As part of a test bench, we need a steady source of heat, that simulates what a CPU puts out. A CPU is a poor choice here, because the heat level is difficult to control, and to measure.
The heat die may use electrical heaters, the output of which can easily be measured by monitoring the voltage and amperage going through it. The accuracy of this measurement will be discussed here so this thread may be more about this heat source, its construction, and very importantly, how to prevent or minimize the secondary losses, which may throw off results. Temperature measurements at the heat die may be discussed here. Some references: -Joe's sim (Is there a link?) -Bill's bench -RoboTech's page Last edited by bigben2k; 09-01-2003 at 01:10 AM. |
![]() |
![]() |
![]() |
#2 | |
Cooling Savant
Join Date: Sep 2002
Location: Santiago, Chile
Posts: 403
|
![]() Quote:
![]() Also I remember some forum thread with pictures of bill's simulator, but I dont have the link. (it was'nt on procooling) |
|
![]() |
![]() |
![]() |
#3 |
Cooling Savant
Join Date: Dec 2002
Location: Dallas
Posts: 339
|
![]()
My suggestion would be to use a T.E.C as a thermal source. A unit like this should generate a constant temperature needed to test a block providing power is adequately regulated.
Last edited by joemac; 09-01-2003 at 05:17 PM. |
![]() |
![]() |
![]() |
#4 |
Thermophile
Join Date: Aug 2002
Location: Just shut up ;) ...
Posts: 1,068
|
![]()
A TEC sounds dodgy, it's not constant. Would'nt it's 'performance' vary with the coldside temp, which would vary with the hotside temp. To much room for fluctuation?.
One of those big resistors they use for discharging battery packs would be better suited I think. I seem to remember Billa suggesting something better though?(surprise, surprise!)... |
![]() |
![]() |
![]() |
#5 |
Cooling Savant
Join Date: Apr 2003
Location: Blackburn / Dundee
Posts: 451
|
![]()
A soldering iron.
I don't know if they work on a DC current but if they do then you could butcher an old one up replace the tip with a heat die shaped one, and give it current through a circuit with capsitors (to regulate) and resistors (to alter the current). They CAN get up to VERY hot temperatures and run for hours (well at least the ones I have do... I'm allways leaving them on.) Worth looking into? ~ Boli
__________________
1800+ @ 2247 (214x10.5) - STABLE, 512MB PC3700 TwinX Cosair RAM, NF7-S v2.0, GeForce3 Ti200 Parallel BIM, 120.1 Thermochill, Eheim 1048, Maze 3, Maze4 GPU, "Z" chipset, 1/2" tubing, PC-70: 5x120mm & 9x80mm fans. Internet Server & second machine (folding 24/7): 512MB DDR RAM, XP2000+ |
![]() |
![]() |
![]() |
#6 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]()
Actually, I was refering to Joe Kelly's bench, not Joe Citarella, but that's a good link, thanks!
joemac: I understand, from correspondence with your partner, that you've been looking at TECs because of this issue that resistor's actual values can shift over time and use. My reply to that (someone correct me if I'm wrong) is that it's really irrelevant, because regardless of the actual resistance, the power is measured by the voltage, and amperage. So I'd refer you to RoboTech's heaters (if I had a link). They're that small cylinder that you know about. They can be mounted inside of a copper or brass die, and then insulated, to minimize the secondary heat losses (a source of error, at ~2%). A power resistor may work, but it may be a bit less convenient to deal with, I think. Dan From dansdata.com uses one. As for TECs, I don't know how reliable that would be, as a heat source: Since it "moves" heat, using the power that is provided to it, the end result may be somewhat unpredictable. You also have to consider the clamping pressure, which could then become another variable, and source of error. We want to minimize the errors, as much as possible, because we can barely afford it. So a heater/resistor is easier to deal with, because the power measurement is direct, and the accuracy is simply down to that of the meters. One thing I've been pondering on and off for some time, is if it's possible to use the same meter, and switch back and forth, between measuring amps and volts. Then it occured to me that the amp measurement, if it's a tap in the power line really can't be interrupted, but there's always the amp probe, or alternatively, if it's acceptable, a power shunt, which has its own set of variables... But that's a discussion for this thread. |
![]() |
![]() |
![]() |
#7 |
Cooling Savant
Join Date: Dec 2002
Location: Dallas
Posts: 339
|
![]()
Ok let me explain this better and maybe a better drawing will help. The cold plate is not just a plain pressure plate as I showed in the original drawing. It is a heat sink enclosed in an insulated environment. This will prevent changes in the temperature outside to affect the temperature at the simulation die.
As for the resistor if W = VI and I = V/R a change in R (resistance) would cause a change in “I” this will cause “W” to change. A T.E.C is less prone to “R” changes if used and installed properly. |
![]() |
![]() |
![]() |
#8 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]()
joemac: you may be right in that the resistance of a TEC doesn't vary, but what I was trying to say, is that it's irrelevant: we can still measure the power output of a resistor/heater, by multiplying the amps and volts going to it. Simple.
Yes, the resistance of a heater/resistor changes, as you apply more power to it. Other than than, maybe some vibrations might change it, during the test, but that would still show up in the voltage and amp measurements. As for the TEC, how would you know, for sure, that you have the same exact clamping pressure, from one day to the next? Are you going to "torque" the coldplate on it, every single time? What kind of errors do you think that would give you? How could you measure that error? Also, you still don't know how much heat the pelt is outputting through its hot side. Although it's proportional to the power that you give it, it's not "directly" proportional. So how would you measure the power? A tec is great if you're trying to get to a specific temperature, but that's not the case here: we want to get to a specific power output. I like your diagram. You'd have to extend the insulation, to make sure that the cold air doesn't find it's way back up. If you use metallic screws, some of the output is going to end up being dissipated on the cold side. So you'd still be back to measuring it. |
![]() |
![]() |
![]() |
#9 |
Cooling Savant
Join Date: Mar 2003
Location: MO
Posts: 781
|
![]()
Here's a crudely drawn representation of my heat die concept. A cartridge heater (shown as red, such as the ones pH has - Watlow Electric?) is imbedded in a chunk of copper. Heat flows up the riser towards the water block. Two thermocouples are embedded into the riser at, say 10 mm intervals.
At steady state the temperature gradient up the riser will be linear and proportionate to the heat flow. Since we know the cross sectional area of the riser and the distance between the thermocouples, we can calculate the heat flow from the temperature difference. Additionally, we can infer the temperature of the die surface without having a probe directly on the die, avoiding the problems of a 'heat shadow'. |
![]() |
![]() |
![]() |
#10 |
Cooling Savant
Join Date: Jun 2003
Location: Miami, Florida US
Posts: 117
|
![]()
Resistor assy used by Dan's Data here
__________________
I stop for 1 C. "Those that give up essential liberty to obtain a little temporary safety deserve neither liberty nor safety." -- Benjamin Franklin (1773) |
![]() |
![]() |
![]() |
#11 |
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
![]()
Here is the slug I built with the round watlow heater cartride.
![]() Note there is 2 "steps" on both sides below the die area. Those are for TC's on both sides. You do not want to put them into the main raised part as that will effect the heat transfer to the top. |
![]() |
![]() |
![]() |
#12 | |
Cooling Savant
Join Date: Sep 2002
Location: Santiago, Chile
Posts: 403
|
![]() Quote:
I'm too lazy to put some numbers on this right now, but the critical factor is going to be the temp probe accuracy, as the temp difference to measure can be small. But precicion of the readings can be increased with probes separation. |
|
![]() |
![]() |
![]() |
#13 | |
Cooling Savant
Join Date: May 2002
Location: Da UP
Posts: 517
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#14 |
Cooling Savant
Join Date: May 2003
Location: NY
Posts: 234
|
![]()
Groth: That is one brilliant idea. It may be too perfect though, at times its difficult to make the math fit the real world and this may be one of those times. Most likely it would would but it would need to be calibrated quite accurately.
BigBen: Why not place a resister between your PS and load, then measure the voltage drop across the resister. Then calculatte the amperage by V=IR. |
![]() |
![]() |
![]() |
#15 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]()
That's an interesting concept, Groth!
I would think that in order to minimize the secondary losses, one would want to keep the heater as close as possible to the top of the die. You may have just gotten rid of that issue, to some extend. So does anyone know what the space shuttle uses for thermal insulation, and if there's anything similar we can use? |
![]() |
![]() |
![]() |
#16 | |
Cooling Savant
Join Date: Sep 2002
Location: Santiago, Chile
Posts: 403
|
![]() Quote:
-A heat die of 100mm2 -100 Watts load That makes a heat density of 1w/mm2 With copper conductivity of 0.386W/mm*k we have a gradient of 2.59ºC for each mm in lenght. With probes 10mm apart there is a delta of 25.9º. If you use two probes with an accuracy of 0.1ºCfor an accumulated error of 0.2º you have a power measurement accuracy of 0.77%. That's not bad at all considering that when monitoring input power only you have to guess how much is your secondary heat loss. Calibration of the two probes is easy: in cold and steady state both should measure the same temp. Applying this calculations to Robotech's die simulator we we can see a real world case: Asume again he's using 1w/mm2 heat density. Given that he's using a brass die (I'll guess 0.120w/mm*k?), the gradient would be 8.3º/mm. In a distance of 10mm the delta is 83.3º. He's using probes with 0.05º accuracy so his error margin is 0.12%. By choosing brass for the heat die the gradient have a big increase and improves accuracy of the reading, but that has a dangerous side effect: The base of the simulator is going to be at burning temps! Guessing again a 1w/mm2 heat load and that his brass die has a height of about 20mm, If he tests a cheasy heatsink that's only cappable of keeping the die surface at 60ºC, the base of the brass die is going to be at 227ºC! Things are going to be worst than that at the cartridges un the aluminium base. Robotech: If I were you, I'll reconsider the use of brass, or at least lower a lot the height of the thin part. |
|
![]() |
![]() |
![]() |
#17 |
Cooling Savant
Join Date: Sep 2002
Location: Santiago, Chile
Posts: 403
|
![]()
Edit: Damn double post!
|
![]() |
![]() |
![]() |
#18 |
Cooling Savant
Join Date: Mar 2003
Location: MO
Posts: 781
|
![]()
Well said, nicozeg. That's precisely what I how I was thinking.
For the calibration, I'd also throw in a test with the die surface air cooled. Readings from an IR thermometer could be compared to the expected value. |
![]() |
![]() |
![]() |
#19 | |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#20 |
Cooling Savant
Join Date: May 2002
Location: Da UP
Posts: 517
|
![]()
ok, you spend big money for .01C resolution and .05C accuracy then immediatly through your implementation you halve its accuracy which means there is a possibility you could be off by as much as .1C. Kinda makes paying for .01 resolution meaningless because you will never see it.
Is this the kind of equiptment we're talking about? $400 plus the sensors and readouts X 2. http://www.microdaq.com/mt/temperature/rtdtemp101.php |
![]() |
![]() |
![]() |
#21 | |
Cooling Savant
Join Date: Sep 2002
Location: Cincinnati, OH
Posts: 229
|
![]() Quote:
![]() Maybe I will re-do it in copper... short, truncated pyramid out of copper with a thin (0.12") brass top plate??? Or maybe I should just forget the brass bit all together??? Copper seems to be working for a few others. Thanks for the heads up... ![]() |
|
![]() |
![]() |
![]() |
#22 |
Cooling Savant
Join Date: Sep 2002
Location: Santiago, Chile
Posts: 403
|
![]()
If copper softness is your concern, you can use some type of dural for it's hardness and better thermal conduction than brass.
|
![]() |
![]() |
![]() |
#23 | |
Cooling Savant
Join Date: Sep 2002
Location: Cincinnati, OH
Posts: 229
|
![]() Quote:
![]() http://science.ksc.nasa.gov/shuttle/....html#sts-hrsi For a more practicle (and affordable) soultion for insulating thermal dies take a look at Cotronics; specifically their flexible ceramic thermal insulation products. http://www.cotronics.com/vo/cotr/fc_1.htm Ceramic blankets, board, moldable sheets and papers (refractory fibers - alumina oxide/silica oxide). |
|
![]() |
![]() |
![]() |
#24 | ||
Cooling Savant
Join Date: Dec 2002
Location: Dallas
Posts: 339
|
![]() Quote:
Quote:
|
||
![]() |
![]() |
![]() |
#25 |
Cooling Savant
Join Date: Dec 2002
Location: Dallas
Posts: 339
|
![]() |
![]() |
![]() |
![]() |