![]() | ||
|
|
General Liquid/Water Cooling Discussion For discussion about Full Cooling System kits, or general cooling topics. Keep specific cooling items like pumps, radiators, etc... in their specific forums. |
![]() |
Thread Tools |
![]() |
#1 |
Cooling Neophyte
Join Date: Feb 2004
Location: Da NBH
Posts: 68
|
![]()
I have a friend who bought a Koolance for the bling factor and now, two months later isn't very happy with the performance. He asked me for some help in terms of what he can change on it, and before I give him any reccomendations, I just wanted to double check that I'm at least sending him down the right path.
Since he doesn't want to buy new blocks, that leaves him the options of changing the pump, rad and fans. My first instinct would be to go to like a 1046, and hack up his Exxos to take 120mm fans on the rad - it appears that it should take 2x120 fine. Am I missing something, or am I on the right track here? I don't want to tell him to just ditch everything and discourage him from watercooling, I just wish he had read up more about what was out there before he bought what he had. Edit: Yes, I realize that this isn't high end like the forum name, but I trust you guys hella more than most other forums. |
![]() |
![]() |
![]() |
#2 |
Cooling Neophyte
Join Date: Dec 2002
Location: Irvine
Posts: 63
|
![]()
"Ditch everything" might not be needed, but you're talking about a near complete system revamp anyway. I mean, with new pump, new fans, new hoses, you're halfway there. A heatercore and mcw6000 waterblock will only run you another $60, and the difference in performance is rather significant. Those 1/4" ID hoses and 90 degree bends inside the kit hurt flow lots, and I'm pretty sure the koolance waterblock itself isn't very good (def. not a cascade or mcw6000).
Honestly, what I'd suggest is keeping the exos and using it as a secondary loop to cool hard drives, north bridge, graphics card, etc. It would work pretty well for that, and there's no sense letting the blocks go to waste if you've got 'em. I had the guts of one of the earlier koolance systems working in this capacity until I decided to cannibilize 'em for a chiller project. Odds are with a fair sized case your buddy can fit in a heatercore and pump in addition to the exos stuff. Plus this way you don't have to jack with the exos itself. ![]() |
![]() |
![]() |
![]() |
#3 | |
Cooling Savant
Join Date: Jul 2003
Location: Michigan, USA
Posts: 456
|
![]() Quote:
First question: what koolance system is it? The external or one of the cases? EDIT: Doh, noticed the exxos part. One big problem with the case ones is the pumps - two little minis. Replacement would seriously help there. I took one of the older PC-601s (or something like that) threw in an extra black ice 2 dual 80mm rad but it really didn't help the temps too much. I'm willing to guess the block itself wasn't all that decent and the pump power just wasn't.
__________________
Thou art God. Last edited by Tempus; 09-22-2004 at 07:51 AM. |
|
![]() |
![]() |
![]() |
#4 | |
Cooling Savant
Join Date: Jan 2004
Location: london, england
Posts: 416
|
![]() Quote:
http://cgi.ebay.co.uk/ws/eBayISAPI.d...tem=6708303746 http://cgi.ebay.co.uk/ws/eBayISAPI.d...tem=6708581973 |
|
![]() |
![]() |
![]() |
#5 |
Cooling Savant
Join Date: May 2004
Location: Kingston, NY
Posts: 269
|
![]()
I'm thinking he should sell it too, buy an Eheim, a 2x120 rad, MCW6000 and 1/2" tubing. He might make a couple bucks back by the end even. Especially if he still has the original packaging and sells the block with it, because to the best of my knowledge, the Exos doesn't even come with a block which would mean he might have bought something sub-par..
What block did he get? |
![]() |
![]() |
![]() |
#6 |
Cooling Neophyte
Join Date: Feb 2004
Location: Da NBH
Posts: 68
|
![]()
Thanks for the advice guys. Seeing those prices on ebay makes me think I might be able to talk him into actually ditching it then. He's only cooling the CPU and GPU, so figure a (heatercore + something like an MCW6000A + mcp650 + MCW50 + tubing) - the $100 or so he could get for it on ebay with the blocks.... Yes, I might get him into a real setup after all hehe.
Thanks for the help guys. |
![]() |
![]() |
![]() |
#7 |
Cooling Neophyte
Join Date: Sep 2004
Location: texas
Posts: 68
|
![]()
I've had several Koolance systems and modified them for better performance and efficiency, however those were all Case versions, not Exos. The Koolance cases have a major problem with the way airflow was set up, It's very restrictive and it also sucks hot exhaust air back in through the radiator. Oddly enough the reason they set up the airflow this way was because the pair of submerged pumps they use run off AC, and they use a transistor circuit and transformer on a controller board to generate this AC from the 12Vdc line. This controller board gets HOT, so hot in fact that without substantial airflow past it the thing melts down. The airflow path in the Koolance cases is deflected and diverted with a plastic sheet so that sufficient airflow ends up flowing past the controller board mounted on the rear roof of the case. If you remove the sheet to improve the airflow you will fry the controller board if you don't provide some other means of providing airflow to it. The simplest way to do that is use a power supply with a bottom fan such as an Enermax. Flip the supply over (you may need to file the mounting bracket a bit to get it to fit) and you will now get enough airflow past the controller board to keep it from overheating.
Now you can rip the Plastic airflow director sheet out and flip the fans over so they are all pulling air out of the case. This will substantially drop the temps of the water cooling system (as much as 10C or more) it also now will pull plenty of air past the harddrives to keep them cool (the Harddrive water blocks are a bad idea, I've lost several drives using them). You can now run the fans much slower and quieter and still achieve lower temps than before. Also you now have lots of airflow over the motherboard and cards where before there was almost none, unless you installed auxilary fans in the back of the case. None of this may apply to the Exos system however. I'm guessing that the performance that is desired is just to lower temps, and that fan noise is not an issue. The Koolance case and Exos systems pumps have a flow rate of 2L/min, or about 32 Gal/hr. This is a fairly low flow rate compared to most water cooling pumps, however if you use waterblocks that are efficient at low flow rates like the Swiftech it's not a major issue. The Exos radiator is fairly large and thin, this works well with lower airflow rates and axial fans that can't generate a lot of pressure differential. If you measure the temp of the air going into the radiator and the temp of it coming out it will give you an idea of how much room for improvement you can get by increasing airflow. The equation is T = 1.76*(Watts)/CFM where T is in Celsius so for 100Watts and 40 CFM the delta T will be 4.4 degrees C. If you double the airflow to 80CFM the delta T will drop to 2.2 degrees C, thus lowering the whole water cooling system temp by 2.2 C. If you increased airflow to 160CFM you would drop temps by 3.3 degrees instead. Note that if you can drop the air temperature going into the radiator by 3.3C (by keeping it away from hot air exhaust say) you get the same benefit as Quadrupling the airflow. More powerful pumps tend to benefit waterblocks that have small effective heat transfer areas, where high flow rates tend to cool the block off more because only a fraction of the water flowing through the block has a chance to contact the block and pick up heat on it's way through the block. Blocks where a large portion of the water flowing through contacts the block and picks up heat (like the Swiftech 6000) work well at low flow rates and benefit little from increased flow rates. Water has a huge thermal capacity. 140Watts will only raise the water temp by 1 C at a 2 Liter/min flow rate. Higher flow rates make almost no difference in this respect, they only help some waterblocks transfer heat to the water better, if you get a block that's efficient at low flow rates a higher capacity pump will not make for much system improvement. I'd suggest getting a thermometer and seeing where the largest temperature differentials in the system are and work on those first. My guess would be that better airflow (and making sure the incoming air is not hot) and possibly a better CPU block like the swiftech would be the cheapest and most effective improvements. I tend to dislike the Koolance systems because of the 80mm fans that make so much noise because of their RPM, but then I'm a silent type freak. Hope you find something usefull in here, or anybody else who crawls through this thread. |
![]() |
![]() |
![]() |
#8 | |
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
![]() Quote:
Of course I would love unregistered or pH to set me strait here as this is just off the top of my head which may be in my ass. ![]() |
|
![]() |
![]() |
![]() |
#9 |
Cooling Savant
Join Date: Jun 2004
Location: Florida
Posts: 414
|
![]()
he said double the airflow through the rad, not once did he reference the free-flow rating of a fan
__________________
"Employ your time in improving yourself by other men's writings, so that you shall gain easily what others have labored hard for." --Socrates "greenman100 = obnoxious ass hole"-gazorp |
![]() |
![]() |
![]() |
#10 | |
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#11 |
Cooling Savant
Join Date: May 2004
Location: Kingston, NY
Posts: 269
|
![]()
I'm with jaydee116 on this one. I'm not sure what he's getting at exactly. I understand everything he's saying, but where he's going with it....?
I don't think equations are particularly useful for anything other than theoretical exercises. So you take the thermal properties of air and you can figure out how much heat you could potentially dissipate in a perfect environment at a given air temperature and given air flow rate. It's great in theory, but you cannot calculate real life temperatures without knowing additional parameters. For instance, the actual air volume being pushed through the radiator, which will vary based upon the design of the radiator and static pressure of the fan, not just the volume it's rated for in free air. You won't know any of this without extensive testing in a controlled environment. Then you have to consider the thermal dissipation effeciency of the radiator, which again you won't know until you've tested for it. But then all of this was done in a controlled environment, so how accurate is it going to be in the real world? All of this testing will only allow you to figure out your maximum potential in a ideal setting. You're better off just estimating and trying things out because each system varies too much. |
![]() |
![]() |
![]() |
#12 |
Cooling Neophyte
Join Date: Sep 2002
Location: New York
Posts: 12
|
![]()
Did somebody say 'modified Koolance'?
![]() ![]() ![]() ![]() Nothing left from the original Koolance components except for the case itself, which now houses 2 separate cooling loops.
__________________
I Am The Glorified Bringer Of Thy Long Due Rest |
![]() |
![]() |
![]() |
#13 |
Cooling Neophyte
Join Date: Sep 2004
Location: texas
Posts: 68
|
![]()
Clearly a fan rated for 40 CFM in free air will flow less than that when put in a real system that has flow resistance through the radiator and the rest of the air path in the case. I refered to actual airflow through the system, not the free air CFM rating of the fans. I'm not saying that you can calculate exact results based on CFM ratings of fans. I was trying to clarify how the thermal system responds to increasing airflow, and to how to calculate numbers for an ideal system. Of course the systems we build are not ideal systems because of the fan CFM/backpressure curves and the thermal transfer characteristics of the radiator. However the equations can give you some reality checks on systems you are planning, especially in systems designed for quiet operation, where air velocities are lower and the system more closely approaches an ideal system.
1) Given a system, if you double the radiator area, and double the number of fans you will double the airflow through the system and reduce the coolant temperature above the ambient air temperature to roughly half what it was. 2) Since Fan CFM is directly related to RPM on a first order approximation, if you double the fan RPM you will double the airflow and half the temperature differential. This increases the fan noise greatly 3) If you reduce the fan RPM to 1/2, you'll halve the airflow and double the temperature differential. You will reduce the fan noise greatly. 4) If you double the radiator area, double the number of fans, but reduce their RPM to half you will end up with roughly the same system temperatures but much reduce fan noise. 5) If your coolant temperature is only 2C above ambient air temperature, no matter how fast you run your fans or how much radiator area you add you will not be able to reduce the system temps by more than 2C. 6) if your coolant temperature is 10C above ambient, then doubling your fan speed will roughly reduce your system temps by 5C. If you are intending to hook up an overclocked/overvolted AMD64 CPU,6800GT video card, and Northbridge chip that is dissipating 200W into BI pro radiator, a Panaflo L1A running at full rpm couldn't possibly pull better than 50 CFM through that radiator and thus your coolant will be at least 7 C above ambient air temp, if not more. The equations and all these examples are only to help you make prudent design decisions. If your coolant temperature is close to ambient air temperature already, adding fans and bigger radiators is not going to improve the system significantly. If your fans are too noisy, doubling the radiator size will let you halve their rpm and thus the noise. If your coolant temperature is significantly above ambient air temperature then the airflow through your system is poor because of fans, restrictions, or sucking hot exhaust air back in. Fix accordingly. Make use of the information as you see fit. |
![]() |
![]() |
![]() |
#14 | |||||||
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
![]() Quote:
Quote:
Quote:
Quote:
Quote:
Quote:
Quote:
|
|||||||
![]() |
![]() |
![]() |
#15 |
Cooling Savant
Join Date: Jan 2004
Location: Alberta
Posts: 631
|
![]()
The radiator is not the issue here... It's a pretty big radiator, and 3 80mm fans move plenty of air. The pumps and the block are the weak points. I say keep the case and the radiator and change the block, tubing and maybe the pump ($60-150 for that, and you've got a pretty watercooling case, a decent radiator, and fans)
|
![]() |
![]() |
![]() |
#16 |
Cooling Savant
Join Date: May 2004
Location: Kingston, NY
Posts: 269
|
![]()
I still say sell it and put the cash towards a real system. Otherwise you're flushing $200 down the drain for a fancy case and fairly sucky radiator.
|
![]() |
![]() |
![]() |
#17 | ||||||
Cooling Neophyte
Join Date: Sep 2004
Location: texas
Posts: 68
|
![]() Quote:
Quote:
Quote:
Quote:
Quote:
Quote:
Thanks for reading over my posts and bringing up points where I may not have been very clear in what I was trying to get across. |
||||||
![]() |
![]() |
![]() |
#18 |
Cooling Savant
Join Date: Jul 2003
Location: Michigan, USA
Posts: 456
|
![]()
Bigger radiators do not necessarily mean less water back pressure (and lets not confuse the fact that many "bigger" [ie. larger surface area] radiators also are thicker and have more air flow resistance) so bigger is not always better.
Component selection is very important and generalization of "facts" and figures/equations are only useful if most of the parts scale in some easily calculably way. They don't. Most of the time the performance is all over the board in regards to water flow resistance, air resistance, heat transfer capacity, weight, and bling-bling factor (oh and cost but hell cost sucks regardless.) Also, while you are correct in that the floor temp is the temp of the air going over the rad, you are forgetting that system temps change over time. Systems with larger rads general have a slightly better resistance to minor temp fluctations just from cunductive heat transfer (err I hope thats the one) Btw, the assumption that doubling the RPM = double airflow (on the same fan) is good on paper but neglects all sorts of air flow issues. Take a micro look at a fan in close proximity to the rad - and more specifically the output air from the rad. My empirical data doesn't support the doubling you seem to be seeing. Have you actually tested this or is it based on the physics of the motor and theoretical performance indexes and not realworld numbers?
__________________
Thou art God. |
![]() |
![]() |
![]() |
#19 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
ferdb
playing with numbers to pass the time do you have even one set of data to demonstrate anything at all ? tested an ideal system ? how about a non-ideal one ? tested anything ? what is the term for technospam ? nulltech ? bah I've probably tested 100 different kit combos in the last 90 days, and not a one of your approximations is valid but you did get it simple enough for your understanding congrats |
![]() |
![]() |
![]() |
#20 | |
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#21 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
it is not that approximations cannot be made, just that his are junk
-> he needs to describe HIS basis (source) for each of those approximations we will wait a while I suspect |
![]() |
![]() |
![]() |
#22 |
Cooling Neophyte
Join Date: Feb 2004
Location: Da NBH
Posts: 68
|
![]()
Okay before this becomes completely an argument concerning assumptions and how to predict fan rotational speed vs. airflow and all the assorted good stuff involved, lemme say thanks to everyone. Right now I'm in the middle of doing some hacking/prying/bending/cutting to switch it over to 2x120mm fans on the rad as he has a couple 120mm fans laying around. We're going to take a good look at how that affects things and depending on that, he's going to decide wether or not to start saving up for blocks/pumps for a 3/8" or 1/2" system. If he does that, I'm prolly going to point him in the direction of something like this or like 2xMCR120s. The transmission cooler matches dimensions of the rad in his exxos much better, and judging from what I've seen of them they would give closer to heatercore performance, but with the thickness being less than half of a normal core (and also a lower FPI count) it should perform better with an axial fan than a core.
|
![]() |
![]() |
![]() |
#23 |
Cooling Savant
Join Date: May 2004
Location: Kingston, NY
Posts: 269
|
![]()
Wicked. I'm getting a transmission cooler soon too. But one twice that size so I can fit 4 120mm fans.
|
![]() |
![]() |
![]() |
#24 | |
Cooling Neophyte
Join Date: Feb 2004
Location: Da NBH
Posts: 68
|
![]() Quote:
He was completely taken aback at the idea of using watercooling for computers, asked me if it would make his Dell run faster. Hehehe. |
|
![]() |
![]() |
![]() |
#25 | |
Put up or Shut Up
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
|
|