For a cheap pump, i don't believe that the inlet/outlet ratio really matters!

The main problem with what I suggested is that there would be a huge loss of pressure/flow, because the centrifugal effect is effectively bypassed: these pumps work by throwing the water around, and as above, it would only be paddling the water around. Not good.

As for flow reversing, I think that as long as the flow rate is high enough, it shouldn't matter in which direction it's going. If the flow is too slow, then yes, there would be that problem in the order of the components.
bigben2k is offline   Reply With Quote
Unread 10-25-2002, 03:45 PM   #27
Puzzdre
Cooling Savant
 
Puzzdre's Avatar
 
Join Date: Aug 2002
Location: Croatia
Posts: 969
Default

I see,

what if we put inlet up and outlet down not inline like the pic, to get half the circle, maybe some more centrifugal effect and get at least 1/2 of it?
__________________
'Out of cheese error...
...please reboot the universe (press the GBL to continue)'

Last edited by Puzzdre; 10-25-2002 at 03:55 PM.
Puzzdre is offline   Reply With Quote
Unread 10-25-2002, 03:53 PM   #28
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Same problem. It would only work if what you're talking about is actually 2 outlets, with a center inlet.

The water must be thrown around.
bigben2k is offline   Reply With Quote
Unread 10-26-2002, 12:31 AM   #29
Volenti
Cooling Savant
 
Volenti's Avatar
 
Join Date: Jan 2002
Location: in a nice cool spot
Posts: 427
GREAT RESULTS!!

Adding the second outlet and simply combining their output with a Y adaptor yeilds excellent results;






I have measured static head as well as just raw flow rate, should make the results a little more relavant.

un-modifed pump static head; 155cm (60.5'') (rated at 200cm)
modified pump static head single outlet; 198cm (77.2'')
modified pump static head dual combined outlet; 210cm (81.9'')

raw open flowrate is ~1100L/H, which from memory is slightly down on what the pump could do in stock condition, but that doesn't matter seeing as we now have more static head to play with now.

I also blocked the center inlet to see if it would pump this way (turning one of the outlets into an inlet) it does actually pump, but not with a lot of flow, or pressure,I didn't bother measuring it.
__________________
feel free to icq/msn me, I'm always willing to toss around ideas.

Last edited by Volenti; 10-26-2002 at 12:38 AM.
Volenti is offline   Reply With Quote
Unread 10-26-2002, 03:16 AM   #30
MadDogMe
Thermophile
 
MadDogMe's Avatar
 
Join Date: Aug 2002
Location: Just shut up ;) ...
Posts: 1,068
Default

**************************************
Quote:
un-modifed pump static head; 155cm (60.5'') (rated at 200cm)
modified pump static head single outlet; 198cm (77.2'')
modified pump static head dual combined outlet; 210cm (81.9'')
WOW!, I really expected it to be less when they were combined, I think some of it is the long legnth of the two tubes before they meet, stops the flow going out one side and back in the other, if they were shorter I think there'd be problems.

Would you try them with very short tubes Volenti?, to see what happens?, Please huh? ...

Last edited by MadDogMe; 10-26-2002 at 03:25 AM.
MadDogMe is offline   Reply With Quote
Unread 10-26-2002, 04:14 AM   #31
Volenti
Cooling Savant
 
Volenti's Avatar
 
Join Date: Jan 2002
Location: in a nice cool spot
Posts: 427
Default

Quote:
Originally posted by MadDogMe
**************************************
WOW!, I really expected it to be less when they were combined, I think some of it is the long legnth of the two tubes before they meet, stops the flow going out one side and back in the other, if they were shorter I think there'd be problems.

Would you try them with very short tubes Volenti?, to see what happens?, Please huh? ...
hmm, I shortened the tubes as much as I could (about half) reduced the static head by about 10cm (3'') but I did use 90 degree elbows to shorten the tubes, probably where the head loss came from...

however something else I observed while "playing" with the pump, was that as you progressively restrict the inlet, the water flow in the tube from the "weaker" outlet slows, stops, then goes backwards, re-circulating back to the pump, it appears that this mod may only be suitable for in-res use only, not in-line.
__________________
feel free to icq/msn me, I'm always willing to toss around ideas.
Volenti is offline   Reply With Quote
Unread 10-26-2002, 04:20 AM   #32
MadDogMe
Thermophile
 
MadDogMe's Avatar
 
Join Date: Aug 2002
Location: Just shut up ;) ...
Posts: 1,068
Default

Don't forget that inline rigs push the water into the pump inlet, I also wrote a bit about the inlet at OCAus that I did'nt do here...
MadDogMe is offline   Reply With Quote
Unread 10-26-2002, 04:25 AM   #33
MadDogMe
Thermophile
 
MadDogMe's Avatar
 
Join Date: Aug 2002
Location: Just shut up ;) ...
Posts: 1,068
Default

I'd also be interseted in what happens to the weaker vent when you introduce pressure/restriction to the outlet, whether it stays balanced or starts to do what you just mentioned. How would you test for it though, fit some blocks and rads inline and see what comes out the end?, if it's still got good pressure all's OK...

If it buggers up there's always the ratchet method, did you try it?, did it work and flip the right way?, or did it keep stalling the wrong way?...

PS, a valve/flap at the Y would work as well, when alls well it would be 'central, if the weak flow gets to low the strong one will force the valve shut. you'd have to make the Y & valve yourself but I'm sure it's 'doable' . worth it too if that's what it takes...

PPS, you could just use 'one way' valves in the two tubes that lead to the Y fitting , I don't know how restrictive they are though?. I'm sure we could make a 'passive' one that works of the water pressure according to flow direction, rather than a spring type one. would have near on zero restriction if made oversized bore wize...

Last edited by MadDogMe; 10-26-2002 at 04:34 AM.
MadDogMe is offline   Reply With Quote
Unread 10-26-2002, 04:39 AM   #34
Volenti
Cooling Savant
 
Volenti's Avatar
 
Join Date: Jan 2002
Location: in a nice cool spot
Posts: 427
Default

Quote:
Originally posted by MadDogMe
I'd also be interseted in what happens to the weaker vent when you introduce pressure/restriction to the outlet, whether it stays balanced or starts to do what you just mentioned. How would you test for it though, fit some blocks and rads inline and see what comes out the end?, if it's still got good pressure all's OK...

If it buggers up there's always the ratchet method, did you try it?, did it work and flip the right way?, or did it keep stalling the wrong way?...

PS, a valve/flap at the Y would work as well, when alls well it would be 'central, if the weak flow gets to low the strong one will force the valve shut. you'd have to make the Y & valve yourself but I'm sure it's 'doable' . worth it too if that's what it takes...
If we assume the combined water flow to be 100% the weak outlet is about 30% and the strong one 70% (roughly judging by eye in free flowing operation) block the weak one and the strong one goes to 95%, block the strong one and the weak one goes to about 55%.
[edit] only under special conditions will the "weak" outlet begin to become an intake, the spinning water in the pump still wants to escape, and if the que at the "strong" intake is too long it will do the almost 120 degree turn (loose energy) and leave via the weak outlet.[/edit]

I'm not sure how I'm going to test the flow in-line, mabie use the T peice thing after the pump to check pressure? may work...

[doh another edit] yea I'll look at the flap valve if the in-line testing turns sour, I'll be using a particularly restrictive in-line set up (like my current high pressure direct die block) so if there's an issue I'll find it.
__________________
feel free to icq/msn me, I'm always willing to toss around ideas.

Last edited by Volenti; 10-26-2002 at 04:48 AM.
Volenti is offline   Reply With Quote
Unread 10-26-2002, 04:47 AM   #35
MadDogMe
Thermophile
 
MadDogMe's Avatar
 
Join Date: Aug 2002
Location: Just shut up ;) ...
Posts: 1,068
Default

To check for adverse reactions under system pressure/restriction:

Try pinching off the weaker one, if flow improves it means water is flowing back throught it. if flow decreases alot you've pinched the good one, if it decreases a little you've pinched the bad one but all's OK cause it's still giving pressure.

Just make sure you put a good bit of restriction in the 'line' (block & rad, more preferably) before the exit where you see the flow/water come out.

***************************************

The only way to check inline is to watch the temps I think, or watch for cavitation, it should'nt make any difference between inline and submersed I think...
**Edited cause I'm an Idiot ...**
MadDogMe is offline   Reply With Quote
Unread 10-26-2002, 04:51 AM   #36
Volenti
Cooling Savant
 
Volenti's Avatar
 
Join Date: Jan 2002
Location: in a nice cool spot
Posts: 427
Default

Quote:
Originally posted by MadDogMe
Try pinching off the weaker one, if flow improves it means water is flowing back throught it. if flow decreases alot you've pinched the good one, if it decreases a little you've pinched the bad one but all's OK cause it's still giving pressure.

Just make sure you put a good bit of restriction in the 'loop' (block & rad, more preferably) before the exit where you see the flow/water come out.
I did that with the static head testing, both combined is about 3'' of head better than the "strong" outlet with the weak outlet blocked, but I will re-test that in the in line testing.

next question?
__________________
feel free to icq/msn me, I'm always willing to toss around ideas.
Volenti is offline   Reply With Quote
Unread 10-26-2002, 05:02 AM   #37
MadDogMe
Thermophile
 
MadDogMe's Avatar
 
Join Date: Aug 2002
Location: Just shut up ;) ...
Posts: 1,068
Default

We're gonna have to stop this 'editing' confusion ...

Did you try a headtest with restriction in the line?, put a really restrictive block and rad in the line after the Y, then try the 'pinch tests' and see how high the fountain is ...

Then when you try it in a 'closed loop' just watch for cavitation, if it's getting enough water pressure it'll be OK. I think it will as the output is pushing back into the inlet(I've heard it said it's better than submersed for flow because of this), as long as backpressure does'nt bugger things up...

Good luck dude!...
MadDogMe is offline   Reply With Quote
Unread 10-26-2002, 08:23 AM   #38
Volenti
Cooling Savant
 
Volenti's Avatar
 
Join Date: Jan 2002
Location: in a nice cool spot
Posts: 427
Default

BAH! I hooked the modded pump up to my direct die watercooling, and as it fired up and the bubbles slowly cleared I could see a line of bubbles going back down the "weak" outlet tube into the pump (water circulating around and around the pump and the Y)

My direct die block is a pretty extreme restriction, and I'm still getting sufficient flow through it, but it looks like my work's not over yet...
__________________
feel free to icq/msn me, I'm always willing to toss around ideas.
Volenti is offline   Reply With Quote
Unread 10-26-2002, 08:35 AM   #39
MadDogMe
Thermophile
 
MadDogMe's Avatar
 
Join Date: Aug 2002
Location: Just shut up ;) ...
Posts: 1,068
Default

I though this might happen under pressure! . the lenght of the tube to the Y is acting as a 'buffer', but as the pressure increases it becomes easier to pump back into the tube than to pump through the system ...

one way valves on the tubes would work. a ball bearing type thing would work well enough for our needs would'nt it?, a flap would be better cause it'd open up the whole tubes diametre, or the 'ball' valve could be oversized...
MadDogMe is offline   Reply With Quote
Unread 10-26-2002, 08:44 AM   #40
Volenti
Cooling Savant
 
Volenti's Avatar
 
Join Date: Jan 2002
Location: in a nice cool spot
Posts: 427
Default

Yea, oh well I'll look at a combined Y and valve setup tomorrow, see what I come up with.
__________________
feel free to icq/msn me, I'm always willing to toss around ideas.
Volenti is offline   Reply With Quote
Unread 10-26-2002, 08:59 AM   #41
MadDogMe
Thermophile
 
MadDogMe's Avatar
 
Join Date: Aug 2002
Location: Just shut up ;) ...
Posts: 1,068
Default

Did you try stopping the impellor from starting the wrong way yet?, does it flip back or not?...

It would be nice to build a mini reservoir and have little rubber flaps that covers each inlet, the pressure would either flip them open for the main flow, or close down for the bad one, they could be very pliable as well so they'd open easy enough without restricting, the system back pressure of the water itself would hold it shut from flowing the wrong way, bit like how a bicycle pump works, so there'd be no positive pressure valve to restrict the flow, they could both open up as well if there was'nt too much backpressure...

I'm pretty sure there are no~return valves that work off of the back pressure rather than having a spring involved, a 'passive no~return valve' maybe?. it's just a job of getting the size/flow~through of the valve right...

RS is a good place to start I 'spose ...

Last edited by MadDogMe; 10-26-2002 at 09:06 AM.
MadDogMe is offline   Reply With Quote
Unread 10-26-2002, 09:40 AM   #42
Volenti
Cooling Savant
 
Volenti's Avatar
 
Join Date: Jan 2002
Location: in a nice cool spot
Posts: 427
Default

hea I like the rubber flaps idea, will look into that.

I havn't looked into the ratchet yet, I feel it will prove to more trouble than it's worth.

/images of broken impellers...
__________________
feel free to icq/msn me, I'm always willing to toss around ideas.
Volenti is offline   Reply With Quote
Unread 10-28-2002, 03:19 AM   #43
MadDogMe
Thermophile
 
MadDogMe's Avatar
 
Join Date: Aug 2002
Location: Just shut up ;) ...
Posts: 1,068
Default

You could make the ratchet out of rubber too , it'd help the 'bounce back' effect ...

Had any joy finding low resistance no~return valves?, there lies the easiest path ...

What do you think of having the outlet shaped as a funnel? O>-*, instead of a circle with the outlet flush? O-* . do you think it'd improve matters?, or would the bulk of the water in the > part retard flow?...
It'd work either way though, that's the important part...

*The - part (barb) is supposed to be central, as in a standard configuration...
MadDogMe is offline   Reply With Quote
Unread 10-28-2002, 05:09 AM   #44
Puzzdre
Cooling Savant
 
Puzzdre's Avatar
 
Join Date: Aug 2002
Location: Croatia
Posts: 969
Default

Could something like this be made without being too restrictive?
Attached Images
File Type: jpg graphic2.jpg (16.7 KB, 50 views)
__________________
'Out of cheese error...
...please reboot the universe (press the GBL to continue)'
Puzzdre is offline   Reply With Quote
Unread 10-28-2002, 05:10 AM   #45
Puzzdre
Cooling Savant
 
Puzzdre's Avatar
 
Join Date: Aug 2002
Location: Croatia
Posts: 969
Default

assembled, with cuts in the rubber...
Attached Images
File Type: jpg graphic3.jpg (13.5 KB, 47 views)
__________________
'Out of cheese error...
...please reboot the universe (press the GBL to continue)'
Puzzdre is offline   Reply With Quote
Unread 10-28-2002, 05:30 AM   #46
MadDogMe
Thermophile
 
MadDogMe's Avatar
 
Join Date: Aug 2002
Location: Just shut up ;) ...
Posts: 1,068
Default

It might be restrictive if not oversized, if the rubber was'nt firm enough it'd leak, too firm and its not going to open up. I was thinking of a kindof 'catflap' that only opened one way, with just enough tensity to keep it in the closed position, you'd still have the full size of the bore with a flap. I'd try to incorporate it into an airtrap~fillpoint or small fitting, as I'm not keen on reservoirs...

It's a good idea though, never seen 'owt like it before...
MadDogMe is offline   Reply With Quote
Unread 10-28-2002, 06:40 AM   #47
Puzzdre
Cooling Savant
 
Puzzdre's Avatar
 
Join Date: Aug 2002
Location: Croatia
Posts: 969
Default

Yeah, I thought so... This would be a little on the hard side to incorporate into tube, if not ovesized. I know something like this is not so good, bu just adding another O between center and outer ring might make it a little stronger on holding water not going throug backwards. Although, added restriction comes in the way...

I just got inspired by the heart (human or animal) blood valves, so if anybody got those artificially made, go for it...

Sorry, this just got too morbid...

Back on the bright side
__________________
'Out of cheese error...
...please reboot the universe (press the GBL to continue)'
Puzzdre is offline   Reply With Quote
Unread 10-28-2002, 08:25 AM   #48
Puzzdre
Cooling Savant
 
Puzzdre's Avatar
 
Join Date: Aug 2002
Location: Croatia
Posts: 969
Default

Maybe something could be derived of this one... It could be made of two pieces of plexi, than glued together, but you would have to have the piece holding the rubber milled, glue the rubber, than glue second part (just with a barb) to first one...Now I see that that second one would have to be milled too, to give space to the rubber to flip open...hmmm....
Attached Images
File Type: jpg graphic4.jpg (21.4 KB, 50 views)
__________________
'Out of cheese error...
...please reboot the universe (press the GBL to continue)'
Puzzdre is offline   Reply With Quote
Unread 10-28-2002, 09:13 AM   #49
gmat
Thermophile
 
gmat's Avatar
 
Join Date: Mar 2001
Location: France
Posts: 1,221
Default

In hydraulic systems i've often seen this:
Attached Images
File Type: png valve.png (2.0 KB, 44 views)
gmat is offline   Reply With Quote
Unread 10-28-2002, 09:16 AM   #50
MadDogMe
Thermophile
 
MadDogMe's Avatar
 
Join Date: Aug 2002
Location: Just shut up ;) ...
Posts: 1,068
Default

Puzzdre!!, that's what I was thinking!, except have both outlets entering side by side, saves making two of them, there may have to be a lip between them, or have them both countersunk in abit, to stop the pressure from the 'good' one 'swirling' the flap up on the 'bad' one.

If the two outlets are side by side on the pump it could be 'built on' to the pump somehow. No!, scratch that!, I think a bit of distance from the pump is important to stop the impellor lifting the weak side, allow a distance for the pressure to diminish, the further H2o travels along the two tubes the greater the difference between the two heads becomes...

G~mat!, It'd be nice to have a 'passive' one, one that works on a 'slight' negative bouyancy of the ball and the backpressure, rather than a spring...

Last edited by MadDogMe; 10-28-2002 at 09:26 AM.
MadDogMe is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 10:07 PM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...