Old 11-05-2004, 04:43 AM   #26
Uncle`BuZZ
Cooling Neophyte
 
Join Date: Oct 2004
Location: France
Posts: 28
Default

Those results are for the block Cascade. But with some more restrictive blocks ( like those we use in Europe such 1A or nexxos ) the best choice is for lower pumps.

For a block like 1a-hv2, the best choice would be the MCP650, MCP600 and probably the DDC and CSP750 instead of MD20.

For the cascade, the DDC seems to have the same figures than the EHEIM 1250 (about 5.2 lpm and 9W) but with a more restrictive block, this lpm are less affected than for the EHEIM or IWAKI.

this topic is very usefulll to give an idea of why bigger pumps aren't the best choice, but I think you should put your figures into concept and say this results are valid for the cascade or others blocks with the same C/W and restriction, and that the best choice could evolve depending of the type of block (less or more restrictive).

It would be greet to do the same thing with many representative blocks, but I know data are missing.
Uncle`BuZZ is offline   Reply With Quote
Old 11-05-2004, 05:02 AM   #27
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Quote:
Originally Posted by Uncle`BuZZ
Those results are for the block Cascade. But with some more restrictive blocks ( like those we use in Europe such 1A or nexxos ) the best choice is for lower pumps.

For a block like 1a-hv2, the best choice would be the MCP650, MCP600 and probably the DDC and CSP750 instead of MD20.
/me glances up and notices that I actually recommended that the MCP600 @13.8v was the best single pump of all the above scenarios. The MCP600 @ 13.8v has about the same peak pressure head as the Laing DDC, but slightly more flow. Only if the MD-20RZ were a DC pump then it could possibly be better than the MCP600.

No, nothing different at all between what you are saying, and what I am recommending.

The slope of the pressure vs C/W curve for a particular waterblock is what also defines which pumps that a certain block might favor. One cannot base the distinction of which pump would be better simply based upon a block's restrictiveness, but rather how steep the pressure vs C/W gradient is.

For the thin-based blocks like the NexXxoS XP, and the 1A-HV2, these blocks actually have a lot more in common with the Cascade in this manner than you may realise.

Last edited by Cathar; 11-05-2004 at 06:04 AM.
Cathar is offline   Reply With Quote
Old 11-05-2004, 05:19 AM   #28
Uncle`BuZZ
Cooling Neophyte
 
Join Date: Oct 2004
Location: France
Posts: 28
Default

I told about DDC, CSP and also EHEIM. The MCP are "polyvalent" so their good results are as good for low restrictive blocks than for very restrictive blocks.

But in your post, you put a sort of "ranking", but this ranking could evolve depending of the type of block. The MCP are great and won't move, but for some blocks we are using in Europe (seems to be 50/50 between very restrictive and low restrictive block here) the EHEIM 1048 and the DDC (which is equivalent with EHEIM 1250 for the cascade in performances) will take better rank instead of the MD20 or others IWAKI pumps.

I just want to put in concept your ranking and not saying

Quote:
Recommended pumps:

Performance: Iwaki MD-20RZ
in all cases.

For very restricitve blocks, I think DDC and MCP650 have a better "profil" than many powerful pump like the MD20.
Uncle`BuZZ is offline   Reply With Quote
Old 11-05-2004, 05:20 AM   #29
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Edited my post above - please read it again for comments.

By "Performance", this also includes a large and highly effective radiator, such as a triple or quad fan radiator. I guess I should have made that more clear.
Cathar is offline   Reply With Quote
Old 11-05-2004, 06:51 AM   #30
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

Quote:
...and the DDC (which is equivalent with EHEIM 1250 for the cascade in performances)
Are you sure about this? Have you plotted the PQ curves for these two pumps with this bloc? And then run through the math for dT based on pump heat, etc (as Cathar has done)?

[perso, j'ai un gros doute ]
lolito_fr is offline   Reply With Quote
Old 11-05-2004, 07:28 AM   #31
bobkoure
Cooling Savant
 
Join Date: Feb 2003
Location: USA - Boston area
Posts: 798
Default

I suspect that there are some low restriction waterblocks for which the 1046 is not as "below the knee" as you mention.
The curve for the Swiftech 6000 comes to mind - there seems to be very little additional benefit as flows increase.
bobkoure is offline   Reply With Quote
Old 11-05-2004, 07:29 AM   #32
Uncle`BuZZ
Cooling Neophyte
 
Join Date: Oct 2004
Location: France
Posts: 28
Default

C'est mon petit doigt qui me l'a dit

I have the PQ curve of the DDC and the EHEIM 1250. They cross themselves at about 5.2 lpm. (first I estimated the PQ curve of the cascade from the cathar's results with the EHEIM 1250,1048 and MCP650 and I used it with the PQ curve of the DDC, and I saw 5.2 lpm like for the 1250)

I used the power/flow curve from rosco to determine the heat given to water by the pump (I used the same efficiency than cathar with the MCP650 alias D4) and found about 9W

5.2 lpm, 9W, same figures for the DDC and the EHEIM 1250, so same perfomances
Uncle`BuZZ is offline   Reply With Quote
Old 11-05-2004, 07:31 AM   #33
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Buzz, you have the PQ curve for the DDC at 13.2v.

Somewhat different, and lower, at 12v where the block tops out at less than 6LPM, and peak pressure is ~20% lower.

Using the 13.2v PQ curve is fine, but be aware that it is a non-standard voltage in PC's and must be achieved through an externally powered means.

I always found it somewhat odd that the DDC was "originally designed for PC cooling", yet somewhat misleadingly all the PQ curves and values reported are at its maximum 13.2v level.

Still, even if the DDC is the equal of the Eheim 1250, that still leaves a fair amount performance gain to be achieved through the use of a stronger pump for blocks.

Last edited by Cathar; 11-05-2004 at 07:37 AM.
Cathar is offline   Reply With Quote
Old 11-05-2004, 07:39 AM   #34
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Quote:
Originally Posted by bobkoure
The curve for the Swiftech 6000 comes to mind - there seems to be very little additional benefit as flows increase.
The pressure vs C/W curve for the Swiftech MCW6000 is very flat in comparison to many other blocks, and I would hazard an educated guess that it is even flatter than many of the European high-restriction low-flow blocks.

Too late now, but I'll run some figures with the MCW6000 tomorrow.
Cathar is offline   Reply With Quote
Old 11-05-2004, 07:56 AM   #35
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

(semi)ok Buzz: I dont think the DDC puts out 9w - it only just absorbs that much. (not that it would make much difference at this level)
My little finger does agree with yours in that it will be a different scenario for a 1a-hv2 type block though
lolito_fr is offline   Reply With Quote
Old 11-05-2004, 07:58 AM   #36
Belenar
Cooling Neophyte
 
Belenar's Avatar
 
Join Date: Oct 2004
Location: Belgium
Posts: 51
Default

So the best noise/performance choice would be two 1048 pumps in series? Or do they become a lot noisier when placed in series? Does anyone have experience with 2 1048's in series?
Belenar is offline   Reply With Quote
Old 11-05-2004, 10:43 AM   #37
redleader
Thermophile
 
Join Date: Jun 2001
Location: The deserts of Tucson, Az
Posts: 1,264
Default

Quote:
Originally Posted by bobkoure
I suspect that there are some low restriction waterblocks for which the 1046 is not as "below the knee" as you mention.
The curve for the Swiftech 6000 comes to mind - there seems to be very little additional benefit as flows increase.
Probably not. Even if the flow curve is perfectly flat the transistion from a 1046 to a 1250 looses by just .3C (remember we're dealing with a 9 w pump here, which isn't a huge problem for a large-ish radiator). If theres even a slight downward curve on the C/W per flow curve, the block will pick up the couple thousands of a C/W needed to offset the 7.5w gain.

Of course, if you assume a small enough radiator, all bets are off
redleader is offline   Reply With Quote
Old 11-05-2004, 11:22 AM   #38
nikhsub1
c00ling p00n
 
nikhsub1's Avatar
 
Join Date: Jun 2002
Location: L.A.
Posts: 758
Default

This is a very nice guide! The only thing I question is the estimation of heat dumped directly into the water by the pumps.
__________________

*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*
E6700 @ 3.65Ghz / P5W DH Deluxe / 2GB 667 TeamGroup / 1900XTX
PC Power & Cooling Turbo 510 Deluxe
Mountain Mods U2-UFO Cube
Storm G5 --> MP-01 --> PA 120.3 --> 2x DDC Ultras in Series --> Custom Clear Res
"Artificial intelligence is no match for natural stupidity."
1,223,460+ Ghz Folding@Home
aNonForums
*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*
nikhsub1 is offline   Reply With Quote
Old 11-05-2004, 12:26 PM   #39
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

Quote:
Originally Posted by nikhsub1
This is a very nice guide! The only thing I question is the estimation of heat dumped directly into the water by the pumps.
which is exactly the basis for this whole exercise
at 3 gpm and 150W I'm looking at a deltaT of 0.20°C, so at 10W the expected deltaT would be 0.0133°C
at a more reasonable/measurable flow rate of 1.5 gpm the deltaT is 0.38°C, so 10W would be ~ 0.0253°C
I would not be too uncomfortable at differentiating between 5W differences, but lesser increments would not be 'measurable' with the equipment I have

next time I'm into pump testing I'll gin out some measured values
BillA is offline   Reply With Quote
Old 11-05-2004, 01:18 PM   #40
bobkoure
Cooling Savant
 
Join Date: Feb 2003
Location: USA - Boston area
Posts: 798
Default

Quote:
Originally Posted by redleader
Even if the flow curve is perfectly flat the transistion from a 1046 to a 1250 looses by just .3C ( If theres even a slight downward curve on the C/W per flow curve, the block will pick up the couple thousands of a C/W needed to offset the 7.5w gain.
So, you're saying it makes sense to go with the 1250 because it might perform about the same as a 1046 in this situation?
bobkoure is offline   Reply With Quote
Old 11-05-2004, 02:39 PM   #41
Jag
Cooling Savant
 
Join Date: May 2004
Location: Portugal
Posts: 179
Default

Cathar,

Would you still maintain your recommendation «Single 120mm radiator: First choice: Swiftech MCP600 or AquaXtreme 50Z. Silence Choice: Eheim 1048» for a radiator that followed somewhat the ideal specs you mentioned in a topic sometime ago: 160x160x32mm, or 160x160x45mm?
Jag is offline   Reply With Quote
Old 11-05-2004, 03:38 PM   #42
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

Cathar
Not happy with the data.
Particularly the assumed constancy of heat imputs
Are the "pump heat" to water measured or a dream?

Last edited by Les; 11-05-2004 at 03:54 PM.
Les is offline   Reply With Quote
Old 11-05-2004, 04:10 PM   #43
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Quote:
Originally Posted by Les
Cathar
Not happy with the data.
Particularly the assumed constancy of heat imputs
Are the "pump heat" to water measured or a dream?
Eheim 1048, 1250, MCP600 @ 12.0 and 13.8, MCP650, Iwaki MD-30RZ are all measured values, since I actually had those pumps in hand.

Eheim 1046 is an extrapolation based on the other Eheims.

The rest of the Iwaki's are extrapolations based on a 63% of rated input figure as determined from testing the MD-30RZ, due to the common shared separated magnetic armature design. The MCP600, which is also of similar design, as well as the March 893-09 that I have here, all have a ratio of in-line heat to pump motor input of around the 65-70%. Given the strong trend, I felt it safe enough to run with those figures.

In the full article I had already explicitly explained that which were measured values, and those which were extrapolations.

I really wanted to include the Danner Mag 3, but I did not feel comfortable with assigning a pump heat transfer value to it without either measuring it, or having a number of other pumps from the same range to extrapolate from.
Cathar is offline   Reply With Quote
Old 11-05-2004, 04:18 PM   #44
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

Quote:
Originally Posted by Cathar
Eheim 1048, 1250, MCP600 @ 12.0 and 13.8, MCP650, Iwaki MD-30RZ are all measured values, since I actually had those pumps in hand.

With a Cascade + rad in the circuit?
Not happy
Les is offline   Reply With Quote
Old 11-05-2004, 04:23 PM   #45
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Quote:
Originally Posted by Les
With a Cascade + rad in the circuit?
Not happy
With a Cascade, no rad.

Not happy? Get over it, or do better.
Cathar is offline   Reply With Quote
Old 11-05-2004, 04:39 PM   #46
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

Happy that info is presented.
Always been a poor experimentalist, and now being slightly physically limited present zero.
However always hope for pure data
Les is offline   Reply With Quote
Old 11-05-2004, 04:46 PM   #47
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Quote:
Originally Posted by Les
Happy that info is presented.
Always been a poor experimentalist, and now being slightly physically limited
However always hope pure data
Les, I do know where you're coming from, although I do get a little frustrated sometimes with the perennial suggestions from you that I'm making this stuff up as I go along.

I'm happy to admit what's extrapolated/estimated vs what I measured. I am also aware of the variance of pump heat output as the flow rate changes. I chose to measure with a Cascade in the loop to provide a single value that I could use. Yes, it does not strictly apply, but in what I measured for the various pumps it offers a pretty good mid-point between stupendously blocked flow (trickle) vs open-flow, with those extremes varying by around 10%, and at most 15% from the values I measured with the Cascade in the loop by itself.

I don't have the time, or really the exacting equipment, to generate detailed heat vs flow graphs, so yes, I did compromise here and settle on a catch-all figure. Even given the heat vs flow variations, we're still only talking about 0.1-0.2C variations at the absolute extremes of the flow rate ranges for the >50W pumps, from what would be calculated given the simplified "mid-point" heat transfer figure.

Last edited by Cathar; 11-05-2004 at 04:54 PM.
Cathar is offline   Reply With Quote
Old 11-05-2004, 05:10 PM   #48
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

As a cooling god you have to be extra cautious.
For example
I am curious about the statement "C/W"=0.003 fora 3.5mx3.5x2.5m room .
With brick walls i would make it more like 0.03c/w
Les is offline   Reply With Quote
Old 11-05-2004, 05:15 PM   #49
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

F**k I hate the "cooling god" appellation.

Quote:
Originally Posted by Les
I am curious about the statement "C/W"=0.003 fora 3.5mx3.5x2.5m room .
With brick walls i would make it more like 0.03c/w
No double brick walls here in Australia (well, not many).

0.003 with the door open accounts for it. Just a really, really rough measurement.

Close the door, and double brick the room, then yeah, 0.03 would probably be more accurate.
Cathar is offline   Reply With Quote
Old 11-05-2004, 05:16 PM   #50
Etacovda
Cooling Savant
 
Join Date: Feb 2004
Location: Dunedin NZ
Posts: 735
Default

Quote:
Originally Posted by Cathar
TDX/RBX will be included with the final article.

Not a whole lot of difference between different pumps though - basically the same sorts of patterns as with the Cascade.
Apologies, didnt notice the 'knee' was very similar - i was under the impression it was steeper than the cascade by quite some margin.
__________________
Hypocritical Signature I tried to delete: Procooling: where scientific principles are ignored because big corporations are immune to mistakes and oversights.
Etacovda is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 4 (0 members and 4 guests)
 
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 06:40 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...