Unread 07-29-2004, 09:07 PM   #1
Etacovda
Cooling Savant
 
Join Date: Feb 2004
Location: Dunedin NZ
Posts: 735
Default Just another post....

Quote:
I've found that its not about water flow or hose size or any of those marketable things.

I'm running part of my aquarius II system (the block and rad) that uses the small hose and I have a new pump/water container.

As I found with the aquarius II system the art in getting it to work was to keep the ambient temp of the water in the reservior as low as possible. The rest of the system wasn't important.

You can work it out.

Joules = watts x seconds.

So we have a CPU thats using max 89 watts (P4 3.0C) which gives 89 joules per sec (about 320k/hour)

it takes 1 kilo-calorie (4200 joules approx) to heat 1 litre of water 1 deg C.

So you can work out how long it will take a P4 3.0C to heat up a litre of water 1 deg.

The important thing to note is that its likely that the surface area of 1 litre of water will radiate heat faster than the CPU would be able to heat it up - so it will probably stay at room (ambient) temp.

Now the problem becomes that of storing a litre of water in your machine. It takes up 1000 cu.cm of space.

Using a rad means you can increase the surface area of the water - so you can use less water. Or if you are not using a rad - you just need to make sure that their is sufficient airflow over the reservoir so that the ambient temp does not rise.

The flow rate of the water is not really important - so long as the water mixes in the reservoir properly - it wont rise above ambient. Remember that if you keep your reservoir inside the case the ambient case temp will often be much higher than outside the case.

Another way of puttin it would be to say - so long as the reservoir of water can radiate heat faster than the cpu can heat it up - the system will stay cool.
An unnamed individual, trying to tell a newbie what he needs to do with his watercooling system.. 'just add more water!'

Worst part is, its an overclockers forum... and this member has been around for quite some time, I think.

Pretty good example of misconception, thought you guys might want to have a chuckle at it; a good example of whats been floating around recently?

edit:: the new pump/watercontainer he is talking about is a mitron POS 400lph, 0.6m head 800ml(ish) pump/res combo.
Etacovda is offline   Reply With Quote
Unread 07-29-2004, 09:17 PM   #2
rundymc
Cooling Neophyte
 
Join Date: Feb 2004
Location: Singapore
Posts: 67
Default

care for another

enjoy the section on reservoirs and cooling
also notice the COMPLETE lack of critique on the product's Al reservoir
rundymc is offline   Reply With Quote
Unread 07-29-2004, 09:19 PM   #3
jaydee
Put up or Shut Up
 
jaydee's Avatar
 
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
Default

Ummmm, so all that tells me is it will take a little longer to heat up the extra water before your right back were you started..... So somehow, defying all logic and basic physics, this rez can cool water to the point of ambient temps!?!
Did I see this guy mention not using a rad at all and just adding airflow on the res to keep water temps to ambient?
Also is that a sharp 90 in that res on the outlet?

Sigh.....
jaydee is offline   Reply With Quote
Unread 07-29-2004, 09:22 PM   #4
Etacovda
Cooling Savant
 
Join Date: Feb 2004
Location: Dunedin NZ
Posts: 735
Default

"Nowadays there are various high quality water blocks from different manufacturers. Many of these manufacturers do not only focus on the appearance of the water block, rather they focus on its actual quality as well. It is a given that having a well constructed water block can instantly knock a couple of degrees of the temperature off. The picture above displays what Coolermaster has to offer, in this regard. The water block is a true beauty, and it is hard to imagine that this elegant device is part of an all-in-one water cooling kit. We would not be able to compare the performance of this water block with others of its kind in our review, but judging by the way it has been constructed, it seems the block will do its job quite well. Though it is small, measuring only 71x50x4mm, it is very effective is removing hot air. This is in part due to the fin-like components above the CPU which aid in cooling. The block is constructed with both copper and acrylic, and it doesn’t seem to have specific water-in or water-out specification. Installation is made easy by the water block’s plate fittings which are attached with a screwdriver."

Interesting, I never thought a block 'removed hot air'...
Also, yet another apparently completely flat base...

Impressive - a cpu thats 0.9 degrees above the water temp under full load!

Should we politely email this man?
Etacovda is offline   Reply With Quote
Unread 07-29-2004, 09:26 PM   #5
rundymc
Cooling Neophyte
 
Join Date: Feb 2004
Location: Singapore
Posts: 67
Default

you can actually tell from the pic that there are a few imperfections on the base
rundymc is offline   Reply With Quote
Unread 07-29-2004, 09:27 PM   #6
Etacovda
Cooling Savant
 
Join Date: Feb 2004
Location: Dunedin NZ
Posts: 735
Default

Jaydee - of course! the only reason we use a radiator is for size, didnt you know?
rundymc - total sarcasm

Also, of cross reference to my quoted post and the review that you posted run;

"However, note that the size of the reservoir can only take up to 450ml of liquid, which may not be enough for an extreme overclocking."
Etacovda is offline   Reply With Quote
Unread 07-29-2004, 09:29 PM   #7
OneMadPoptart
Cooling Neophyte
 
Join Date: Dec 2003
Location: Rochester, NY
Posts: 23
Default

What a great quote from that article:

Quote:
Notice the radiator’s condition. It is in superior condition without any bending or damage to any of the pins. Having a decent radiator is one of the most important factors in cooling the water. Some might believe that having a bigger reservoir would be more effective for cooling but I remember seeing a benchmark a long time ago, where the results suggested that without a radiator the water would become hot like the water you use in the bathtub.
And my personal favorite about the waterblock:

Quote:
Though it is small, measuring only 71x50x4mm, it is very effective is removing hot air. This is in part due to the fin-like components above the CPU which aid in cooling.


Wow.
__________________
.: || P4 2.8 800 @ 3.8 || Gigabyte 8KNXP || 1 Gig Crucial PC3200 || ATI 9800 PRO 128 || 2x WD 250GB RAID 0 || :.
.: || Danger Den RBX, Zchip, and Maze4 GPU || Black Ice Xtreme || Eheim 1250 || DD Fillport || :.
.: || Antec TrueBlue 480 || Modded Lian-Li PC65 || :.
OneMadPoptart is offline   Reply With Quote
Unread 07-29-2004, 09:54 PM   #8
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Quote:
Originally Posted by rundymc
care for another

enjoy the section on reservoirs and cooling
also notice the COMPLETE lack of critique on the product's Al reservoir
Anyone notice anything wrong with this picture from the review?

Cathar is offline   Reply With Quote
Unread 07-29-2004, 10:06 PM   #9
Chew_Toy
Cooling Savant
 
Join Date: Apr 2004
Location: Wisconsin
Posts: 120
Default

Nice probe placement.
Chew_Toy is offline   Reply With Quote
Unread 07-29-2004, 10:18 PM   #10
Etacovda
Cooling Savant
 
Join Date: Feb 2004
Location: Dunedin NZ
Posts: 735
Default

Also, the probe visably moves in the gif to godknowswhere
Etacovda is offline   Reply With Quote
Unread 07-29-2004, 10:25 PM   #11
AntiBling
Cooling Savant
 
Join Date: Jan 2004
Location: orlando FL
Posts: 147
Default

deleted post
__________________
www.nrlc.org
AntiBling is offline   Reply With Quote
Unread 07-29-2004, 10:48 PM   #12
OneMadPoptart
Cooling Neophyte
 
Join Date: Dec 2003
Location: Rochester, NY
Posts: 23
Default

Wow...I didn't notice the probe. Amazing. Simply amazing...
__________________
.: || P4 2.8 800 @ 3.8 || Gigabyte 8KNXP || 1 Gig Crucial PC3200 || ATI 9800 PRO 128 || 2x WD 250GB RAID 0 || :.
.: || Danger Den RBX, Zchip, and Maze4 GPU || Black Ice Xtreme || Eheim 1250 || DD Fillport || :.
.: || Antec TrueBlue 480 || Modded Lian-Li PC65 || :.
OneMadPoptart is offline   Reply With Quote
Unread 07-29-2004, 11:59 PM   #13
Chew_Toy
Cooling Savant
 
Join Date: Apr 2004
Location: Wisconsin
Posts: 120
Default

To me its not so much it moves as the fact it is even there.
Chew_Toy is offline   Reply With Quote
Unread 07-30-2004, 12:26 AM   #14
Razor6
Cooling Savant
 
Razor6's Avatar
 
Join Date: Apr 2002
Location: Houston, TX
Posts: 192
Default

Quote:
Originally Posted by Chew_Toy
To me its not so much it moves as the fact it is even there.
I like the fact that it got the best appearance award.
Razor6 is offline   Reply With Quote
Unread 07-30-2004, 03:45 AM   #15
Etacovda
Cooling Savant
 
Join Date: Feb 2004
Location: Dunedin NZ
Posts: 735
Default

"nope. Ive used 3 different thermal probes including a medical grade lazer probe.

All results are accurate on mobo +/- 2 deg max.

My ambient at the moment is 22C and you are telling me an Intel CPU should be running at 25 deg above that = 50C.

Bugger off

Its never been that high - even the time when I forgot to put water in the block and ran it air cooled.

None of you guys have even considered the insulating effect of any of the plastic hoses, reservoirs or anything.

Its sounds like your all using crazy academic theory to me."

What happens when you try to get someone to see reason. Oh well, i dont think this kind of thing is possible to stop... is it? (hes running a p4 3.0C @ 3.4 and claiming a 3 deg over ambient temp at what he claims is an 89w heat output)

Im failing to see, seriously, how something can be done about it. This guys refusing to read; i posted thermaltakes own C/W graph, with 90w @ 24ish degrees shown on the graph. Hopefully a pretty picture will get the point across.

Nope, the graph didnt get the point across; hes wanting to 'see the maths' after he posted his own maths about the 1L of water never being able to heat up (of course, he neglected to show the surface area of the water, or the thermal gradient of the tim/copper/rad etc etc etc)

Its too frustrating arguing with people like this; they are adament in their assumptions, and they refuse to look at things in a different manner. This is why procooling is hated, because procooling is at the opposite end of this equation, with the facts to back it up; when they deny what 'we' (again, loosely) say, we tell them to go shove some form of suppositry up their arse. Whats the bloody point in arguing with people like this? its frustrating, and seemingly pointless. He will _not_ think any differently, no matter how much 'evidence' i give him...

Last edited by Etacovda; 07-30-2004 at 05:28 AM.
Etacovda is offline   Reply With Quote
Unread 07-30-2004, 08:34 AM   #16
msv
Cooling Savant
 
msv's Avatar
 
Join Date: Dec 2002
Location: Sweden
Posts: 336
Default

*Sigh*
In another thread I spoke against flaming incompetent testers.
Maybe I should reconsider.
I´m by far no skilled WB-tester, but even my eye spotted a few doubtful things in that review.
"It is a given that having a well constructed water block can instantly knock a couple of degrees of the temperature off"
Amazing. It´s so relieving to know that.
Shit, I´m getting mean.
regards
Mikael S.
__________________
The only constant factor in all Your failures is You.

Catapultam habeo. Nisi pecuniam omnen mihi habis, ad caput tuum saxum immane mittam.

Last edited by msv; 07-30-2004 at 08:40 AM.
msv is offline   Reply With Quote
Unread 07-30-2004, 04:47 PM   #17
OneMadPoptart
Cooling Neophyte
 
Join Date: Dec 2003
Location: Rochester, NY
Posts: 23
Default

Quote:
Originally Posted by Etacovda
Its never been that high - even the time when I forgot to put water in the block and ran it air cooled.

None of you guys have even considered the insulating effect of any of the plastic hoses, reservoirs or anything.
When I think of watercooling, I naturally think of insulators

Oh my....

And where the hell are these passive heatsink blocks that keep a processor within 3 degrees of ambient...Someone could make a fortune with one of those
__________________
.: || P4 2.8 800 @ 3.8 || Gigabyte 8KNXP || 1 Gig Crucial PC3200 || ATI 9800 PRO 128 || 2x WD 250GB RAID 0 || :.
.: || Danger Den RBX, Zchip, and Maze4 GPU || Black Ice Xtreme || Eheim 1250 || DD Fillport || :.
.: || Antec TrueBlue 480 || Modded Lian-Li PC65 || :.
OneMadPoptart is offline   Reply With Quote
Unread 07-30-2004, 04:54 PM   #18
OneMadPoptart
Cooling Neophyte
 
Join Date: Dec 2003
Location: Rochester, NY
Posts: 23
Default

I know this is getting close to not being funny anymore, but read this:

Quote:
After you have done this, turn on the PC and just make sure no water is leaking from the device. Pay close attention when checking for leaks because even a small drip on the motherboard will force you to go on an unexpected shopping trip to get a new motherboard. However, we didn’t find any leaks from Coolermaster’s mighty Aquagate! The tubes are tightly secured so all is well
So wait...nobody ever told this guy it's ok to test a brand new watercooling setup without his precious hardware components close by? Sheesh...

I would have loved to see his review that said "I turned my computer on and ZAP!@$#. The aquagate just killed my motherboard and videocard because of a small leak from the hoses... I consider this a failure on the Aquagate's part to warn us about the possibility of water shorting out components when there is electricity running through the system..."
__________________
.: || P4 2.8 800 @ 3.8 || Gigabyte 8KNXP || 1 Gig Crucial PC3200 || ATI 9800 PRO 128 || 2x WD 250GB RAID 0 || :.
.: || Danger Den RBX, Zchip, and Maze4 GPU || Black Ice Xtreme || Eheim 1250 || DD Fillport || :.
.: || Antec TrueBlue 480 || Modded Lian-Li PC65 || :.
OneMadPoptart is offline   Reply With Quote
Unread 07-30-2004, 06:00 PM   #19
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

msv
careful, its catching
I too used to be real nice before I hit this place, bad company
LOL
BillA is offline   Reply With Quote
Unread 07-31-2004, 03:39 AM   #20
Kobuchi
Cooling Savant
 
Join Date: Jan 2003
Location: BC, Canada
Posts: 313
Default

Quote:
Originally Posted by Unnamed Individual
Another way of puttin it would be to say - so long as the reservoir of water can radiate heat faster than the cpu can heat it up - the system will stay cool.
I'm ticked off at him because he's ignorant. When I'm in the tub, my body temp warms the water. The water does not magically cool all by itself. It will just keep getting hotter. Surface area of reservoir doesn't matter. Lakes, oceans, full of mammals - it's the flow rate and heatercores. Fool.
Kobuchi is offline   Reply With Quote
Unread 07-31-2004, 04:16 AM   #21
rundymc
Cooling Neophyte
 
Join Date: Feb 2004
Location: Singapore
Posts: 67
Default

Quote:
Originally Posted by OneMadPoptart
snip....
read about the tissue paper
rundymc is offline   Reply With Quote
Unread 07-31-2004, 04:18 AM   #22
Etacovda
Cooling Savant
 
Join Date: Feb 2004
Location: Dunedin NZ
Posts: 735
Default

See, and you're not even arguing with him

Now put into effect the fact hes calling me an idiot because i refuse to 'show him the math', and saying i dont know much about 'pc architecture'... wtf does pc archtecture have to do with cooling a specific heat load?

This has gone on for pages, and I have yet to resort to name calling, and its increasingly hard. Ive called him stubborn, and thats about it.

frustration personified. I can understand bill's 'straight to the point, no bullshit or **** off' attitude now.
Etacovda is offline   Reply With Quote
Unread 07-31-2004, 08:40 AM   #23
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

msv
see, another's got the uglies now
BillA is offline   Reply With Quote
Unread 07-31-2004, 12:29 PM   #24
Kobuchi
Cooling Savant
 
Join Date: Jan 2003
Location: BC, Canada
Posts: 313
Default

Quote:
Originally Posted by Etacovda
hes calling me an idiot... saying i dont know much about 'pc architecture'

This has gone on for pages, and I have yet to resort to name calling
Oh! I see. I thought you were just scouting up dubious posts, to here, so we could all snicker and feel superior.

A real argument with "you are an idiot" must be frusterating. It seems to me his main point was that a large enough reservoir will do the job of a radiator. That's correct, in theory, isn't it? Maybe he thinks you're denying it. Of course the longer you two flame each other, the more particulars you'll find to disagree over.
Kobuchi is offline   Reply With Quote
Unread 07-31-2004, 12:57 PM   #25
Butcher
Thermophile
 
Join Date: May 2001
Location: UK
Posts: 1,064
Default

Quote:
Originally Posted by Kobuchi
I'm ticked off at him because he's ignorant. When I'm in the tub, my body temp warms the water. The water does not magically cool all by itself. It will just keep getting hotter. Surface area of reservoir doesn't matter. Lakes, oceans, full of mammals - it's the flow rate and heatercores. Fool.
I tend to notice the water gets cool pretty quick... But then a human body only produces about 95W while lying in a bath, while the surface area of the water is quite large (especially compared to anything in use in water cooling).
__________________
Once upon a time, in a land far far away...
Butcher is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 06:34 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...