BillA 11-29-2004 01:52 PM

the plastic pump housing capability, nothing to do with the pump itself

Nicepants42 11-29-2004 03:35 PM

I've found Cathar's post Here to be very informative - although I'm not 100% up to speed on the math.

I eyeballed this pumps performance curve, used Cathar's math, and came up with the following:

~4.7lpm flow rate, 0.174 C/W at the block, 0.0435 C/W at the radiator. As for heat added to the water, I pulled 5W right out of my ass and crunched the numbers:

17.4C rise from the CPU, 105*0.0435 = ~4.6C rise from the pump, to give a total of 22.0C delta between the CPU die and ambient.

This would mean that this pump is at best slightly better than a Eheim 1250 in this situation (giving 0.1-0.2C for a pulling-out-of-ass factor).

Anyone want to have a more accurate crack at it?

BillA 11-29-2004 04:32 PM

sure the numbers are fun, any correlation with real-world data ?
i.e. is this useful ?

I know that you think you know, but has it been verified ?
- pressure and temps across a system in operation
other than the theoretical in Dave's article, I have not seen such data

lolito_fr 11-29-2004 04:40 PM

Quote:

sure the numbers are fun, any correlation with real-world data ?
Am considering playing with numbers for the Swiftech kits -
may I ask what length of pipe is used on the bench when establishing the system C/W's ?

Nicepants42 11-29-2004 05:02 PM

2 meters of 1/2" ID tubing, like it says in Cathar's original post that I linked to.

BillA 11-29-2004 05:03 PM

hose lengths not strictly limited, a 'tight' system might have 4' - an external rad to 6' or so

I am presently trying to setup to monitor a complete system but I lack some addl instruments - and data lines
- workin' on it

flatline 11-30-2004 04:28 AM

found 1


looking into geting 1 just dont like the whole 3/8's thing

lolito_fr 11-30-2004 04:49 AM

Quote:

dont like the whole 3/8's thing
why? 3/8 or 1/2 not gonna make any difference with this pump:)
and another

flatline 11-30-2004 05:42 AM

just got a 1/2 system made but maybe i can use it regardless (thows reduser thingys)

tnx 4 cheeper link :D

Jag 12-01-2004 07:18 AM

In the Swiftech MCP350 web page, the picture of the DDC is the version 1, but the performance graph is of the DDC version 2, right?
So, is Swiftech selling the version 1 with a "wrong" graph, or the other way around, a correct graph with a "wrong" picture?

Uncle`BuZZ 12-01-2004 08:12 AM

there is no V2 in fact, and swiftech have the graph for what you name V1 (less than 6 lpm so less than 360 l/h)

Jag 12-01-2004 08:35 AM

But these two graphs aren't the same:
http://www.thermal-management-testin...curve%20SI.gif
http://www.swiftnets.com/assets/imag...%20sm%20SI.gif

Are we talking C-Systems dynasty here?
Who can we trust?

Edit: The MTBF value of 50.000/h still stands if you operate this pump at 13,2v?
Anyone?

Uncle`BuZZ 12-01-2004 08:57 AM

1 lpm = 60 lph
6 lpm = 360 lph

I read same results on both, units are different but results are equals.

Maybe the different max flow rates are the cause of your mistake ? the second curve seems to be more "compact", but max flow rate is 480 lph and it is only 400 on first graph.

BillA 12-01-2004 08:58 AM

not your ability to read, or reason - that much is clear
Excel rounds 0.5 to 1, as in the vertical axis of the small graph

you are a fool Jag, try again

version 1, version 2 - where is thes crap coming from ?
Europe ?
there is only one version of the DDC sold in the US (only the case and or wiring may vary, pumps all the same)

Jag 12-01-2004 09:01 AM

The "version 2" comes from the *.pdf that Laing released with a new pump casing.
In case yo don't know it's here: http://www.laing.de/10Produkte/40Pum...DC/00index.htm

Don't call a fool without any proof.

Here's the revised performance graph that Laing released:
http://www.laing.de/10Produkte/40Pum...leichDDC/3.gif
So??

Uncle`BuZZ 12-01-2004 09:04 AM

BillA, Rosco put on cooling-masters a link where ou can find a PQ curves from Laing with a ma flow rate of 570 lph instead of the 350 lph you and Rosco measured.

His body is also different (fixations) so we believed there is a new version of the pump. In fact the old PQ curve is extrapoled over 270 lph, and new PQ curve is a full measured results from Laing.

Rosco is waiting for some answer because you and him have same results and it correspond to the old PQ curve

EDIT : the link http://www.laing.de/10Produkte/40Pum.../GleichDDC.pdf

BillA 12-01-2004 09:11 AM

my data is from Laing, let us hope that the same info is being given to all
I would not presume to use my test data to describe the Laing pumps, these people are quite competent to characterize pumps

I would add that this technical data is formally transmitted from Laing to Swiftech
but I will confirm the DDC PQ curve - will post any results

Rosco (Roscal no ?) should be able to confirm this kind of stuff too ??

Edit
looked at the link and now I am quite as confused as all of you
the pump shown is what Swiftech is shipping
I have never seen that curve before
WTF ?

EDIT
yes Jag, pointing out the difference is valid

Jag 12-01-2004 09:16 AM

This "revision" has been out for days now on the Laing web site.
Strange how it appears to be new info for some.

BillA 12-01-2004 09:17 AM

you are not the center of the universe ?

Jag 12-01-2004 09:18 AM

No Bill, if I were, i would call fool to a lot of people...

BillA 12-01-2004 09:21 AM

post #162 is your foolish badge

Jag 12-01-2004 09:25 AM

No, I inserted the wrong graph, then when I noticed and was going to correct it, the posts started to come and i decided to maintain it, and inserted the correct graph on the following post.
O.K?

BillA 12-01-2004 09:34 AM

better to have cleaned it up
the comparison to C-Systems is your bias, showing up on a recurring basis

"Who can we trust?"
get stuffed

Jag 12-01-2004 09:41 AM

Quote:

Originally Posted by unregistered
the comparison to C-Systems is your bias, showing up on a recurring basis

??
Care to demonstrate that?

BillA 12-01-2004 10:51 AM

ok, the European brochure is wrong - all disclaim knowledge of how this happened (to me)
the brochure will be changed

there is NO version 2

still no clue as to who can be trusted ?
get stuffed

Roscal 12-01-2004 11:02 AM

There's no version 2 in fact, they only added external fix on the body as a little improvement.

I don't know what the matter with graph but their 570L/h are impossible to achieve @12V with my test, for sure ! I mailed Ralf from Laing to know exactly the conditions of their test because, as usual, a lot of data are missing (voltage?).

Here's his first mail to my question about these strange 570 L/h today :

Quote:

Hi David,
About the flowrate:
Before we used the pump curve for the requirements of Delphi (we stopped measuring at the 270 l/h), now we measured to the maximum characteristics, that's what we'll use for the end customer market.
Is maximum characteristics refer to 13.2 V, I don't know it's not clear...

Bill I'm waiting your test, it take a couple of minutes to confirm or not.

DDogg 12-01-2004 11:04 AM

Quote:

Originally Posted by unregistered
not your ability to read, or reason - that much is clear
Excel rounds 0.5 to 1, as in the vertical axis of the small graph

you are a fool Jag, try again

version 1, version 2 - where is thes crap coming from ?
Europe ?
there is only one version of the DDC sold in the US (only the case and or wiring may vary, pumps all the same)

- Jeez Bill, seems like you are transitioning from the 'lovable grippy old curmudgeon' to being just downright mean spirited. Gee whiz!

BillA 12-01-2004 11:28 AM

no, "lovable" is not an adjective normally associated with me (that's your thing)
my fuse is pico-seconds when compared to other vendors

Roscal
Oliver is aware of the graph and it is being pulled - period
so the quotation seems strange to say the least

would test but the bench is tied up with rads and the second not yet assembled
more than a bit overloaded here

Jag 12-01-2004 12:10 PM

Quote:

Originally Posted by unregistered
ok, the European brochure is wrong - all disclaim knowledge of how this happened (to me)
the brochure will be changed

there is NO version 2

still no clue as to who can be trusted ?
get stuffed

Bill, no wild guesses and/or clues; convictions (trust?) result from firm actions and facts.
Some kind of answer was needed. You took the kind of (re-)action Swiftech consumers, WC community and resellers nedded.

As you surely realise, this market (WC) and in particular WC pumps doesn't have a lot of good references to sustain its credibility. So, one couldn't afford to loose this one.
Nevertheless, Laing's move wasn't a smart one («all disclaim knowledge of how this happened (to me)»).

get stuffed

Roscal 12-02-2004 11:51 AM

Some news about the 570L/h mystery.

Mail from Laing :

Quote:

Hi David

Now it gets a little bit difficult for me to explain the “mystery” about our pump curves, even because I’m not a technician.

The curves that you measured are correct, but our curves are correct too. That is to trace back to the fact that we use different test facilities and test methods.

To get the max. flow at no resistance, you have to compensate the resistance of the measuring facility itself. Also you have to use a second pump in the system to neutralise the system resistances. If you work accordant to this process, you will measure also the 570l/h, as we did it.

If you compare some duty points of the actual curve and the former curve you won’t find too many differences.

David, I hope I could clarify the differences in the measuring methods, even if I have the opinion that we will not work in the area of 5 to 15 kPa, because the resistance of the coldplates, the tubes and other components of the cooling system will be higher. What`s your opinion?
It could be 2 DDC in parallel and 570L/h could be the result, but it's a strange method again... I ask him some pics/diagrams of their test bench to have more precise info because he don't know really the procedure as he said...

Thoughts?


All times are GMT -5. The time now is 11:26 AM.

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...