Go Back   Pro/Forums > ProCooling Technical Discussions > General Liquid/Water Cooling Discussion
Password
Register FAQ Members List Calendar JavaChat Mark Forums Read

General Liquid/Water Cooling Discussion For discussion about Full Cooling System kits, or general cooling topics. Keep specific cooling items like pumps, radiators, etc... in their specific forums.

Reply
Thread Tools
Unread 10-26-2005, 01:43 PM   #1
Kemist
Cooling Neophyte
 
Join Date: Sep 2005
Location: NJ
Posts: 14
Default Y pressure drop / Rads parallel or series

Hey guys

Im building an external rad box and i have two MCR-220 rads. As of right now im not sure how im going to plumb them. I will be running two 1/2 modded ddc pumps in series. Basically i am considering (A). Running rads in series or (B). running in parallel using a wye to split the flow into the rads, then from the rads running a hose from each to the reservoir (so two hose inlets into the res).

I know there is basically no way to know without proper testing which way would be better. I am wondering however if wye's are associated with large pressure drops? Right now im leaning towards going parallel rather than in series. While flow rate would be lower the Dt (air/water) of the water entering the second rad would be higher compared to the Dt of the cooled water entering the second rad in series. Since i will have two pumps i am assuming that the Dt component will be more important in lowering temps than the water's flow rate, since flow rate should be relatively high.

Just wondering everyone's thoughts on this and also that whole wye pressure drop question. Thanks
Kemist is offline   Reply With Quote
Unread 10-26-2005, 02:11 PM   #2
redleader
Thermophile
 
Join Date: Jun 2001
Location: The deserts of Tucson, Az
Posts: 1,264
Default

Given the sheer pumping head and radiator area, I'm guessing the difference will be immeasurably small as you will have extremely low radiator C/W either way. I'd route whichever way allows for easiest/neatest plumbing.
redleader is offline   Reply With Quote
Unread 10-26-2005, 05:53 PM   #3
greenman100
Cooling Savant
 
Join Date: Jun 2004
Location: Florida
Posts: 414
Default

Dt across rad will be less than a degree, more than mad eup for by increased water velocity of the seriec config


go series
__________________
"Employ your time in improving yourself by other men's writings, so that you shall gain easily what others have labored hard for."
--Socrates
"greenman100 = obnoxious ass hole"-gazorp
greenman100 is offline   Reply With Quote
Unread 10-26-2005, 07:32 PM   #4
bobo5195
Cooling Savant
 
Join Date: Aug 2005
Location: uk
Posts: 400
Default

water velocity really doesnt matter much.

As long as Mass flow water * Cp water is above the equivlant of air. Look at Bills graphs
bobo5195 is offline   Reply With Quote
Unread 10-26-2005, 07:36 PM   #5
Cyco-Dude
Cooling Savant
 
Cyco-Dude's Avatar
 
Join Date: Feb 2002
Location: Dayton, Ohio
Posts: 836
Default

Quote:
Originally Posted by greenman100
Dt across rad will be less than a degree, more than mad eup for by increased water velocity of the seriec config
exactly how will having a higher water velocity in the radiators help? wouldn't it be better to have the water moving slower in the radiators (i.e., spends more time in the radiators) to transfer more heat to the fins? or was that disproved?
Cyco-Dude is offline   Reply With Quote
Unread 10-26-2005, 07:58 PM   #6
jaydee
Put up or Shut Up
 
jaydee's Avatar
 
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
Default

Quote:
Originally Posted by Cyco-Dude
exactly how will having a higher water velocity in the radiators help? wouldn't it be better to have the water moving slower in the radiators (i.e., spends more time in the radiators) to transfer more heat to the fins? or was that disproved?
It was disproved.
jaydee is offline   Reply With Quote
Unread 10-26-2005, 11:08 PM   #7
Long Haired Git
Cooling Savant
 
Long Haired Git's Avatar
 
Join Date: Jan 2003
Location: Sydney, Oz
Posts: 336
Default

Cathar tested dual BA radiators and found that serial was better in his rig on the day he did the testing. Its the case that parallel results in half the flow rate in each rad which does reduce performance, but it also reduces the overall restriction and thus increases overall flow rate to a small degree, but then you also have to factor in the impedence of the Y fittings.

The "Y"'s add restriction, most notably for 3/8" tubing and barb rigs. My modelling (cringe, I am crap at it) shows 1/2" barbs 30mm long with 8.46mm ID creates approx 20cm of head at 5m. 3/8" with 7.1mm ID Y is 40cm of head. I've assumed the Y "convergance" has the same head characteristics. Note also that my modelling results in barb conversion effects about 20% higher than noted in BillA's testing of HE rads with different barbs.

Time for approximator!
Swiftech MCP655 @ 5, Swiftech Storm block over 70W. In serial, I have 2m of tubing, whilst in parallel I have 1.2m outside of the two Y peices, and then 10cm runs from the arms of each Y to the radiators.
Each MCR220QP radiator has a fan at 7v as most people run rads like this these days.

Serial: 6.4 LPM, pump adding 16.2W, water temp at exit of pump is 2.2°C, CPU delta-T is 11.5°, radiator C/W is 0.0492
Parallel: 6.05 LPM, pump adding 16.0W, water temp at exit of pump is 2.3°C, CPU delta-T is 11.6°, radiator C/W is 0.0529

In parallel, I approximate the head of each Y connector at 29cm of H20.

Anyone want to do a PQ graph of a common brass 1/2" Y for me? Even a single flow rate value would be SOMETHING!?!?!

Assuming my approximator is correct, it looks basically the same either way you do it. So, plumb it the way that's most convenient, which is typically in serial.
__________________
Long Haired Git
"Securing an environment of Windows platforms from abuse - external or internal - is akin to trying to install sprinklers in a fireworks factory where smoking on the job is permitted." (Prof. Gene Spafford)
My Rig, in all its glory, can be seen best here
AMD XP1600 @ 1530 Mhz | Soyo Dragon + | 256 Mb PC2700 DDRAM | 2 x 40 Gb 7200rpm in Raid-0 | Maze 2, eheim 1250, dual heater cores! | Full specifications (PCDB)

Long Haired Git is offline   Reply With Quote
Unread 10-27-2005, 10:12 AM   #8
bobo5195
Cooling Savant
 
Join Date: Aug 2005
Location: uk
Posts: 400
Default

Y splitter is something like 0.3*mean velocity^2 of highest speed side (NOT Q)
bobo5195 is offline   Reply With Quote
Unread 10-27-2005, 12:45 PM   #9
billbartuska
Cooling Savant
 
Join Date: Jun 2005
Location: Skokie, Illinois
Posts: 322
Default

Quote:
Originally Posted by Cyco-Dude
exactly how will having a higher water velocity in the radiators help? wouldn't it be better to have the water moving slower in the radiators (i.e., spends more time in the radiators) to transfer more heat to the fins? or was that disproved?
Whatever the velocity of the water is , it will spend the same amount of time in the rad. Doubling the velocity also doubles the number of times the water passes through the rad per given time period. But increaced flow will result in increaced efficiency due to turbulance For example see http://overclockers.com/articles1158/

Also note the effect of airflow. Trippling the water flow increaces cooling about 34%, but just doubling the airflow increaces cooling about 38%.....for this rad under the stated conditions....user results may vary.
__________________
My new rig....
Intel SE440BX-3, PIII 550 (@ 680)
MX440 275/332 (@ 350/400) and 3DFX Voodo 5 5500 160/160 (@180/180)
Two Opticals and 120 gigs (w/28gigs in RAID0) on 4 Maxstors
billbartuska is offline   Reply With Quote
Unread 10-27-2005, 02:06 PM   #10
redleader
Thermophile
 
Join Date: Jun 2001
Location: The deserts of Tucson, Az
Posts: 1,264
Default

Quote:
Originally Posted by Cyco-Dude
exactly how will having a higher water velocity in the radiators help? wouldn't it be better to have the water moving slower in the radiators (i.e., spends more time in the radiators) to transfer more heat to the fins? or was that disproved?
Swiftech actually publishes the data for this radiator. THeres a fairly strong dependenance on higher flow, at least with stronger fans. Google for the page, its quite interesting.

I suppose the answer to this question also depends on the fans used. If you have very low airflow, the difference between parallel and serial for radiator C/W will be vanishingly small, however the overall decrease in flow resistance may be worthwhile.
redleader is offline   Reply With Quote
Unread 10-27-2005, 02:19 PM   #11
Cyco-Dude
Cooling Savant
 
Cyco-Dude's Avatar
 
Join Date: Feb 2002
Location: Dayton, Ohio
Posts: 836
Default

alrighty then, thanks for filling me in guys. i've been outta the loop for awhile
Cyco-Dude is offline   Reply With Quote
Unread 10-27-2005, 03:40 PM   #12
Long Haired Git
Cooling Savant
 
Long Haired Git's Avatar
 
Join Date: Jan 2003
Location: Sydney, Oz
Posts: 336
Default

Quote:
Originally Posted by bobo5195
Y splitter is something like 0.3*mean velocity^2 of highest speed side (NOT Q)
I got: Head in meters H20 = 0.0088 * Flow in LPM * Flow in LPM.
I did the pressure drop for each barb as a tube of the right ID, the pressure drop for the lip of the entry to the tube, and then the PD over the split, and then the PD for the two exit tubes at half the flow of the original.

Eg: 1/2" Y with 8.46mm ID at 4 LPM entry:

Entry lip: 7.9 PSI
Entry barb: 0.8 PSI
Y section: 4.9 PSI
Two exit barbs at half flow: 0.25 PSI each = 0.5

Hmmm, I add the two exits together, which is a mistake. Nuts. Anyway, adding and converting to mH20 I get 0.143m. I am out by 0.5PSI, but that will be like 3% which is within my margin of error.

Quote:
I suppose the answer to this question also depends on the fans used. If you have very low airflow, the difference between parallel and serial for radiator C/W will be vanishingly small, however the overall decrease in flow resistance may be worthwhile.
1. My simulator's pretty good. Dropping to 5v fans, parallel is still worse, by about 0.9 degrees C. At 12v this drops to a mere 0.06 degree difference.
2. Current model shows the Y joints result in a larger resistance than the benefit of parallel radiators, so no overall flow rate improvement.
__________________
Long Haired Git
"Securing an environment of Windows platforms from abuse - external or internal - is akin to trying to install sprinklers in a fireworks factory where smoking on the job is permitted." (Prof. Gene Spafford)
My Rig, in all its glory, can be seen best here
AMD XP1600 @ 1530 Mhz | Soyo Dragon + | 256 Mb PC2700 DDRAM | 2 x 40 Gb 7200rpm in Raid-0 | Maze 2, eheim 1250, dual heater cores! | Full specifications (PCDB)

Long Haired Git is offline   Reply With Quote
Unread 10-27-2005, 04:08 PM   #13
Kemist
Cooling Neophyte
 
Join Date: Sep 2005
Location: NJ
Posts: 14
Default

Long Haired,

If I am not mistaken you made the calculations using two 1/2 wye's. If i do go parallel I will only be using one 1/2 wye and each rads outlet will have a dedicated line to the reservoir. Additionally, i will be using 7/16 tubing which should reduce the lip's effect on flow, correct? Taking the above into account this would probably reduce the difference between serial and parallel making them even more comparable, correct? Thanks for your input guys.

If you did mean only one wye then sorry i misunderstood you. Anyway from your simulator and most peoples comments it seems like it isnt gonna change things by much so ill probably just plumb whichever way is easier.

Last edited by Kemist; 10-27-2005 at 04:16 PM.
Kemist is offline   Reply With Quote
Unread 10-27-2005, 08:41 PM   #14
Long Haired Git
Cooling Savant
 
Long Haired Git's Avatar
 
Join Date: Jan 2003
Location: Sydney, Oz
Posts: 336
Default

Quote:
Originally Posted by Kemist
If I am not mistaken you made the calculations using two 1/2 wye's. If i do go parallel I will only be using one 1/2 wye and each rads outlet will have a dedicated line to the reservoir.
Will change things, but I have no PQ graph for a reservoir.
I am in the process of blowing up my code in order to enforce tubing ID to barb OD correctness, so will post new model soon.


Quote:
Additionally, i will be using 7/16 tubing which should reduce the lip's effect on flow, correct?
Ahhh, but due to the smaller ID, more restrictive than 1/2" tubing. I cite lack of PQ graphs and testing, and declared overall it was the same and don't cater for it. You lose on the tubing, win with the lip, and so flow wise you're even. Flexibility wise you're ahead, so you win.
__________________
Long Haired Git
"Securing an environment of Windows platforms from abuse - external or internal - is akin to trying to install sprinklers in a fireworks factory where smoking on the job is permitted." (Prof. Gene Spafford)
My Rig, in all its glory, can be seen best here
AMD XP1600 @ 1530 Mhz | Soyo Dragon + | 256 Mb PC2700 DDRAM | 2 x 40 Gb 7200rpm in Raid-0 | Maze 2, eheim 1250, dual heater cores! | Full specifications (PCDB)

Long Haired Git is offline   Reply With Quote
Unread 10-27-2005, 09:32 PM   #15
Kemist
Cooling Neophyte
 
Join Date: Sep 2005
Location: NJ
Posts: 14
Default

Quote:
Originally Posted by Long Haired Git
Ahhh, but due to the smaller ID, more restrictive than 1/2" tubing. I cite lack of PQ graphs and testing, and declared overall it was the same and don't cater for it. You lose on the tubing, win with the lip, and so flow wise you're even. Flexibility wise you're ahead, so you win.
Yeah i didnt really think about the restriction of the tubing. Im just gonna go series, the pressure drop on the mcr220's doesnt look all that high anyway, at least according to the graphs on swiftechs site.
Kemist is offline   Reply With Quote
Unread 10-27-2005, 11:12 PM   #16
Long Haired Git
Cooling Savant
 
Long Haired Git's Avatar
 
Join Date: Jan 2003
Location: Sydney, Oz
Posts: 336
Default

Kemist: I used that very same data for my calculations. Pump PQ graphs are easily sourced, as are tubing PQ graphs, as are the Swiftech storm PQ graphs, as are the MCR220QP graphs. Just a matter of plugging in the numbers and looking up the CW charts to work out benefits and losses.
__________________
Long Haired Git
"Securing an environment of Windows platforms from abuse - external or internal - is akin to trying to install sprinklers in a fireworks factory where smoking on the job is permitted." (Prof. Gene Spafford)
My Rig, in all its glory, can be seen best here
AMD XP1600 @ 1530 Mhz | Soyo Dragon + | 256 Mb PC2700 DDRAM | 2 x 40 Gb 7200rpm in Raid-0 | Maze 2, eheim 1250, dual heater cores! | Full specifications (PCDB)

Long Haired Git is offline   Reply With Quote
Unread 10-28-2005, 03:56 AM   #17
bobo5195
Cooling Savant
 
Join Date: Aug 2005
Location: uk
Posts: 400
Default

Discharge into and flow from an infinitely large (for our cases a resviour is infinitely large) body of water the k factor is 1.

Ie dP= K * V^2 where w is the mean velocity.

This is an analytical relationship and is completely geometry independent. A real res where there is flow between teh inlet and outlet is different.

The main advantage of running parallel is not presure drop but increase in fluid dT.
bobo5195 is offline   Reply With Quote
Unread 11-15-2005, 09:39 PM   #18
guandi
Cooling Savant
 
guandi's Avatar
 
Join Date: Dec 2003
Location: UK
Posts: 174
Default

what if you had two pumps, each feeding a seperate rad and then going into a Y peice? would it help if the Y peice was 5/8ID with 1/2id tube?
__________________
A8N-SLI Deluxe
FX55@3ghz
2x TwinX1024-3200XL
2x BFG6800Ultra
Audigy2 ZS + Gigaworks S750
2x120gb/4x80gb
lots of water/copper/pumpy goodness.
guandi is offline   Reply With Quote
Unread 11-16-2005, 01:51 PM   #19
Long Haired Git
Cooling Savant
 
Long Haired Git's Avatar
 
Join Date: Jan 2003
Location: Sydney, Oz
Posts: 336
Default

My model is flawed in the amount of heat added by the pumps, in that I assume 60% to 80% of heat pump is added to the coolant (depending on flow rate). However, testing at cooling masters has found that this is way too high for some pumps.
Until I fix that, I find that any effort to add in extra pumps results in worse temps due to the extra heat of the pumps.
__________________
Long Haired Git
"Securing an environment of Windows platforms from abuse - external or internal - is akin to trying to install sprinklers in a fireworks factory where smoking on the job is permitted." (Prof. Gene Spafford)
My Rig, in all its glory, can be seen best here
AMD XP1600 @ 1530 Mhz | Soyo Dragon + | 256 Mb PC2700 DDRAM | 2 x 40 Gb 7200rpm in Raid-0 | Maze 2, eheim 1250, dual heater cores! | Full specifications (PCDB)

Long Haired Git is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 08:32 PM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...