Gooserider 08-08-2003 02:33 AM

Am I estimating my airflow needs right?
 
I have been working on figuring out the cooling reqirements for the system I'm working on, and want to see if there are any obvious problems with the way I'm doing it.

I am water cooling the all the major heat producers in the system. The radiator will be mounted in the front of the case, with the fans behind it sucking through the radiator, and dumping into the case. The air will then pass through the case and exit out the back. To control the airflow and contain the noise, I intend to seal all case openings other than the radiator and the 3 fan outlets on the back of the case.

Some of the 'radical coolers' I've talked to don't think sending the air from the rad through the case is a good idea, but I don't think it will hurt anything since the figures I've seen say air only gets warmed 2-3*C max on its way through a WC rad. I don't see that as a significant diference from ambient.

For the purposes of making my estimate, I am trying to be very conservative. I think it is better to estimate to high and have to turn fans down / off, rather than not having enough cooling power available when it's needed.

I am making two assumptions, 1. That all the heat to be dissipated will be coming out of the radiator (I know it's false, but it makes the numbers much easier...) 2. That my maximum allowed temperature rise in the rad is 10*C. (I probably could get away with a bigger Delta-T, but that's part of being conservative

My heat budget is as follows:

2 X CPU @ 100W = 200W
1 X pump @ 50W = 50W
4 X HDD @ 18W = 64W
1 X FGF @ 100W = 100W (FGF = Fudge and Growth Factor :wink: )
----------------------
Total Heat out = 414 W

According to the NMB website, to calculate required air flow, one uses the following formula

required CFM = (1.7 X Watts) / max allowed Delta-T *C

or

required CFM = 1.7 X 414 / 10 = 72.4 CFM

Does this seem like a valid figure?

Gooserider

bigben2k 08-13-2003 10:17 AM

Got a link?

The formulae can only apply to a specific model of core, no?

Since87 08-13-2003 11:38 AM

Re: Am I estimating my airflow needs right?
 
Quote:

Originally posted by Gooserider


According to the NMB website, to calculate required air flow, one uses the following formula

required CFM = (1.7 X Watts) / max allowed Delta-T *C

or

required CFM = 1.7 X 414 / 10 = 72.4 CFM

Does this seem like a valid figure?

I suspect (haven't worked it out) that the equation from the NMB website refers to the Delta-T between incoming air temperature and outgoing air temperature.

My impression is that you might be treating that Delta-T as if it is the differential between the water temperature and the air temperature.

These are significantly different issues. The water temperature will be somewhat higher than the temperature of the air exiting the rad.

CoolROD 08-18-2003 11:20 AM

If you put 414W into your rad and 72.4 cfm air at 100 kPa 22Deg. C

Your exit air temp will be 32.2 deg C or 90 Deg F

I will be glad to discuss this.

The delta T (air temp) was 10.2 deg. C

My assumption was the same as Since87's so I checked it...

Gooserider 08-18-2003 01:51 PM

Hmmm... Interesting!
 
There was an article either here or on Overclockers that said the temp change for air going through a WC rad would be 2-3* C max, based both on math and actual measurments.
I believe the reasoning was based at least in part on the idea that thermal transfer takes time, and the air wouldn't be spending long enough passing through the rad to do the complete heat transfer.

The article was by BillA, or one of the other senior cooling gurus, so I'm inclined to believe he knows what he's talking about...

One of the ideas I've had, is that since I'm using a single pass rad (FedCo 2-342) there will be a significant temp. gradient between the inlet at the bottom, and the outlet at the top. Per heat xfer laws, the greater the temp difference, the more heat will be transferred. Since I'll be using two fans in parallel, the lower fan will get hotter air than the top fan, so why not duct it out the bottom of the case? This would keep the worst of the heat load from getting blown back through the case.

Gooserider

t00lb0x 08-18-2003 02:55 PM

Quote:

Originally posted by CoolROD
If you put 414W into your rad and 72.4 cfm air at 100 kPa 22Deg. C

Your exit air temp will be 32.2 deg C or 90 Deg F

I will be glad to discuss this.

The delta T (air temp) was 10.2 deg. C

My assumption was the same as Since87's so I checked it...

Would you please elaborate on this forumla. Or at least show the formula. That would be really, really helpful.

CoolROD 08-18-2003 02:59 PM

Sure, I will post a spreadsheet tonight that anyone can use.
Do you have Excel?

Since87 08-18-2003 03:01 PM

Re: Hmmm... Interesting!
 
Quote:

Originally posted by Gooserider
There was an article either here or on Overclockers that said the temp change for air going through a WC rad would be 2-3* C max, based both on math and actual measurments.
I believe the reasoning was based at least in part on the idea that thermal transfer takes time, and the air wouldn't be spending long enough passing through the rad to do the complete heat transfer.

Find the article and see what heatload that 2-3°C figure was based on.

I'll bet it wasn't 414 Watts.

t00lb0x 08-18-2003 03:03 PM

Quote:

Originally posted by CoolROD
Sure, I will post a spreadsheet tonight that anyone can use.
Do you have Excel?

Yes I do, could you please post it. Thanks a lot (i'll have to save it because its helpful.)

Since87 08-18-2003 03:04 PM

Quote:

Originally posted by CoolROD
Sure, I will post a spreadsheet tonight that anyone can use.

That would be great. I tend to avoid doing these calculations because of all the conversions that need to be looked up.

t00lb0x 08-18-2003 03:48 PM

Yeah but it would be good just to know it in the first place. Formulas are always helpful, wait, they should have a thread of all the equations that could be used. Like C/W, airflow, and stuff like that.

CoolROD 08-18-2003 03:59 PM

I am starting a new one tonight. The first post will relate total watts dissipated from the radiator, cfm, and the temperature change of the air through the radiator. Keep in mind that this has all been covered before, but is burried in the forum.

t00lb0x 08-18-2003 03:59 PM

Yeah but having it in one place would be helpful to noobs like me.

Zhentar 08-18-2003 04:07 PM

There's a flaw in your heat calcs- the pump/HDs will not make 114 watts of heat. Most of this energy is converted to kinetic energy moving either the water or platters.

I'm guessing 250W would be much more realistic, and thats including growth factor.

CoolROD 08-19-2003 12:12 AM

I have uploaded the work that relates airflow to temperature rise through a radiator. Since I have to host the information, I am going to hold off on creating a new thread for formulas and spreadsheets until I complete more of them.

This example assumes no pressure drop across the radiator. This is not true, but the pressure difference is insignificant and I will do the thermo the hard way to prove it. I am doing this for myself anyway, b/c I want to model my whole system.

Here is an example of the work. You can launch the excel spreadsheet from the link at the top of the page -or- click here.

edit: let me know if that is what you wanted.
The variables are kind of messy b/c I haven't found the right ones in Excel yet.

t00lb0x 08-19-2003 12:14 AM

Thanks man! I've been waiting for this.

CoolROD 08-19-2003 12:21 AM

No problem -That was an instant response! I hope it is not too messy. I am sure it will look terrible when I critique it tomorrow!

t00lb0x 08-19-2003 12:22 AM

Yeah, it was quick, I have been waiting for this almost all day (sad...) That looks pretty good and it makes sense. So if you can improve on that, that is pretty impressive.

Solarian League 08-19-2003 02:16 AM

ouch! i'm looking at 10-15 degree increase in my delta

enter temp is 22c and my watt load is about 660 which yields an exit temp of about 35c

ouch

Les 08-19-2003 03:00 AM

Some sums previously shown in a "Water Cooling Simulator Discussion" thread http://forums.procooling.com/vbb/sho...5&pagenumber=4

http://www.jr001b4751.pwp.blueyonder.co.uk/Air1.jpg

Gooserider 08-19-2003 03:15 AM

Some reference stuff...
 
Quote:

Since87: quote: Originally posted by Gooserider "There was an article ... that said the temp change for air going through a WC rad would be 2-3* C max..." Since87: Find the article and see what heatload that 2-3°C figure was based on. I'll bet it wasn't 414 Watts.
Well, I've been searching, haven't found it yet, but here are some other things I found on Overclockers that appear relevant...

"Radiator System Resistance" This is the source for my assumption of 50% of rated fan performance.

"Pump-Off"
Commentary on the influence of system resistance on waterflow from pumps. (Note that I'm designing for a comparatively high flow volume.)

"Waterblock Bench Testing Results"
Discussion of waterblock testing.

"Water Cooling Flow Rate and Heat Transfer"
Zhentar, see the bottom part of this one, it addresses your comment about pump heat. (sorry, you got it wrong...)

"Measuring Airflow Resistance"
An interesting background peice on how airflow resistance is measured.

"Radiator Heat Dissipation Testing"
This is a primary info source, though a bit dated. It does it's measurements in BTU's, and I forget offhand how they xlate into Watts, but an interesting read. In terms of the rad that I'm using vs. this article; my rad is bigger than either the Serck or the Big Momma. It is the same type of construction as the BM, but is a single pass design which gives it low flow resistance like the Serck. Some crude testing w/ just the rad shows my pump can push about 6GPM through it, showing ~6' of head loss, out of a rated 14' head and 8 GPM flow )

It might also be worth reviewing the Water Cooling Simulator Discussion message area here on Pro-Cooling, there is alot of good info there.

Gooserider

Since87 08-19-2003 06:21 AM

Quote:

Originally posted by CoolROD

This example assumes no pressure drop across the radiator. This is not true, but the pressure difference is insignificant and I will do the thermo the hard way to prove it. I am doing this for myself anyway, b/c I want to model my whole system.

In what sense is pressure drop across the radiator insignificant? (In terms of power dissipated due to the flow through it?)

I haven't had a chance to look at the spreadsheet. (Computer is under construction and doesn't have Excel ATM. Will take a look when I get to work.)

How about posting your simulation work in the Water Cooling Simulator Discussion forum? It will make it easier to find at a later date. BTW, you can attach small files to your post, (like a zipped spreadsheet) if long term hosting is problematic.

Since87 08-19-2003 06:42 AM

Re: Some reference stuff...
 
Quote:

Originally posted by Gooserider

"Water Cooling Flow Rate and Heat Transfer"
Zhentar, see the bottom part of this one, it addresses your comment about pump heat. (sorry, you got it wrong...)

Yes, all the power going into the pump in a closed loop system exits the pump as heat. (The proportion that exits through the pump casing and through the water will vary depending on the system.) Only in a system where water is pumped from one location to another, is power exiting 'the system' in the form of kinetic energy.

CoolROD 08-19-2003 07:09 AM

Quote:

Originally posted by Since87:

In what sense is pressure drop across the radiator insignificant? (In terms of power dissipated due to the flow through it?)
The maximum pressure generated by the fan is only around 1" W.C. or .036 PSI. For comparison: the atmosphere we are working in is 407" W.C. or 14.7 PSI. In this context, the temperature change of the air due to the change in it's internal pressure is small. I said that I am going to figure this the hard way (which includes the air's internal pressure drop) to validate this. I am trying to make the math easier...

This is actually irrelevant -What is important is that I am assuming "Constant Specific Heats" for air at room temperature. This is acceptable for the range of -20 to 70 Deg C with an error of less then 1/2 a percent.

edit:
Quote:

Originally posted by Since87:

(In terms of power dissipated due to the flow through it?)
This is a little vague...please take a look at my post when you get your computer running...and tell me what you are asking. ;)

CoolROD 08-19-2003 07:16 AM

I might post in the "Water Cooling Simulator Discussion" when I get some more significant relations completed. This is toy stuff and probably the easiest model in thermodynamics (Constant Pressure, Ideal Gas, etc.) Some people here wanted to use it -so I put it here.

Now I have to figure out this "attachment thing" with a post...


All times are GMT -5. The time now is 11:41 PM.

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...