Quote:
Originally Posted by Cathar
Was referring to data that you know that I don't have the permission to publish......
Said data projected a unit thermal resistance lower than that of the inherent thermal spreading resistance of the copper in the unit.

Just wanted to make that point clear before leaving this.

Cathar, not according to my analysis.
When R=C/W
where W=total heat dissipation through all of IHS
C= Local IHS Temp-Coolant Temp
which is the definition used for TTV testing in July 2005 pdf
W distribution will depend on heater/heat-die dimensions and thermal characteristics and to a,probably, lesser extent the cooling properties of wb.
The case Post133 illustrated was a uniform flux 1x1cm die with 0.33x0.33mm Local area Temp(width of groove 0.33mm)
For 270,000w/m^2c on 14.4x14.4x1mm case
A tapered Flux Channel 14.4x14.4mm >0.33x0.33mm
Cu Resistance=Total Resistance- 1/h(eff)A =3.57949 -0.017861=3.561628775 c/w (Waterloo
This resistance with reference to a 0.33x0.33mm area
Translated to 1sq cm ref area this is 0.003879 c/w
This a major part,but not all, of the total Resistivity of 0.003898c/w/cm^2

Edit Corrected pdf date to 2005