I used the basic program to run a few numbers.
First:
Quote:
The flow range to be covered is determined by the nozzle diameter. In order to have better resolution, the maximum flow should be near the 3.0+ inches w.g. range in differential pressure. ... If the differential pressure is below 1 inch w.g., select a smaller nozzle. If the differential pressure exceeds 4.0 inches w.g., select a larger nozzle or combination of nozzles.
|
(from
fantester)
so 1" is min, and 3" is max.
Using the program, I calculated the following flow rates:
Code:
DIAMETER Flow at 1" wc Flow at 3" wc
0.75" 11.8cfm 20.5cfm
1" 21.5cfm 37.5cfm
1.25" 33cfm 57cfm
1.5" 48cfm 83cfm
1.6" 54cfm 94cfm
2" 85cfm 147cfm
2.5" 133cfm 231cfm
3" 192cfm 333cfm
Nozzles listed are from the standard size list from
Helander.
Back Monday.