#1 |
Cooling Savant
Join Date: Sep 2004
Location: Los Angeles, Ca
Posts: 310
|
![]()
I am in the process of building a psuedo die simulator and I was wondering what would be the best heat source. I have seen alot of ppl reccomend the heater cartridges, but the ones that I have seen are all AC and i dont particularly like dealing with 120V AC.
I have also gotten reccomendations to use a TEC, but I have my doubts as to how accurate this method would be. If anyone has any suggestion as to either side of this matter please say so.
__________________
Excuse me, I believe you have my stapler. |
![]() |
![]() |
![]() |
#2 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]()
You can use DC on an AC unit, just don't exceed the current rating.
|
![]() |
![]() |
![]() |
#3 |
Cooling Savant
Join Date: Sep 2004
Location: Los Angeles, Ca
Posts: 310
|
![]()
Well it seems the tooth fair has solved my problems anyway.. lol.
but still its a good question. u can put AC into the heater as well as DC? so it doesnt matter which you use? the only thing is that the heater is rated for 120v... 120v dc is just as nasty as AC.
__________________
Excuse me, I believe you have my stapler. |
![]() |
![]() |
![]() |
#4 |
Cooling Savant
Join Date: Oct 2004
Location: Sunny Florida
Posts: 246
|
![]()
actually DC is worse - AC current will knock you away from the source but DC will do the opposite, in fact just 50 mAmps (.05 Amps) can kill you
also i don't think that it's the same thing and is not safe to run DC on an AC circuit Last edited by jman1310; 04-12-2005 at 03:02 AM. Reason: clarification |
![]() |
![]() |
![]() |
#5 | |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]() Quote:
you will need a 100V 3A psu for 200W, ~75V 2A for 100W use a shunt @ 30% of rating to measure current cal everything |
|
![]() |
![]() |
![]() |
#6 |
Cooling Savant
Join Date: Sep 2004
Location: Los Angeles, Ca
Posts: 310
|
![]()
I will be using a multiple shunt system so that I can run it at full voltage the entire time with a range of 100 to 350watts. I see no reason to go over 350watts as it is not realistic. a prescott core with dual 6800's overclocked to the moon should get somewhere close to 350watts heat dump but nothing over it.
Even though all shunts will be at full voltage and their rated capacityies I will be using a clamp meter to measure the wattage and measuring the voltage on each just to make sure that everything is working properly and at the heat range i want.
__________________
Excuse me, I believe you have my stapler. |
![]() |
![]() |
![]() |
#7 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
so why on earth are you adding the GPU heat load to the CPU sink/source ?
you need to think on what you are setting up for cal the shunt at its use temp running a shunt at over 30% will cause progressively more self-heating -> changing the resistance you should engage in conversation with Lee Garbutt use his system as your guide if you do not wish to use professional equipment a clamp-on meter ! wheeeeee BTW, this is ALL dangerous, particularly for the uninformed if you are not comfortable, and proficient, at working with electrical circuits -> DON'T DO SO Last edited by BillA; 04-12-2005 at 01:48 PM. Reason: spflng |
![]() |
![]() |
![]() |
#8 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]()
Excellent tips from Bill, as usual (thanks Bill!).
Yeah, you can use DC on an AC heater cartridge. As Bill stated, figure out the power that you intend to run it at, and check the max current rating of the heater, so that you're still running it safely. I didn't mention the voltage simply because I assumed that you were going to use DC and a relatively moderate power level, so you wouldn't be anywhere near 120 Vdc, which would be the max voltage at which you could safely run the heater. Just pick a cartridge with a wattage rating a bit above your intended power run, with the other advice above. I also didn't mention the other operating limit, temperature, because it's in the 400 dec C and above (far above, sometimes), and really doesn't apply here, unless you goof up (never run a heater without a cooling solution, doing so would damage it, and alter its properties, if it doesn't kill it, colateral damage aside). McMasters.com page 454. |
![]() |
![]() |
![]() |
#9 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
use a phenolic holder
if to run unattended: install temp shutdowns install loss of coolant shutdowns think about all the different ways the system could fail, you will eventually experience most of them coming in at 6AM and seeing a smoking die in a puddle of plastic is distressing |
![]() |
![]() |
![]() |
#10 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
wait a minute
"I will be using a multiple shunt system so that I can run it at full voltage the entire time with a range of 100 to 350watts." this is REALLY dumb, get an adjustable amp, I prefer linear but switchers will work LOOK at Lee's setup you seem hell bent on doing this in the most inaccurate manner possible |
![]() |
![]() |
![]() |
#11 |
Cooling Savant
Join Date: Sep 2004
Location: Los Angeles, Ca
Posts: 310
|
![]()
Bill the multiple shunts wasnt my idea. I will talk to the guy who is building it for me to see if i can just get it with one shunt that is really powerful.
The gpu and cpu is only for radiator testing as most users have their gpu's and cpu's in the waterloop. This wont be used for cpu or gpu waterblock testing. I just need a heatsource. I will prbably just atach a maze4 to it. "cal the shunt at its use temp running a shunt at over 30% will cause progressively more self-heating -> changing the resistance" so you say not to run the shunt at over 30% of its rated voltage??? If that is the caes to get to 350watts I would need about a 1100 watt shunt.. EEK.
__________________
Excuse me, I believe you have my stapler. |
![]() |
![]() |
![]() |
#12 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
shunts are rated for current
stop building at once you are wasting time, effort, and $s you need to figure out what you are about re testing, and not really from me there are several visible individuals doing testing who disclose their equipment if you choose to do something different, without even understanding the BASIS for the equip selection, how do you think you will fare ? I will leave you to Ben who is far ahead of you in terms of his understanding, and he has been at it some time what you are seeking are reasons for not doing something different (dumb ?), you need to test in a simple manner, then progress to more sophisticated setups - if sophistication is not your bag, you'll find little solace for crappy test setups here |
![]() |
![]() |
![]() |
#13 | ||
Thermophile
Join Date: Jun 2001
Location: The deserts of Tucson, Az
Posts: 1,264
|
![]() Quote:
Both will hold you to a wire if you grab it (its not like your muscles can flex open and shut 60 times a second, so you'll stick anyway). If anything AC is maybe worse since it'll have a greater chance of arrhythmia and death by heart attack. http://www.emedicine.com/emerg/topic162.htm Quote:
|
||
![]() |
![]() |
![]() |
#14 |
Cooling Savant
Join Date: Sep 2004
Location: Los Angeles, Ca
Posts: 310
|
![]()
Well clearly Bill has had enough of my questions.
so Ben to get 350watts and below output from one shunt what exactly would i need to get. The actual block used for this is already created by a more knowledgeable individual in this area in myself (he designs cooling systems and is an electrician) so I dont really have any questions on that matter. Just need help with the power source and measuring the output of it. Bill do you have any links to such persons with these setups?
__________________
Excuse me, I believe you have my stapler. |
![]() |
![]() |
![]() |
#15 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
pleeeeze
Lee Garbutt - systemcooling Joe Citarella - overclockers 'Roscal' - cooling-masters (have to read the articles) an ounce of experience is worth a ton of "I think" by those w/o experience "The actual block used for this is already created by a more knowledgeable individual in this area in myself (he designs cooling systems and is an electrician) so I dont really have any questions on that matter. Just need help with the power source and measuring the output of it." if he is an electrician I would stick with him, up or down its on his head I DO have a concern that the electrical part of this is beyond your present experience, keep to your buddy I have 1KW psus that will take a direct short (which I have done !, blew up a switcher though), yours may not |
![]() |
![]() |
![]() |
#16 |
Cooling Savant
Join Date: Sep 2004
Location: Los Angeles, Ca
Posts: 310
|
![]()
Bill, I have several ppl that I can refer my questions to about electrical. stuff. Me EE skills are something that need to be improved on and I have no plans on going about building this thing on my own electrical knowledge.
EDIt: I wont be wiring the shunt, so I couldnt tell you. If it were me doing it i would use some solder, good low resistnace copper wire and some heatshrink.. but thats just me. anyway thanks for the info on them. I read Lee's reviews alot, but was not aware he had a die simulator setup.
__________________
Excuse me, I believe you have my stapler. |
![]() |
![]() |
![]() |
#17 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
MR
sorry, but you are adrift your 350W psu that will run flat out, dropping the 'excess' on a 'dropping resistor' will create ~500W from the psu + ~250W 'excess' that you will be dumping; thats 750W continous being dumped into your 'lab' go get a 750W heater and run it in your lab, but wait - there is more you still have to dump the 100W in your coolant, how is that going to happen ? to air ? -> got a constant temp air source ? (not if you're putting 850W into it, rest assured) back up, get a feel for what your SYSTEM must do that will give you an insight into HOW to do it |
![]() |
![]() |
![]() |
#18 |
Cooling Savant
Join Date: Sep 2004
Location: Los Angeles, Ca
Posts: 310
|
![]()
sigh.... testing is just about the most agrivating experience known to man.
So I ask you, is there a sensible way to get 350watts of heat into the loop other than connecting a prescott and two 6800ultras... As to what I need the system to do. I need a copper block that will output a maximum of 350watts and have the output be measurable with DMM's and Ampmeters. The heat dump into the room can be handled. I can duct the PSU so that it is dumping its heat out the window. As to the heater itself I will insulate it with closed cell foam to stop leakage through the sides of hte heater block.
__________________
Excuse me, I believe you have my stapler. |
![]() |
![]() |
![]() |
#19 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
I do not believe you have started testing yet, much to pass through first
350W ? for rads use a water heater for wbs use a resistor on a copper plate if you want simple, keep it that way |
![]() |
![]() |
![]() |
#20 |
Cooling Savant
Join Date: Sep 2004
Location: Los Angeles, Ca
Posts: 310
|
![]()
hmm. well I was suggested this method I will present below.
take some 20pounds of water heat it to 150F and then run it through the radiator with a pump and measure the temperate at set times and also take count of how long it will take to get to 100F. Then this can be coverted to BTU over time. 20 pounds of water going from 150F to 100F is 100BTU's. So it would be a relatively simple calculation to get the time. also first test how many degrees the water will drop per time from 150F in the bucket used along with the pump hooked up and the tubing used. This would be a constant that you pull out. for instance if it dropped 10F per hour then 200BTU's per hour.. just subtract htat from the BTU's measured for each radiator. Bill pls let me know if you see any holes in this plan. one question. do you know where to acquire a water heater that has a measured heat input into the water? Preferably one that doesnt cost an arm, leg and a baggie of gems..
__________________
Excuse me, I believe you have my stapler. |
![]() |
![]() |
![]() |
#21 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
ok
test the concept with the thermometer of the accuracy that you intend on using, see how uniform is the temp in that 20# of water - cannot be uniform w/o mixing (which adds heat), isn't this fun MR go to an engn prof and talk to him, someone is blowing smoke up your ass I've said my bit |
![]() |
![]() |
![]() |
#22 |
Cooling Savant
Join Date: Sep 2004
Location: Los Angeles, Ca
Posts: 310
|
![]()
fun doenst beging to describe it.. so you stir the water it adds kinetic engergy.. gee how fun is that..
I was thinking the same thing about the uniformity of the water... but it will be pumped hte entire time which will move it arounda bit i think. sigh.... can you elaborate on the blowing smoke up my ass part.. I really dont want to start doing all this testing and then realize that I have a totally fubared test method. getting all the possible error points out of the setup before i start testing is the optimal solution imo.
__________________
Excuse me, I believe you have my stapler. |
![]() |
![]() |
![]() |
#23 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]()
Check eBay for 800 amp shunts; they're there, here's one:
http://cgi.ebay.com/ws/eBayISAPI.dll...tem=5766468739 Here's 1000 amps, with meter: http://cgi.ebay.com/ws/eBayISAPI.dll...tem=7507355711 350 W is a lot of heat power. Are you sure that's what you want? From what you're describing, you're looking to test a cooling solution (i.e. radiator), not a water block; is that right? If that's the case, I'd recomend a custom made block; a solid copper piece, with integrated heater, inlet and outlet. edit: ...or more simply a water heater, as Bill suggested... Last edited by bigben2k; 04-12-2005 at 08:17 PM. |
![]() |
![]() |
![]() |
#24 |
Cooling Savant
Join Date: Sep 2004
Location: Los Angeles, Ca
Posts: 310
|
![]()
thats a good idea ben.. the block that is being made would work well for that actually. its a round copper block that is 1.5inch in diameter. not sure on the length. but i could easly cross drill it and tap it for 1/2inch fittings.. that would work well.
350Watts its alot but that will be the max testing. I will do 100 to 350.. it will show how some rads max out and cant take the heat and where the limit is drawn for good cooling ability at each wattage rating. I would like to do 100-350 in 50 watt incriments. EDIT: how the heck would i use one of those shunts....? it looks like it would just heat up the air no?
__________________
Excuse me, I believe you have my stapler. Last edited by MaxxxRacer; 04-12-2005 at 08:27 PM. |
![]() |
![]() |
![]() |
#25 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]()
So this is for testing a cooling solution then?
Is this for yourself, or for site reviews, or for R&D/product development? Did you understand the purpose of using DC versus AC? There's more questions than answers in this thread. |
![]() |
![]() |
![]() |