U is the thermal resistance per unit area
TEMA types are not vaid here. End effects and assorted problems like that are going to be proportional to Q. |
![]() |
![]() |
![]() |
#77 |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]()
1) Used UA
2) Stated only valid for TEMA. Unsure whether invalid for Compact Xflow. Have you an example? 3) "End effects and assorted problems" = "extra bits and pieces" Are we agreeing there are problems? Last edited by Les; 10-30-2005 at 05:42 AM. |
![]() |
![]() |
![]() |
#78 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
sure
some are sidestepped by the general similarity of form (six 120mm fan/rads can be externally very similar, six 2-core (dual row) rads can be compared to each other) with enough data on different aspects then those can be characterized depends on the type of/purpose for the data collection many other 'problems' can be minimized by focusing on the actual conditions of use 10% is rather good for 'hand calcs' such as we are doing I generally settle for an understanding of 'which was better' in testing, but such will involve smaller increments than I would presume to calculate with accuracy |
![]() |
![]() |
![]() |
#79 |
Cooling Savant
Join Date: Aug 2005
Location: uk
Posts: 400
|
![]()
We agreed that there were problems ages ago but that there were to small to be worried about.
To measure second law effects you have to take into acoount all 4 temps which is a bugger for testing especially as they are only useful in scaling calcs not overall performance. TEMA is invlaid use xflow results. There are actually many types of crossflow as well, in our case counterflow might be valid as well. Actual conditons can play a bit part. Attaching a rad to a warm case full of warm air is obviously going to cause an effect for examplem thats there is obviously no point focusing on. Another way of including UA is given below. Eq 2 and 3 show relations for eq 1. NTU is a commonly used perfromance indicator for rads. Cmin is whatever masslfow * cp is lower. This is why on other areas i say that either fan or water flow rate is important not both. The effect is easily seen in bills graphs where performance bottoms out at a set point. |
![]() |
![]() |
![]() |
#80 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
Yes ".....but that there were to small to be worried about." with the exclusion of me. You have conjured up 10% (or was it 11%) out of thin air. May well be 10% but have not been shown evidence. Yes, use crossflow.Why I was asking you for "crossflow example" The interrelations shown can be useful in presentation data. but do little to validate method. Unless you can demonstrate with an example - proof of pudding. |
|
![]() |
![]() |
![]() |
#81 | ||
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
Not the plot you wished. Old data and possibly errors(link to data) However shows performance bottoming out. This tells us nothing. The values however suggest something may be amiss Need examples Edit1: Added link Edit2 : Reply to Quote:
Last edited by Les; 10-30-2005 at 10:25 AM. |
||
![]() |
![]() |
![]() |
#82 |
Cooling Savant
Join Date: Aug 2005
Location: uk
Posts: 400
|
![]()
We agreed that they were too complicated to worry about. Proof of how right they are is impossible as you dont know what you are comparing them to.
The current method was accepted practice in the industry from the 40's to the presnt day. Various books use it as a good first order interpretation. The jet airliner where you entrust your life to a heat exchanger uses this method. Its wrong yes but not wrong enough. |
![]() |
![]() |
![]() |
#83 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
hold it please
let me generate a set of accurate data for Les et all to work with (several weeks +) (a shame Swiftech does not seem inclined to put up their rad comparison) I am unsettled by references to 'small' values wrt my earlier testing, it was not that accurate |
![]() |
![]() |
![]() |
#84 |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]()
No intention of creating work.
If "small" values you are referring to are the E=100%+ for Big Momma, feel these are caused by P/Q curve error . Fouling (rabbit hair) comes to mind. |
![]() |
![]() |
![]() |
#85 |
Cooling Savant
Join Date: Aug 2005
Location: uk
Posts: 400
|
![]()
anythign above 60% for a computer rad take with a pinch of salf. More than likely they are caused by other means.
A really good rad test would have all 4 temps, 2 mass flows and Qin. If we have all of those accurately you can quantify pretty much everything. I think that gives you 4 ways to get C/W so errors should be minimal. |
![]() |
![]() |
![]() |
#86 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
My modeling suggests a range of 20-100% is possible in a 120x120mm rad. Edit1: Added more points to graph Edit2 : Finished off sums, attached Last edited by Les; 11-01-2005 at 05:35 AM. |
|
![]() |
![]() |
![]() |
#87 |
Cooling Savant
Join Date: Aug 2005
Location: uk
Posts: 400
|
![]()
I am convinced anything over at least 80% is completely wrong. Definitly. The only heat exchangers that achieve over 95% are the huge industrial type that cost more than your house. If there are results over 100% then they are quite obviously wrong. In this forum we obey the laws of thermodynamics. The other flow could be Cmin.
Car heat exchangers are in the 40% range. A paper i was reading expressed worries about using a heat exchanger of over 60% as it is "too good" because you end up paying more money for it. Last edited by bobo5195; 10-31-2005 at 01:34 AM. |
![]() |
![]() |
![]() |
#88 |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]()
Again a source or evidence would be useful.
Use big book and calculate for some sample 120x120rads Edit: Of course results over 100% are wrong. These are beermat calculations using rough, average Specific Heats and Convection Coeffs. Normalizing(terminology) max % of 101.9% to 100%(or less, 95% say) would be no biggy Last edited by Les; 10-31-2005 at 01:52 AM. |
![]() |
![]() |
![]() |
#89 | |
Cooling Savant
Join Date: Aug 2005
Location: uk
Posts: 400
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#90 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
from a procedural perspective, if you have questions ask
I'm presently w/o data but should have some soon (?) the air side is characterized by the fan inlet air temp only (as described earlier) the data is not 'wrong', it is our assumptions regarding the data, etc. EDIT just took a look at "Radiator" Effectiveness v Air Flow and I see the units "Air Flow (83.min) this was measured with a thermal anemometer and a traverse across the 6" duct used for a 'wind tunnel' one thing is quite certain, the 'tunnel' - not being calibrated - IS going to be off at at least one end of its range, and likely both iffy data to be beating up each other over Last edited by BillA; 10-31-2005 at 07:42 AM. |
![]() |
![]() |
![]() |
#91 |
Cooling Savant
Join Date: Aug 2005
Location: uk
Posts: 400
|
![]()
I had a read of my heat exchanger book on the train. Bit of a headfock. Alot of the 2nd law stuff is not applicable here as we do not know Air temp out
Last edited by bobo5195; 10-31-2005 at 03:08 PM. |
![]() |
![]() |
![]() |
#92 |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]()
Hear you Bill.
However my current dispute with Bobo does not involve data, it is the theoretical expectations of PC radiators. Have finished current set of sums and will keep further thoughts to myself. Final update is now attached to Post 86 Last edited by Les; 10-31-2005 at 05:37 PM. |
![]() |
![]() |
![]() |
#93 |
Cooling Savant
Join Date: Aug 2005
Location: uk
Posts: 400
|
![]()
Do you mean a full analytical model from first principals?
2nd law equations which mean not very much? How to design a good 120mm rad? Variation of c/w with various gemetric parameters? 2nd law stuff cannot be computed from current data as all 4 tempratures are need. Measurement of current data is fairly simple, although bills +/- 1 air temp resutls in huge errors, and there is the problem of no test for air water content |
![]() |
![]() |
![]() |
#94 |
Cooling Savant
Join Date: Aug 2005
Location: uk
Posts: 400
|
![]()
This is quick and rough but it looks right.
3 sheets, condensed is the one your after(tidier interface), designed for converting bills thermochill results (C/W) into eff, SD and "bobo" C/W (being the correct one of course). Enjoy. Results are not entered properly (not proper bill C/W), but i have attempted to calculate errors and show how things are affected. Shows limits of DIY CAUTION Bills C/W results read of the graph will effect the eff results alot, take with pinch of salt. |
![]() |
![]() |
![]() |
#95 |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]()
Initial comments
1)Bill at that time was , I think, using a LMT for water T component of C in C/W 2) Your sums appear correct if using correct units in Cp(air)m calcs. I get ~10w/c to your ~600 . Bloody units. Will check mine .Whichever, it explains all. 3) Hate magic in Excels - messes up my simple sums - I suppose I must learn sometime. Edit: Checked mine, looks ok, but forever screwing-up unit conversions Air @ 0.5m^3/min , Cp=1005.70 J/kg-C, Density=1.1774 Kg/m^3 m[Kg/hr]Cp= 35523.34 (J/hr)/C = 9.867593 W/C Will check again in the morning. Anyone? This would make Effectiveness ~ 97% at all considered water flow-rates Not in disagreement with Post 86's modeling predictions for a 24 FPI rad Last edited by Les; 11-01-2005 at 08:24 PM. |
![]() |
![]() |
![]() |
#96 |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]()
Morning
Checked again, my numbers are fine. Your numbers are also fine. However you are, I think, working at AirFlow=30m^3/min( 0.5m^3/s), which is 75X the AirFlow at which there is a "Measured Heat Dissipation" of ~50w ( Graph 12) Looks GIGOish Also not at all happy in your description of Bill's C/W. His C/W, IMO, should be C/"Measured Heat Dissipated" Using current practice this is, for these tests, 5/"Measured Heat Dissipated" As can be seen from Graph 12 it decreases with increasing flow. Last edited by Les; 11-02-2005 at 02:30 AM. |
![]() |
![]() |
![]() |
#97 | |
Cooling Savant
Join Date: Aug 2005
Location: uk
Posts: 400
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#98 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
one thing is quite certain, the 'tunnel' - not being calibrated - IS going to be off at at least one end of its range, and likely both" Plus the measurement error bars are some what arbitrarily set(case of ask Bill) and think your Cp and Density ranges are rather large(no numbers just ....) (Fan+Rad)'s Eff. may well be a better option Entropy - dunno but happy as long as don't bring in activation volume Last edited by Les; 11-02-2005 at 08:20 AM. |
|
![]() |
![]() |
![]() |
#99 |
Cooling Savant
Join Date: Aug 2005
Location: uk
Posts: 400
|
![]()
consider psycromery (spelling?) science of water in air. Creates large density and heat capacity changes in air.
Not sure what bill means by tunnel and calibration. If it is way off then that could explain results. In fact it makes this entire argument null and void. Water results were quite high but i was worried about additives. Last edited by bobo5195; 11-02-2005 at 11:58 AM. |
![]() |
![]() |
![]() |
#100 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
(2) No My dispute is that you(with the Big Book backing) say that when E is above 60% the data should be taken with a pinch of salt, and when E is above 80% the data is completely,definitely wrong. I say above 60% and 80% are acceptable values, as indicated by my modeling You and Big Book would automatically discard this data in any case. I would accept unless there are reasons to reject Last edited by Les; 11-02-2005 at 12:41 PM. |
|
![]() |
![]() |
![]() |