better to multiply your s&m 140W by 0.7 to address secondary path losses
and the "C/W" would be 0.217 or so
this all relates to the CPU/coolant temp differential

then you need to do so for the rad (Since87 added the wb "C/W" and the rad C/W)
and it is not the room temp that is the baseline, but the air temp through the rad - generally a bit higher

but yes, you have the idea