-2002, 05:24 PM   #9
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

It's REALLY hard to know how much variability there might be between pumps. Plus mfgrs sometimes overstate performance (see C/Ws at www.thermaltake.com for more info).

I suspect the Danners pull more watts than the others I seem to recall my model 2 being around 25W.
pHaestus is offline   Reply With Quote
Unread 11-27-2002, 05:36 PM   #10
Joe
The Pro/Life Support System
 
Joe's Avatar
 
Join Date: Dec 1999
Location: Denver, CO
Posts: 4,041
Default

Wait!!! you mean there is something mis stated or incorrect on the web?!?! NOOO! Someone needs to get on this, I am calling the FBI right now since obviously some hax0r has changed the numbers on them... cause no one would ever lie on a [W]ebsite.

hehehehe
__________________
Joe - I only take this hat off for one thing...

ProCooling archive curator and dusty skeleton.
Joe is offline   Reply With Quote
Unread 11-27-2002, 05:39 PM   #11
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

Well there is just SO much potential variability. Someone told me that they had their heatsinks tested by several different labs, and that they came back with C/W from 0.2 to 0.6. And those were all professional testing labs.
pHaestus is offline   Reply With Quote
Unread 11-27-2002, 05:44 PM   #12
bigdawginva
Cooling Savant
 
Join Date: Oct 2002
Location: VA
Posts: 104
Default

My apologies if I hit a nerve.

I assumed all the pump manufacturers (and others) embellished approximately the same.
bigdawginva is offline   Reply With Quote
Unread 11-27-2002, 05:48 PM   #13
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

Well they may. It is a reasonably straightforward measurement I would think, and so perhaps the numbers are all right on.

But I think people are (reasonably) skittish about mfgr performance claims. Industrial pumps undoubtedly have standards for such, and I would expect the curves for the mfgrs who also make higher end pumps to be pretty reliable. Not so sure about the "hobby pump" makers though.
pHaestus is offline   Reply With Quote
Unread 11-27-2002, 06:57 PM   #14
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

nice compendium pHaestus

some unquantified opinion based on bits and pieces:

from a European mfgr, pretty much on
from US mfgr for industrial (small pump) apps, pretty much on
from US mfgr for 'hobby' market, very variable (some correct, others smoke)
from Japan, spot on
from China, whatever they chose to say
BillA is offline   Reply With Quote
Unread 11-27-2002, 08:08 PM   #15
Joe
The Pro/Life Support System
 
Joe's Avatar
 
Join Date: Dec 1999
Location: Denver, CO
Posts: 4,041
Default

Wow I didnt know accuracy knew country borders... I thought it was more a per company thing
__________________
Joe - I only take this hat off for one thing...

ProCooling archive curator and dusty skeleton.
Joe is offline   Reply With Quote
Unread 11-27-2002, 08:47 PM   #16
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

no, its a fraud penalty thing

the EU will levy fines,
etc
BillA is offline   Reply With Quote
Unread 02-23-2003, 07:31 PM   #17
psychofunk
Cooling Savant
 
Join Date: Jan 2003
Location: Los Angeles
Posts: 365
Default

I can't remember who or where other then in these forums but this graph was posted. He said he ran the water through 1/2" ID tube to come up with it. What if you guys did the same thing for each pump and started a database.
Attached Images
File Type: jpg pump_curves.jpg (64.0 KB, 1228 views)
psychofunk is offline   Reply With Quote
Unread 02-23-2003, 11:11 PM   #18
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

Quote:
Originally posted by psychofunk
I can't remember who or where other then in these forums but this graph was posted.
http://forums.procooling.com/vbb/sho...5&pagenumber=2
Reduced to a link.in edit.
Les is offline   Reply With Quote
Unread 07-02-2003, 08:12 PM   #19
sevisehda
Cooling Savant
 
Join Date: May 2003
Location: NY
Posts: 234
Default

I need to get a new pump as my old one is dieing(or at least making plenty of noise). The cheapest pump I've seen is a VIA AQUA for 18.49. But the stores min online purchase is 30$ so sshould I either get 2 VIA AQUA 1300's for 37$ or get a Danner Mag3 for 36$.


Also I know theroretically 2 pumps in series is double the pressure and 2 in parallel is double the flow. But in the REAL world more double the pressure actually means double the possible head so flow would actually increase. And for parallel doubleing the flow would actually create more resistance which would decrease flow. Not even taking into account that its not actually 1 + 1 = 2 but6 slightly less. The previsous period is confusing I know but so is the math behind it. Does anyone have any formulas or rules of thumb for calculating flow using multiple pumps? Thanks for any help.
sevisehda is offline   Reply With Quote
Unread 07-02-2003, 08:39 PM   #20
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

You could simply spend $30 on the Johnson pump .

Otherwise, I believe you'll find about 85% of the total pressure that you expected.
bigben2k is offline   Reply With Quote
Unread 09-03-2003, 03:15 PM   #21
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default update with new swiftech pump



Click for larger image.

I should note I am using 3.785L/gallon and 0.3048m/foot in all corrections (should you want the numbers for conversion).

Does anyone know how that sites like this: http://stats.zerothelement.com/cgi-b...led.pl?Id=4562
generate graphs on the fly from text data? It would be really sweet to be able to graph all of these P-Q curves on the fly rather than on this single graph that is getting pretty busy.
pHaestus is offline   Reply With Quote
Unread 09-03-2003, 06:38 PM   #22
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

-

Last edited by Les; 09-03-2003 at 07:48 PM.
Les is offline   Reply With Quote
Unread 09-03-2003, 08:17 PM   #23
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

Les: It's from the mfgr specs and is as good as their word. Bill has some pretty good evidence that the Eheim P-Q curves are a bit optimistic. Of course he's also a mfgr now too and subject to the same suspicions right? I personally think the Via Aqua numbers are bogus for sure (as mentioned above).

But hey we have to start somewhere right? Of interest to me is the apparent dominance of a relatively inexpensive pump (Danner Mag3) and the high head performance of Swiftech's new entry.
pHaestus is offline   Reply With Quote
Unread 10-01-2003, 09:41 PM   #24
Got KarmA?
Cooling Neophyte
 
Got KarmA?'s Avatar
 
Join Date: Jun 2003
Location: Too far from Canada ...
Posts: 95
Default

hmm, no iwaki's or eheim 1060 ...

beggars can't be chosers I guess
Got KarmA? is offline   Reply With Quote
Unread 10-09-2003, 11:19 AM   #25
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

Graph updated today to reflect newer P-Q curves for MCP600 from Bill.

I can't include many more pumps without ending up with a graph noone can read...
pHaestus is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 09:15 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...