Unread 12-16-2002, 09:12 PM   #26
Since87
Pro/Guru - Uber Mod
 
Join Date: Sep 2002
Location: Indiana
Posts: 834
Default

Quote:
Originally posted by Mr. Baz
Normal pelts will do great at 12v....however drift pelts have a max of 25v. This is why he is running it at 20v, where it should be kept for optimal performance.
I know the specs for the Drift 0.8 pelts. I also know a bit about pelt operation.

The optimum operating point for the pelt is dependent on the performance of the hot side cooling system. It is not a fixed voltage like 20V.

Pelt cooling characteristics are very nonlinear, and they maintain substantial cooling capability to voltages (and/or currents) much lower than Vmax. See Figure 4 of this document for an illustration of this.

The power consumption of (and heat dissipated by) the pelt goes up roughly as the square of the voltage. Above Vmax/2, the pelt's cooling ability is increasing less and less for each additional volt.

With an underperforming watercooling system and a 16 Amp powersupply, two Drift 0.8's connected in series for 12V apiece, is going to be much more optimal than two in parallel at 20V.
Since87 is offline   Reply With Quote
Unread 12-16-2002, 10:02 PM   #27
Mr. Baz
Cooling Neophyte
 
Join Date: Dec 2002
Location: FL
Posts: 18
Default

One single 172w drift will not perform good at all at 12v. The optimal range for ONE 172w drift pelt is between 18v and 20v (I used to run one).

The clamping pressure is what helps determine the amps it can draw.
For the best performance, an ampmeter and a variable output PSU should be used. Hook the rig up and put the comp under load. Start the pelt at 17v and watch the ampmeter and your load temps. SLowly start upping the voltage until you see that there aren't anymore amps going to the pelt and/or you aren't able to cool the processor down anymore.

I see where you are coming from. You are just running two pelts at under their performance rating as to keep the hot side cooler. That's kinda cheating, but gets the job done. I still say shoot for the moon on it though.

With a better performing cooling system for the pelts, you should be able to run them both separately to insure each pelt gets its own fair share of amps.
Mr. Baz is offline   Reply With Quote
Unread 12-16-2002, 10:43 PM   #28
Since87
Pro/Guru - Uber Mod
 
Join Date: Sep 2002
Location: Indiana
Posts: 834
Default

Quote:
Originally posted by Mr. Baz
The clamping pressure is what helps determine the amps it can draw.
Can you show me data from a TEC manufacturer that says this?

The clamping pressure recommendations are to ensure good thermal contact between the TEC and the hot and cold plates. It has no significant correlation with the current draw.

Quote:
Originally posted by Mr. Baz
For the best performance, an ampmeter and a variable output PSU should be used. Hook the rig up and put the comp under load. Start the pelt at 17v and watch the ampmeter and your load temps. SLowly start upping the voltage until you see that there aren't anymore amps going to the pelt and/or you aren't able to cool the processor down anymore.
This is (almost) total nonsense. The current will continue going up as the voltage goes up. It's not going to stop going up at some magical point of optimal pelt operation. Given a beefy enough supply, it will continue going up until something dies.

I certainly would agree that checking the CPU temperature over a wide range of pelt voltages would be a good idea. (Need to give the system time to stabilize at each voltage setting though.) Not many people are going to have the supply to be able to do that testing though.
Since87 is offline   Reply With Quote
Unread 12-16-2002, 11:51 PM   #29
ap0calyps
Cooling Neophyte
 
Join Date: Dec 2002
Location: Ottawa, ON
Posts: 30
Default

About clamping pressure. I read that article AGES ago. Like I said, I have a DangerDen Maze 2.2, have a look and SEE what it is:

Specs: http://www.dangerden.com/mall/maze2.asp

Just the pic: http://www.dangerden.com/images/MAZE...ront_large.gif

As you can see, the coldplate uses the EXACT SAME mounting system. My pelts already HAVE that much pressure.

I have mounted the block without the springs to get better pressure from the coldplate to the chip. Not much difference. Maybe 1-2C under load better than with the springs.

Don't have time right now to mention the rad, but will check the review out tomorrow.

Thanks for all the input. Really like the shroud idea. I should have known to do that But thanks!
ap0calyps is offline   Reply With Quote
Unread 12-17-2002, 08:11 AM   #30
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

For what it's worth...

I checked out the mechanical properties of those nylon bolts, and they should be able to provide the clamping pressure necessary.

http://www.plasticnutsandbolts.com/

So you're down to getting that water temp lower.
bigben2k is offline   Reply With Quote
Unread 12-17-2002, 08:16 AM   #31
ap0calyps
Cooling Neophyte
 
Join Date: Dec 2002
Location: Ottawa, ON
Posts: 30
Default

You guys don't seem familiar with the DangerDen Maze 2.2. I should have been a little more clear. The nylon bolts hold the coldplate to the CPU. There are steel bolts holding the coldplate and block together with the pelts between them.

Yeah here is a link to my pump, check it out:

http://www.pumpworld.net/prod8.htm#3B-500

500gph @ 1 foot, 300gph @5 feet. Quieter than my MagDrive.
ap0calyps is offline   Reply With Quote
Unread 12-18-2002, 02:56 PM   #32
Mr. Baz
Cooling Neophyte
 
Join Date: Dec 2002
Location: FL
Posts: 18
Default

Quote:
Originally posted by Since87
Can you show me data from a TEC manufacturer that says this?

The clamping pressure recommendations are to ensure good thermal contact between the TEC and the hot and cold plates. It has no significant correlation with the current draw.



This is (almost) total nonsense. The current will continue going up as the voltage goes up. It's not going to stop going up at some magical point of optimal pelt operation. Given a beefy enough supply, it will continue going up until something dies.

I certainly would agree that checking the CPU temperature over a wide range of pelt voltages would be a good idea. (Need to give the system time to stabilize at each voltage setting though.) Not many people are going to have the supply to be able to do that testing though.
Just a quick question. You ever used a 172w pelt? Cause I have...and I speaking from my experience.
Mr. Baz is offline   Reply With Quote
Unread 12-18-2002, 03:14 PM   #33
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Quote:
Originally posted by ap0calyps
You guys don't seem familiar with the DangerDen Maze 2.2. I should have been a little more clear. The nylon bolts hold the coldplate to the CPU. There are steel bolts holding the coldplate and block together with the pelts between them.

Yeah here is a link to my pump, check it out:

http://www.pumpworld.net/prod8.htm#3B-500

500gph @ 1 foot, 300gph @5 feet. Quieter than my MagDrive.
Oops, my bad. It's been a while since I looked at a 2.2 .

Nice pump. It has an odd curve, where it's most efficient at the limits of its range. This tells me that it's designed for a fountain. Yup, it is. You'll do well with that pump.
bigben2k is offline   Reply With Quote
Unread 12-18-2002, 06:18 PM   #34
Skulemate
Cooling Savant
 
Skulemate's Avatar
 
Join Date: Jul 2002
Location: Toronto, Canada
Posts: 381
Default

The curve looks odd because they're not using a linear scale on their x-axis... 0 - 300 - 360 - 500 at even spacing? If you plot the individual points that can be read from that graph in Excel it looks much more like a "normal" pump curve... a little flat actually, but not too bad.
__________________
Michael E. Robbins
M.A.Sc. Candidate, University of Toronto

12.1 GHz of AMD's finest (17.7 GHz total) crunching proudly for the AMDMB.com Killer Frogs
SETI BOINC: Dual Opteron 246s (Iwill DK8N) | XP2800+ (Shuttle SN41G2) | 3x XP2400+ (ASUS A7N266-vm)
SETI BOINC: 2x P4 2.8E (ASUS P4R800-vm) | Crunching 24/7
Skulemate is offline   Reply With Quote
Unread 12-18-2002, 10:04 PM   #35
Since87
Pro/Guru - Uber Mod
 
Join Date: Sep 2002
Location: Indiana
Posts: 834
Default

Quote:
Originally posted by Mr. Baz
Just a quick question. You ever used a 172w pelt? Cause I have...and I speaking from my experience.
Yeah, I just now hooked a 172 Watt pelt up to an AA cell and cooled my thumb off. I've got experience too.

You're still totally wrong about the current leveling off at a certain voltage, and that voltage being the optimum operating point for the pelt. (Are you aware, that a lot of variable output supplies have current limiting circuitry, and they will actually stop increasing the voltage when the current limit is hit, regardless of how much higher you crank the voltage output knob?)

How about demonstrating some understanding of how a pelt operates and proving that you're right, rather than giving such a lame response? If my understanding of pelts is lacking and you can explain why, I'd be glad to know it, and humbly apologize for being such an arrogant asshole.

Until then, I'm going to consider you a fool giving bad advice. When messing around with pelts, foolishness has significant risks.
Since87 is offline   Reply With Quote
Unread 12-18-2002, 10:33 PM   #36
ap0calyps
Cooling Neophyte
 
Join Date: Dec 2002
Location: Ottawa, ON
Posts: 30
Default

Quote:
Originally posted by Since87
Yeah, I just now hooked a 172 Watt pelt up to an AA cell and cooled my thumb off. I've got experience too.

You're still totally wrong about the current leveling off at a certain voltage, and that voltage being the optimum operating point for the pelt. (Are you aware, that a lot of variable output supplies have current limiting circuitry, and they will actually stop increasing the voltage when the current limit is hit, regardless of how much higher you crank the voltage output knob?)

How about demonstrating some understanding of how a pelt operates and proving that you're right, rather than giving such a lame response? If my understanding of pelts is lacking and you can explain why, I'd be glad to know it, and humbly apologize for being such an arrogant asshole.

Until then, I'm going to consider you a fool giving bad advice. When messing around with pelts, foolishness has significant risks.
I think your misunderstanding him. I think what he means is, that a pelt operates most efficiently at a certian voltage. The lower the voltage, the more efficiently it transfers heat. Some people have found that 18-20V is optimal. If you up the voltage above that, you get no decrease in temps. Read DrRom's article on www.overclockers.com
ap0calyps is offline   Reply With Quote
Unread 12-18-2002, 10:38 PM   #37
ap0calyps
Cooling Neophyte
 
Join Date: Dec 2002
Location: Ottawa, ON
Posts: 30
Default

And I think Mr. Baz has misunderstood DrRom's findings, and believes that because the temps don't change as you add voltage above 18-20V, the amperage does. However, I don't know where clamping pressure affecting current draw came from.
ap0calyps is offline   Reply With Quote
Unread 12-18-2002, 10:40 PM   #38
ap0calyps
Cooling Neophyte
 
Join Date: Dec 2002
Location: Ottawa, ON
Posts: 30
Default

Quote:
Originally posted by ap0calyps
And I think Mr. Baz has misunderstood DrRom's findings, and believes that because the temps don't change as you add voltage above 18-20V, the amperage does. However, I don't know where clamping pressure affecting current draw came from.
Oops! Should say:

and believes that because the temps don't change as you add voltage above 18-20V, neitehr does the amperage.
ap0calyps is offline   Reply With Quote
Unread 12-18-2002, 11:06 PM   #39
Since87
Pro/Guru - Uber Mod
 
Join Date: Sep 2002
Location: Indiana
Posts: 834
Default

To quote DrRom, "I'm running the 172w with 18v from a switchmode PSU - higher voltages offered no cooling improvements for me at all."

He didn't say that he found 18V to be the optimal voltage to run at. He only said that running at higher voltages was useless or worse.

The simulations I've done, show 16V to 17V to be the optimal place to operate with "good" watercooling. "Extremely good" watercooling might get the optimal operating voltage up to 20V.
Since87 is offline   Reply With Quote
Unread 12-19-2002, 01:03 AM   #40
ap0calyps
Cooling Neophyte
 
Join Date: Dec 2002
Location: Ottawa, ON
Posts: 30
Default

Got my new pump installed. Sure is nice! Temps dropped a bit, the block is cooler, but CPU temps are still too high. ROughly the same as they were.

Would a shroud make a HUGE difference? Am I going to need a new rad/heatercore? What would you suggest as highest performance available?
ap0calyps is offline   Reply With Quote
Unread 12-19-2002, 09:30 AM   #41
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Quote:
Originally posted by ap0calyps
Got my new pump installed. Sure is nice! Temps dropped a bit, the block is cooler, but CPU temps are still too high. ROughly the same as they were.

Would a shroud make a HUGE difference? Am I going to need a new rad/heatercore? What would you suggest as highest performance available?
Your water/CPU temps shouldn't have changed dramatically, from a new pump: you still have a cooling problem.

A shroud won'y make a significant difference.

Maybe you could tell us which model fan you're using?

BTW, if you've read Bill Adam's radiator roundup article, you should have noticed the airflow graphs: if you can get a fan to create a pressure drop equivalent to 1/4 inch water, you should have plenty of cooling power.

I suspect you're using an L1A panaflo fan, which really can't get you the airflow you need.
bigben2k is offline   Reply With Quote
Unread 12-19-2002, 09:46 AM   #42
ap0calyps
Cooling Neophyte
 
Join Date: Dec 2002
Location: Ottawa, ON
Posts: 30
Default

Well, there is an article on www.overclockers.com under watercooling, where the author makes a nice shroud and gets a 40% INCREASE in cooling performance from his heatercore.

I have a YS Tech 120MM FD1212387B-2R roughly 135CFM I think?
ap0calyps is offline   Reply With Quote
Unread 12-19-2002, 10:22 AM   #43
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

I stand corrected!

Link to shrouding article

If this fella can drop his CPU temp from 51.8 to 44, You might as well give it a shot.

If you want a quick idea of how beneficial it can be, try ducting with tape first.

As for the fan, it will deadhead at .25 inch pressure drop. In other words, the actual flow you are getting is probably closer to 75 cfm (max 125) with a pressure drop closer to 1/16 inch.

Specs here

You might consider a more powefull fan, or multiple fans.
bigben2k is offline   Reply With Quote
Unread 12-19-2002, 08:37 PM   #44
ap0calyps
Cooling Neophyte
 
Join Date: Dec 2002
Location: Ottawa, ON
Posts: 30
Default

I don't have room for multiple fans. What would you suggest for a more powerful, yet not DELTA sounding 120MM fan?
ap0calyps is offline   Reply With Quote
Unread 12-20-2002, 09:40 AM   #45
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

You can go through this chart and pick a unit that has a low noise to flow rate ration, while maintaining a good cfm (with either a voltmod, or a rheobus, or whatever controlling device you prefer).

[edit]
It looks like the Sunon KD1212PMB1-6A is a winner in the 120mm size.

Last edited by bigben2k; 12-20-2002 at 09:47 AM.
bigben2k is offline   Reply With Quote
Unread 12-22-2002, 07:09 PM   #46
ap0calyps
Cooling Neophyte
 
Join Date: Dec 2002
Location: Ottawa, ON
Posts: 30
Default

Which rad/heatercore can cool 2x 172w pelts? BIX can't......
ap0calyps is offline   Reply With Quote
Unread 12-23-2002, 08:47 AM   #47
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Quote:
Originally posted by ap0calyps
Which rad/heatercore can cool 2x 172w pelts? BIX can't......
How much room do you have?
bigben2k is offline   Reply With Quote
Unread 12-23-2002, 12:05 PM   #48
ap0calyps
Cooling Neophyte
 
Join Date: Dec 2002
Location: Ottawa, ON
Posts: 30
Default

well I have a 120mm hole in the top of my tower which I cut for my BIX. So I can only use a single 120MM fan, but the rad can be bigger than that.

My tower is Antec SX1200
ap0calyps is offline   Reply With Quote
Unread 12-23-2002, 12:21 PM   #49
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

I'd try
Code:
Fedco#	Height	Width	Thickness	Inlet	Outlet	Make	Model	Years
2-549	6.25	6.375	2.625	0.625	0.5	Nissan	210	80-82
2-549	6.25	6.375	2.625	0.625	0.5	Nissan	510	78-81
2-548	6.25	6.125	2.625	0.625	0.5	Nissan	210	76-79
2-551	5.25	6.625	2.625	0.625	0.625	Nissan	240Z	70-73
2-554	6.375	6.75	2.625	0.625	0.625	Nissan	B210	74-78
2-547	6.375	6.75	2.625	0.625	0.625	Nissan	310	79-82
2-554	6.375	6.75	2.625	0.625	0.625	Nissan	200SX	77-79
Check them out at heatercore4u.com (but buy it locally: it'll be cheaper).

They're the smallest cores that are 2 5/8 inch thick.

Last edited by bigben2k; 12-23-2002 at 12:26 PM.
bigben2k is offline   Reply With Quote
Unread 12-23-2002, 12:38 PM   #50
ap0calyps
Cooling Neophyte
 
Join Date: Dec 2002
Location: Ottawa, ON
Posts: 30
Default

What makes you think it would be ANY better than my 100% copper (YES the WHOLE RAD is COPPER, NO OTHER TYPE OF METAL) 2 pass high flow BIX?

I just checked out the Swiftech kits and noticed they include TWO fans with all kits. One blowing air through the rad and one sucking out the otehr side. Would that help at all??
ap0calyps is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 10:10 PM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...