One would actually want to quantify the heat load entering the cooling loop, without estimates, before making a statement as to the C/W.

Would need approximately ~165CFM at the least to reach a 0.01 C/W, and that presumes 100% radiator efficiency.

The fans may be 44CFM each, but unlikely that they'd be pushing that much air-flow through the 1.75" thick radiator.

Still, what you're proposing is potentially possible, but I'd still want to know what the actual heat load is before I believe it to be anything more than a guess.

Still, when it comes to radiators, surface area rules all, and you've definitely shown that to be true.