Unread 11-14-2004, 03:49 PM   #51
nikhsub1
c00ling p00n
 
nikhsub1's Avatar
 
Join Date: Jun 2002
Location: L.A.
Posts: 758
Default

Quote:
Originally Posted by pHaestus
I don't see any of their canadian distributors stocking the thermochills. I guess I'll need to order direct from DD.
You asked about North America? AFAIK, DD has an exclusive at least in the US on the Thermochill's. www.mountainmods.com has them too I believe (via DD). Ben Rising over at Mountain Mods is a very good guy.
__________________

*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*
E6700 @ 3.65Ghz / P5W DH Deluxe / 2GB 667 TeamGroup / 1900XTX
PC Power & Cooling Turbo 510 Deluxe
Mountain Mods U2-UFO Cube
Storm G5 --> MP-01 --> PA 120.3 --> 2x DDC Ultras in Series --> Custom Clear Res
"Artificial intelligence is no match for natural stupidity."
1,223,460+ Ghz Folding@Home
aNonForums
*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*'``'*:-.,_,.-:*
nikhsub1 is offline   Reply With Quote
Unread 11-14-2004, 04:01 PM   #52
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

I was looking at the DD resellers in canada for someone who might carry the thermochills. Figured I'd save on customs fees and shipping costs that way.
pHaestus is offline   Reply With Quote
Unread 11-14-2004, 07:05 PM   #53
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

Joe just PMed me from IRC that the madshrimps people (jmke and liquid3d) have been banned from the forums and their IPs are banned from even viewing this site. I apologize for the interruption in this discussion earlier. Hopefully it won't happen again.
pHaestus is offline   Reply With Quote
Unread 11-17-2004, 07:41 AM   #54
Incoherent
Cooling Savant
 
Join Date: Sep 2003
Location: Vallentuna, Sweden
Posts: 410
Default

(from Nexxos thread regarding PQ)
Quote:
Originally Posted by Cathar
To do it properly you really need to measure it.

For a "ballpark" though. Classic flow mechanics tells us that the level of flow resistance is proportional to the flow rate squared (P = Q ^ 2). This doesn't take into account turbulence and boundary layer conditions though.

For a fairly decent ballpark equation to extrapolate from OC.com's results I've personally found that P = Q ^ 1.85 offers a pretty decent approximation across the typical range of flow rates seen in water-cooling. P = pressure. Q = flow. Not as ideal as having real data, but when given a single pressure/flow point like OC.com I personally found it to give a fairly close ballpark curve.
Re the P=Q^1.85 fit, I think there is a better way.

I assume you are familiar with the idea of a "k-factor", I stumbled across it recently when exploring the flow measurement problem.
Your PQ curves are not behaving, shouldn't one be able to generate a constant which, even allowing for transitions between flow regimes and boundary conditions, is relatively flat across flowrate?. I am getting this with measured data, (see attachment) it is constant enough that I would propose that every block has a "K-factor", a constant encompassing restrictivity described by the equation: K=Q/sqrt(dP) or P=(Q/K)^2, essentially the flow rate squared relationship. It's probably your curve fit that I am seeing, it is not generating a constant. If it is real, that's very interesting, there's probably a way to extract a Reynolds number curve from it.

Sorry if I am being disruptive, I have not been following this closely but I thought the K-factor thing might be relevant. It for sure is another way to generate a PQ curve from a single data point...

Attached Images
File Type: gif 6000_g5_k.gif (7.9 KB, 65 views)

Last edited by Incoherent; 11-17-2004 at 08:10 AM. Reason: Wrong units in chart, kPa vs m H2O
Incoherent is offline   Reply With Quote
Unread 11-17-2004, 10:55 AM   #55
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

Quote:
Originally Posted by Incoherent
(from Nexxos thread regarding PQ)

Re the P=Q^1.85 fit, I think there is a better way.

I assume you are familiar with the idea of a "k-factor", I stumbled across it recently when exploring the flow measurement problem.
Your PQ curves are not behaving, shouldn't one be able to generate a constant which, even allowing for transitions between flow regimes and boundary conditions, is relatively flat across flowrate?. I am getting this with measured data, (see attachment) it is constant enough that I would propose that every block has a "K-factor", a constant encompassing restrictivity described by the equation: K=Q/sqrt(dP) or P=(Q/K)^2, essentially the flow rate squared relationship. It's probably your curve fit that I am seeing, it is not generating a constant. If it is real, that's very interesting, there's probably a way to extract a Reynolds number curve from it.

Sorry if I am being disruptive, I have not been following this closely but I thought the K-factor thing might be relevant. It for sure is another way to generate a PQ curve from a single data point...

yes, you are correct
I am in the process of converting all Swiftech flow resistance curves to a 'K-factor'

pH or Cathar
why not write an article on flow resistance characterization ? (yes, I'm lazy)
BillA is offline   Reply With Quote
Unread 11-17-2004, 11:58 AM   #56
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

Bill I have a question about dP measurement. It seems to me that the easiest way to deal with all the different possibilities of tubing and fittings and such is to:

1) zero the xmitter
2) Run a length of the tubing to be used over the flow range of interest (blank)
3) Cut the tubing in half, mount block/rad, and repeat (sample)
4) sample - blank = dP of only block/rad (this takes care of the dP of crosses and fittings and tubing and all leaving only wb).

Is that unnecessarily complicated? I was concerned that the friction factor of clearflex or silicone would be difft enough from copper pipe to make doing a calibration with just copper pipes of difft ID to be a mistake.
pHaestus is offline   Reply With Quote
Unread 11-17-2004, 02:26 PM   #57
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Hmmm, maybe some of you more engineering types could help me out to understand as I may have the following wrong (being self-educated and all on this stuff):

P=(Q/K)^2

seems to me to be simplification of Bernoulli's equation. However if we consider viscous head, being the energy that gets lost as heat (and absorbed into the liquid itself), then for turbulent flow the friction co-efficient of the viscous head term will fall away as the Reynold's number increases (which is proportional to the flow rate).

So what we then have is an effect where P=(Q/K)^2 isn't really followed cleanly. For the more restrictive blocks I intuitively would have thought that they would deviate even further from the classic P=(Q/K)^2 equation.

Now, quite true, Bernoulli's viscous equation consists of two primary terms, being the constant head loss due to inviscid flow (which is proportional to the flow rate squared), and the head loss due to viscous flow. The relative effect of viscous flow term diminishes as the flow rate increases, meaning that we end up with a curve that doesn't fit P=(Q/K)^2 any more.

I threw out P = Q ^ 1.85 as a really quick and dirty approximation of this effect, perhaps only valid for within 0.5 to 2.0x the data point given at somewhere like OC.com.

I measured various data points from 2.0 - 5.0LPM for the Storm/G4, and it didn't seem to me to quite follow a simple P=(Q/K)^2 curve.

That could also just be due to measurement error too.

Or perhaps one of you kind lads could tell me if viscous flow effects don't even apply here?
Cathar is offline   Reply With Quote
Unread 11-17-2004, 03:02 PM   #58
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

nothing is too simple once one gets into it

- the dP units are temp sensitive, if not temp controlled you'll need a zero reading at the start and end; use this to 'correct' the dP reading
(I would not suggest re-setting the zero, this is part of the unit's cal)

yes, your procedure is correct
I lay out the crosses flat on a table and connect them with a short piece of tubing, run a dP curve, then cut that tubing in half to connect wbs; then the single connection loss can be deducted from the wb reading at each flow rate

but you need to do this for each tubing size you will be testing with
BillA is offline   Reply With Quote
Unread 11-17-2004, 03:05 PM   #59
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

What about the fact that the tubing has a curve in it when the wb is connected, but is straight through w/o the block?
pHaestus is offline   Reply With Quote
Unread 11-17-2004, 03:44 PM   #60
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

Quote:
I threw out P = Q ^ 1.85 as a really quick and dirty approximation of this effect
Isn't that the same law used by the Hazen William equation?
lolito_fr is offline   Reply With Quote
Unread 11-17-2004, 05:49 PM   #61
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

Quote:
Originally Posted by pHaestus
What about the fact that the tubing has a curve in it when the wb is connected, but is straight through w/o the block?
nooo, the cross must/should (?) be close coupled to the wb/rad and that connection tube kept straight
- a bend will have an effect
BillA is offline   Reply With Quote
Unread 11-18-2004, 05:39 PM   #62
Uncle`BuZZ
Cooling Neophyte
 
Join Date: Oct 2004
Location: France
Posts: 28
Default

Quote:
Originally Posted by pHaestus
In MY opinion, the solution is to produce C/W vs flow data and dP vs flow data for waterblocks and a few common radiator/fan combos. Then to use that data along with the other components in the loop and the pump P-Q curves to predict a final C/W for the system. That is what groth was going for here:

http://pages.sbcglobal.net/water.gro...20process1.htm

The interface would have to be simplified a lot and it's awaiting my dP vs flow data...

It's waiting on my dP vs flow numbers to be generated; that's next up after this Alphacool nexxos XP review is done
I think we tried to do same thing in different way...


you can found my solution (version alpha) here (in french). I stopped development cause I miss data to put into my db...

you can define your loop with some tubing, radiator and waterblock, in series or what you want, you just need to drag elements where you want on the loop and see results...

You need the JVM from SUN and not the JVM from microsoft to use it. You could see some difference from your results because I probably haven't the same data of you (very few data in fact) but they should be minim.

In my dream I hoped to add some C/W data to do a prediction of performences, but I miss drop pressure data, so I don't imagine having enough C/W data... :shrug:
Uncle`BuZZ is offline   Reply With Quote
Unread 11-18-2004, 06:51 PM   #63
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

I am happy to open source all data. Let me get it in a reasonable format. I suspect dP vs Q numbers will be more useful to others and I'm in the process of fiddling w/ that now
pHaestus is offline   Reply With Quote
Unread 12-07-2004, 02:12 PM   #64
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

Danger Den most graciously sent me a Thermochill 120.2 radiator (thanks guys!)
I will buy some Papst fans (anyone have a source for the ones used in these simulated loops?) and then try to reproduce some of the dT vs pump results using our modeled cooling loop.
pHaestus is offline   Reply With Quote
Unread 12-07-2004, 02:38 PM   #65
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

good luck
correlating that systems stuff will be a chore, you'll have no 'free' time this xmas
BillA is offline   Reply With Quote
Unread 12-07-2004, 02:41 PM   #66
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

I am a dummy. Danger Den had the 4312L's in stock; should have gotten them to drop a few in the box. I ordered them just now and should have them next week.

I'm in research scientist mode still: NO correlation is still worth knowing right? LOL
pHaestus is offline   Reply With Quote
Unread 04-06-2005, 12:09 PM   #67
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

OK I am setting up the thermochill-based test loop tonight when I get home. I'll post an update when I get it running. The New AMD64 system I built for general testing will allow me to keep using my TBredB box for interesting stuff like this I hope.
__________________
Getting paid like a biker with the best crank...
-MF DOOM
pHaestus is offline   Reply With Quote
Unread 04-06-2005, 09:36 PM   #68
MaxxxRacer
Cooling Savant
 
MaxxxRacer's Avatar
 
Join Date: Sep 2004
Location: Los Angeles, Ca
Posts: 310
Default

dont kill the winnie man...
__________________

Excuse me, I believe you have my stapler.
MaxxxRacer is offline   Reply With Quote
Unread 06-06-2005, 09:34 PM   #69
plywood99
Cooling Neophyte
 
plywood99's Avatar
 
Join Date: Feb 2005
Location: Cincinnati, ohio
Posts: 39
Default

Quote:
Originally Posted by pHaestus
OK I am setting up the thermochill-based test loop tonight when I get home. I'll post an update when I get it running. The New AMD64 system I built for general testing will allow me to keep using my TBredB box for interesting stuff like this I hope.

Hope this hasn't died down. Looking forward to the results...
plywood99 is offline   Reply With Quote
Unread 06-25-2005, 05:51 PM   #70
YEP
Cooling Neophyte
 
Join Date: Jun 2005
Location: Scandinavia
Posts: 2

Quote:
Originally Posted by pHaestus
You guys are too damn clever. Now I suppose all that you need is pressure drop numbers for all the wbs I've tested right?
Not to be rude ..... sure "buddy"

This thread is really really nice. Good work you guys are doing.

When putting a new system together it's reall nice to have an idea how much pressure drops across a waterblock.

Again invaluable work you guys are doing for the community
YEP is offline   Reply With Quote
Unread 08-23-2005, 01:26 AM   #71
bobo5195
Cooling Savant
 
Join Date: Aug 2005
Location: uk
Posts: 400
Default

Nice work, the computer model saves me answering many questions.

I havent been able to find this information anywhere else:
What are the assumptions in the model though.
Is the friction from the pipe based on tubulent or lamina flow and is the small diameter and possible boundary layer problems consider (ie has boundary layer thickness been considered as a check).
When comparing different widths of pipes is the head loss coefficent from varying diameter considered. For example thermochills are 3/8ths but piping might be 1/2 (this might be taken into account by bills testing) and the inlet and outlet to blocks or pump.
bobo5195 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 12:59 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...