#2 |
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
![]()
I am going to think on this for a while. It seems to me a hydrolic jack might work to raise the unit/scale. Like one of the $15 1-2ton bottle jacks. Bolt that to a metal plate for stability then weld another plate ontop of it to hold the unit. Make the bolting system from the jack to the lower plate adjustable and use a level to level the top plate. Then you can use the lower plate for the support to mount the water block to keep it from raising. 4 threaded rods tacked or screwed to the bottom plate and you have something to suppor the water block mount....
I will ponder this some more. Or instead of the bottle jack you can use one big peice of all thread with nuts for more precision mounting. The jack might be to sloppy. I think one center mounted chunk of all thread will make adjusting a lot simpler...... I got tons of the stuff at the shop. |
![]() |
![]() |
![]() |
#3 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
no jd
alignment is the key |
![]() |
![]() |
![]() |
#4 |
Cooling Savant
Join Date: Jan 2003
Location: VA Tech
Posts: 111
|
![]()
what about the WB's what use the stock socket clip? will you just rely on it to provde whatever pressure it makes?
__________________
1700@2050 (205x10@2.0v) Abit NF7-S rev2.0 3x 512 Corsair XMS3200C2 11-3-3-2 ATI Radeon 9800 Pro 128MB |
![]() |
![]() |
![]() |
#5 | |
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
![]() Quote:
![]() |
|
![]() |
![]() |
![]() |
#6 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]()
that's pretty clever
|
![]() |
![]() |
![]() |
#7 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]() ![]() big bucks here for the Zig Align ZD3 |
![]() |
![]() |
![]() |
#8 | |
Thermophile
Join Date: Oct 2002
Location: U.S.A = Michigan
Posts: 1,243
|
![]() Quote:
A pretty impressive use of what he had on hand to reach his goal. And his 8 mount average, WOW! It will be very interesting to see how this does for him in testing of blocks. ![]() |
|
![]() |
![]() |
![]() |
#9 |
Cooling Savant
Join Date: Mar 2003
Location: MO
Posts: 781
|
![]()
Very impressive reproducibility, and the addition of the digital scales is clever advance.
I'm not sure I see the point of spending the time with the Zig Align. Is the scales perfectly parallel between corrugated top and rubber-footed bottom? Is the die-sim? It will be interesting to see how he adapts his block hold-down for center inlets or for uneven/irregular tops. Edit: spelling and clarity Last edited by Groth; 11-12-2003 at 11:33 PM. |
![]() |
![]() |
![]() |
#10 | |
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#11 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
Yes at a constant angle but not necesarily normal. |
|
![]() |
![]() |
![]() |
#12 |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]()
Bill
I note that at 1gpm(3.785lpm) the PSID of 0.57(0.4mH2O) is about double your value*(eyeballed at 0.2mH2O). This discrepancy ,repeated in the subsequent article**, makes correlation of the C/W data somewhat difficult. Any info/thoughts on the anomaly. * http://thermal-management-testing.com/slitedge.htm ** http://www.overclockers.com/articles873/ |
![]() |
![]() |
![]() |
#13 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
"C/W"s are specific to a particular bench setup,
and will change also for that bench if components or procedures are changed JoeC and I have worked together for some years, notwithstanding this collaboration I (continue to) have 'issues' with some of his equipment - specifically his heat dies consider the SlitEdge results: Joe's "C/W" is considerably below that from my setup what are the components of the "C/W" ? °C, Watts, and the TIM joint - I will assume that the difference between Joe's and my temps is not so large as our equipment is similar (Fluke 2180A) - I will again assume that the effect of differences in the TIM joint is not so large - which leaves the power characterization and the die temp for Joe to have a lower "C/W", his Watts have to be 'greater' than mine and/or the die temp lower possible ? - sure, even probable 1. his die has less insulation resulting in greater secondary losses 2. as I understand his setup; while the die pedestal is in contact with the wb, the whole of the heat die body is in close proximity to the wb bp and its top surface uninsulated - but this should increase the actual heat picked up by the wb and if so will shift the die temp down a bit -> but it is also quite possible that where he is reading the die temp may be yielding a lower temp than with my setup ??? none of this will be too clear until Joe has posted 3 or 4 wbs that I also tested the shame is that Joe is going to put up only the "C/W" at 1gpm - though I too am mystified by the 'freeflow' and 'waterblock' head loss values no idea why they should be so different than mine, but I suspect he has not subtracted the 'connection/pressure tap' losses |
![]() |
![]() |
![]() |
#14 |
Thermophile
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
|
![]()
JoeC's heat die is 120mm^2, as opposed to Bill's 100mm^2.
As we all know, the TIM thermal resistance is proportional to the inverse of the surface area. The TIM thereby has about 20% lower thermal resistance than Bill's setup, so there's some of the difference. More of the difference arises in thermal density and its effects on the waterblock. The surface area presented to the block in Bill's test scenario is smaller. Now a smaller die "footprint" equates to a smaller concentration of heat that is presented to the water coming into contact with the wb. This is offset a bit by the spread of heat through the wb base-plate though, but given an assumed fixed value of h, being the rate of thermal convection, measured as W/m^2K, we are again left with a situation where a smaller die has less effective cooling "effort" acting upon it, resulting in a higher C/W for the block itself (which Bill has coined as T/W), even after discounting the TIM. Now the thermal density effect is not going to be linear, again highly dependent upon the wb base-plate thickness, but we given the bp thickness that seems apparant on the SlitEdge, one could probably predict a 10-15% higher block T/W. Weighting out the predicted proportion of TIM C/W and block T/W, we can predict that we're roughly looking at something a bit more than a 15% higher C/W for BillA's test-setup over JoeC's test setup for any particular wb that gets tested, again dependent upon bp thickness. Thicker bp's will incur a less significant relative "cost" for smaller die sizes. The rest of the differences (~5%) can easily be accounted for by Bill's rationale above. At least that's my take on the situation. Where it gets confusing for the common reader is when they see Bill's and Joe's C/W data presented on the same page, and people mistakenly assume that JoeC's naturally lower C/W figures means that certain blocks are better than those tested by BillA, as witnessed by someone sparking up this thread over at OC.com forums. |
![]() |
![]() |
![]() |
#15 |
Cooling Savant
Join Date: Mar 2003
Location: notts uk
Posts: 408
|
![]()
i feel like i am a little fish swimming with the big sharks but here goes.
i dont know if this is possible but you could improve on this by only using 2 hold down screws or even better one. Like an old pulp press with one one big screw on top. this should allow even pressure to be applied in one motion instead of one at each corner. just something that i thought after seeing the pictures at oc.com ![]()
__________________
Folding , Folding , Folding ! |
![]() |
![]() |
![]() |
#16 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
"h"'s relation with Waterloo's "Film Coefficient" is wb dependant. Waterloo's "Film Coefficient" can be used to calculate the Spreading Resistance* A previous post** took into account the change in "h" for a Slit-Edge model My previously posted guess at the relationship for the Slit-Edge :- Assumed JoeC's Die was 128sq mm Heat Spreading calculations using Waterloo and guessed relevant Dimensions (not all given in article). Used "C/W(TIM)"=0.1 and scaled to 0.078125(1/1.28) for JoeC's(no Spreading). ![]() * http://www.mhtl.uwaterloo.ca/tools.html# ** http://forums.procooling.com/vbb/sho...5&pagenumber=4 |
|
![]() |
![]() |
![]() |
#17 |
Thermophile
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
|
![]()
JoeC's information said a T'Bird sized die, which is 120mm^2.
Basically Les's graphs are showing a similar sort of relationship though between JoeC's and BillA's test-die sizes, and accounts for a very large percentage of the differences in results between the two setups for the same block. |
![]() |
![]() |
![]() |
#18 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
2 Have not considered either of these.Further thought required on leakage from Shoulders of die to wb. However,would think, the effect of die probe position can lumped with "C/W(TIM)" as far as scaling with die-size. 3. Think I would put it stronger - data at other flow rates may be vital to rationalise the observations |
|
![]() |
![]() |
![]() |
#19 | |
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#20 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]()
I gotta side with Bill here: the placement of the temp probe within the die is more than likely creating a difference: it'd be hard not to. What's missing is a compensation/adjustment factor, for actual CPU temp readings, and that's where pHaestus' excellent work comes in.
I like that idea Les. I also fail to see the relevance of the Zig-Align. The only problem is that if either surfaces (die or block) are convex, the results may vary. My original plan was to use 4 calibrated springs, and a "normal" 4 bolt hold down. Hadn't given the socket clamp much thought, yet. What spooks me in this whole thing, is having a clamp system that flexes against the springs, thereby lowering the actual pressure applied. Now if this clamp was calibrated before hand, maybe. Maybe it's time for an air suspension... I'll ponder this some more. |
![]() |
![]() |
![]() |
#21 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
google on 'load cell'
flexure is unimportant so long as the alignmeit is maintained Joe's setup will doubtless change when he gets around to testing with a 60lbf load such as is now used with several of our products |
![]() |
![]() |
![]() |
#22 |
Thermophile
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
|
![]()
The other thing to add here is WB base-plate flatness variations. Unless Joe is testing the same block as Bill did, there are bound to be some variations here. BillA's review showed that the flatness on the block that he reviewed could be improved and he makes mention of this in his review of it.
Bill has pointed out many times that block makers should all find themselves access to a proper lapping machine. I'm still hunting for one in my area that doesn't cost an arm and a leg. |
![]() |
![]() |
![]() |
#23 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
New PSID of 0.15(0.105mH2O) at 0.96gpm compared to an eyeballed 0.28(0.2mH2O) in Billa tests:http://thermal-management-testing.com/slitedge.htm However PSID a 0.46(0.3244mH2O) at 0.9gpm for the PolarFLO* corresponds to an eyeballed 0.28(0.2mH2O) in Billa's tests** The picture gets fuzzier as the results come in. * http://www.overclockers.com/articles879/ ** : http://www.thermal-management-testing.com/polarflo.htm |
|
![]() |
![]() |
![]() |
#24 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]()
Not too sure of the specifics of JoeC's setup, but I know that Bill measured the pressure drop due to the fittings and hose and subtracted that from all waterblock measurements. Perhaps this wasn't done by JoeC?
|
![]() |
![]() |
![]() |
#25 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
Seems weird in testing articles. |
|
![]() |
![]() |
![]() |