#101 | |
Pro/Guru - Uber Mod
Join Date: Sep 2002
Location: Indiana
Posts: 834
|
![]() Quote:
Try thinking through it again with a fixed quantity of heat being transferred. That heat being equal to the electrical energy dissipated in the die. (In actuality there will be heat drawn out of the motherboard, air, etc, but it's probably best to neglect these for the first pass at trying to understand what's going on.) Instead of the amount of heat changing, think in terms of how temperatures need to change in order to move that fixed amount of heat. |
|
![]() |
![]() |
![]() |
#102 |
Pro/Staff
Join Date: Oct 2001
Location: Klamath Falls, OR
Posts: 1,439
|
![]()
I actually was assuming a fixed heat load. I was trying to work with a fixed amount of heat being dumped into the cold side of the TEC and being moved out the hot side.
When you change the mass flow rate (and ignore things like laminar flow and such) the only thing that changes is the dT at both TEC and CPU. The question is why a TEC would move more heat when the dT between hot and cold sides of the TEC is larger. I was under the impression that a TEC is moves fewer BTUs when dT(TEC) is larger. |
![]() |
![]() |
![]() |
#103 |
Cooling Savant
Join Date: Mar 2002
Location: Mass
Posts: 185
|
![]()
You know I was thinking.... hehe happens sometimes ....
You have two options... High Flow which will create the copper to become cold by the water giving up its cold to the copper... In this you are overcoming the energy that the cpu is giving, very little movement of the energy through the water (I think at least)... Low Flow (impingement), which will create the copper to give up its heat to the water, in making the water warm... In this you are more or less moving the energy, absorbing and moving (block doesnt become as cold).... Unfortunately my theory makes no sense now that I think about it... The longer the water is in if it is cold enough to overcome the heat by a certain amount of X and then stays to absorb it for on a certain amount of time Y.... hmmm..... Now in each you have energy exchanging within itself always creates heat, which is very, very minimal here... Hmmm..... just thinking outloud... Its interesting though from what I have read about the High Flow vs Low Flow (Impingement) that High flow doesnt need a very good radiator and a Low Flow does.... (correct me if I am wrong please) Well guys tear it up hehehe... we need to get to the bottom of this and I am sure we can... we just need to find the formula's to use... Someone help me out with figuring heat exchange for the elements... copper and water....paweese! ![]() later guys..
__________________
fr33t3chi3 |
![]() |
![]() |
![]() |
#104 | |
Cooling Savant
Join Date: Mar 2002
Location: FL
Posts: 787
|
![]() Quote:
__________________
When you do things right, people won't be sure youv'e done anything at all. Looking to buy/trade for used Deep Fryer and Vacume Pack Sealer. |
|
![]() |
![]() |
![]() |
#105 | |
Pro/Staff
Join Date: Oct 2001
Location: Klamath Falls, OR
Posts: 1,439
|
![]() Quote:
Removing the same number of BTUs/Calories from different amounts of water will yield a different temperature. If 10g of water are moving through the chiller per second, then moving 10 calories of heat per second will lower the outgoing water temperature by 0.001C (check my figures on this calculation please!). Moving 1g of water through the same theoretical chiller would lower the outgoing water temp by 0.01C. Same amount of heat moved per second. Different amount of water being chilled per second. |
|
![]() |
![]() |
![]() |
#106 |
Thermophile
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
|
![]()
I must admit that I'm slightly perplexed about people talking about using ultra-low flow rates through a TEC chiller.
It doesn't make sense to me. TEC's are more efficient when their delta T between Tc and Th (cold and hot sides of the TEC) is low. Now, as many waterblock tests have shown, block performance (measured as C/W) improves as the flow rate goes up. This means that the dT within the TEC is lower, because the cold side is warmer, thereby raising its effiency. Even though it may seem somewhat counter-intuitive at first glance, the cold side being warmer is actually drawing more heat out of the water due to the increase in TEC efficiency. When one wants to build a TEC based chiller, we want to follow exactly the same principles as for cooling the hot side of the TEC. We want the cold side to be kept warmer than with a less efficient block. TEC dT will therefore drop, the TEC efficiency will go up, and more watts of heat will be pumped from the cold side to the hot side. Now that wattage is coming out of the water, hence the water will get colder, faster. Remember too, we're talking about closed loop systems, so it matter little what the entry/exit temperatures of the TEC chiller is. Over time, more watts are being drawn out of a fixed quantity of water than with a less efficient cold-side setup utilising ultra-low flow rates. |
![]() |
![]() |
![]() |
#107 |
Pro/Guru - Uber Mod
Join Date: Sep 2002
Location: Indiana
Posts: 834
|
![]()
Bill,
By any chance, can you tell us the dT between; chiller copper at the inlet barb, and chiller copper at the outlet barb? (And the conditions under which that dT was measured) Edit: By "conditions" I mean heatload and chilled water flowrate specifically. |
![]() |
![]() |
![]() |
#108 | |
Cooling Savant
Join Date: May 2002
Location: Da UP
Posts: 517
|
![]() Quote:
A tec will be operating at X efficiency using the hot side cooling, insulation, voltage applied as adjustable variables. This is the tec itself, not the efficiency of the cooling chamber. The cooling chamber is actually the applied load to the tec cold side (heat stored in the cooling chamber block). Slowing the flowrate will increase the load seen by the tec. Is this not the same thing you said quote "the cold side being warmer is actually drawing more heat out of the water due to the increase in TEC efficiency. " end quote But the tec is not drawing heat out of the water, it is drawing it out of the heat stored in the coldplate. Slowing the flowrate increases the stored heat in the coldplate. In a die waterblock you want this stored heat to be minimal for a low die temp but in a chiller you want this stored heat to be high in the coldplate. This is my logical understanding, please explain why I am off or on track. |
|
![]() |
![]() |
![]() |
#109 | ||
Thermophile
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
|
![]()
gone_fishin, allow me to dissect your post if you will:
Quote:
The greater the temp differental, the more the heat wants to flow back from the hot side to the cold side by natural forces of conduction as the TEC elements are essentially made out of metal. You are right when you say that the TEC's efficiency is affected by hot-side cooling, but to say so is only stating half of the issue. The efficiency, being watts moved, is really affected by Th - Tc. The minimum temperature achievable by the cold side is a side-effect of keeping the hot side cooler. This is a desirable thing, but really what's going on is that we've lowered Th, and Th-Tc remains essentially the same (given perfect insulation and identical heat loads). Quote:
Through increasing the water flow rate on the cold-side/cold-plate, we are increasing the TEC's cold-side temperature (because the water is always warmer than the TEC cold-side) due to an increase the thermal convectional transfer rate. In doing so, we raise Tc, and hence Th-Tc gets smaller, thereby improving the heat pumping efficiency of the TEC. Heat pumping, measured in watts, goes up, therefore there is an increased flow of heat energy moving from the water, to the cold side of the TEC (via whatever is sitting in between). Now I can't be sure if this isn't exactly what you were already thinking or not. It could very well be, just that I disagree with some of the terminology used. |
||
![]() |
![]() |
![]() |
#110 | |
Cooling Savant
Join Date: May 2002
Location: Da UP
Posts: 517
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#111 | |
Cooling Savant
Join Date: Sep 2002
Location: Atlanta, GA
Posts: 135
|
![]() Quote:
Originally, when a low flow block was mentioned i thought of some thing like the maze 4 ( confusing low flow and low resistance), so in a block like this there isn't as much turbulent flow as laminar and convective heat transfer. Therefore raising the flow would not cause such a great change in performance ( steeper (sp?) initial d(c/w)/d(flow) ). But in a block like the cascade or WW performance is better with higher velocity,sacrificing of higher possible flow. So If you used something like the Cascade Peltier sized to warm the cold plate wouldn't that work better? So in the end isn't this just another Flowrate disscussion ( note: that argument was ended saying more flow is always better ( as mentioned earlier)).
__________________
Epox 8RDA+ v1.1----------Tyan K8SDPro 1700+ JUIHB 0310XPMW (12.5x200Mhz@1.792v)--------2xOpteron246 (2Ghz 1MB L2) 2x256MB Kingston PC3000 (BH5?) 2-2-2-8 2.7v---2x512MB Corsair Reg.&ECC PC3200 ATi Radeon 9800Pro (stock, too hot)-----ATI RageXL WD800JB+WD2500JB-------WD1600JD Sony DVD/CDRW-------NEC 3520A Black Forton350W--------Antec TruePower2.0 550W EPS12v |
|
![]() |
![]() |
![]() |
#112 |
Cooling Neophyte
Join Date: Aug 2002
Location: Sweden
Posts: 63
|
![]()
The only thing that i can think of that is good with the low flow of the chilled water is if you gain more by the colder water than you gain with a higher flow that will lead to a more efficient heat removal from the die. But then the difference of the water entering/exiting the chilled loop of water has to be pretty high unless the WB is extremely well suited for lowflow/high pressure? :shrug: I think im way out of track here.
![]() Edit: Compare situation 1 and 2: #1 Heatload 50W, HS+Fan 0.5c/w, ambient temp 20 degrees C. Heatload temp = 45 degrees celsius. #2 Heatload 50W, HS+Fan 0.6c/w, ambient temp 10 degrees C. Heatload temp = 40 degrees celsius. Thats just a crude example of what im thinking atm, im probably completly lost.
__________________
Asus A7N8X Deluxe, 2500+@2700MHz (13,5x200), 2x256MB TwinMOS pc3200 @ 2-2-2-11, GFFX 5900 Ultra@500/950MHz, 2x120GB Maxtor Diamondmax 9 8MB SATA raid-0, Prometeia, Logitech z-680. 20000+ 3Dmark2001 Duron 600@1521MHz RIP Last edited by HMB; 09-26-2003 at 11:47 AM. |
![]() |
![]() |
![]() |
#113 | |
Cooling Savant
Join Date: May 2002
Location: Da UP
Posts: 517
|
![]() Quote:
Here we are arguing the flowrate for best chiller performance. The reverse is true in this situation. You want higher stored thermal energy in the cold plate at equalibrium for the detaT differential Cathar pointed out to raise efficiency of the tec. Lower flowrate does this. How this effects the whole system loop is another discussion. To me it seems clear that this approach will enable extremely low flows with the use of a tec to equal or better the use of a high flow pump without a tec. BillA's showing was of a unit that has dual tecs and dual coldplates and has shown data that looks promising (below ambient die temps). |
|
![]() |
![]() |
![]() |
#114 | ||
Pro/Guru - Uber Mod
Join Date: Sep 2002
Location: Indiana
Posts: 834
|
![]() Quote:
Quote:
Why use a TEC and two TIM joints to acheive 'max TEC efficiency' and dT of zero? Discussing "efficiency" of a TEC without reference to specific hot side and coldside temperatures is fairly meaningless IMO. |
||
![]() |
![]() |
![]() |
#115 | |
Pro/Guru - Uber Mod
Join Date: Sep 2002
Location: Indiana
Posts: 834
|
![]() Quote:
Some Kryotherm calcs with nothing changing aside from the ambient temperature input, yielded: (172 Watt TEC, 50 Watt heatload.) Ambient = 23C, Th-Tc = 42.6C Ambient = 33C, Th-Tc = 45.0C Ambient = 43C, Th-Tc = 47.8C TEC's are somewhat 'forgiving' of hotside temperature. These Kryotherm results are also consistent with other literature on TEC operation. Edit: Changed "53C" to "43"C. |
|
![]() |
![]() |
![]() |
#116 |
Cooling Savant
Join Date: Sep 2002
Location: Atlanta, GA
Posts: 135
|
![]()
We are trying to transfer heat to the baseplate to warm the tec( cold side). Using jet impingement rasies the Heat transfer value between the water and copper. So, since the water will always be warmer than the TEC's cold side ( as stated) the heat will try to go to the area that is colder (right?). So by increaseing the heat transfer you also increase the temp of the bp.
Also as an explanation of why it is always harder to cool something: Because of the laws of thermodynamics ( specificlly the 2nd i think) you will always make more heat than you remove causing more heat for you to remove. ( I think this statement is correct, my Chem teacher said some thing like this during our unit on thermodynamics I just exterpolated a little. )
__________________
Epox 8RDA+ v1.1----------Tyan K8SDPro 1700+ JUIHB 0310XPMW (12.5x200Mhz@1.792v)--------2xOpteron246 (2Ghz 1MB L2) 2x256MB Kingston PC3000 (BH5?) 2-2-2-8 2.7v---2x512MB Corsair Reg.&ECC PC3200 ATi Radeon 9800Pro (stock, too hot)-----ATI RageXL WD800JB+WD2500JB-------WD1600JD Sony DVD/CDRW-------NEC 3520A Black Forton350W--------Antec TruePower2.0 550W EPS12v |
![]() |
![]() |
![]() |
#117 | |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]()
I am going to change the topic here somewhat. If flow rate is reduced below a certain point, would water not freeze at the pins of the chiller? That seems pretty obviously a bad thing. But what if we are near that point and with laminar flow overall? Does that imply that there is a substantial amount of water that is staying in the chiller for longer times due to the velocity profile?
Quote:
Could be irrelevant or even incorrect but it is a thought I just had. I am still having an issue with how the change in peltier efficiency would offset dropping from turbulent to laminar flow regimes inside the CPU block anyway... |
|
![]() |
![]() |
![]() |
#118 |
Cooling Savant
Join Date: May 2002
Location: Da UP
Posts: 517
|
![]()
There is an important DeltaT that is not being considered here. That is the differential between coldplate/heatexchanger temp and temp of the water in contact with the heat exchanger. Greater efficiency in thermal transfer would coincide with a higher DeltaT here would it not?
This would mean that tec power would have to increase with increased flowrate to maintain an equal deltaT here when changing flowrate. If flowrate were reduced then the opposite would be true - tec power would have to be reduced to maintain an equal DeltaT. Does this shed light on the benefit of a lower flowrate in a tec chiller? Remember the coldness of the coldplate is not cooling the water, the heat is traveling through the coldplate and on up through the tec. |
![]() |
![]() |
![]() |
#119 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
Not got far, but for what it's worth:- ![]() and an unencouraging comparison of "Effect of Coolant Temp on C/W" with some of my predictions :- ![]() EDIT Using info(Cold-side Flow rate=2.417 lpm) from Switech Site* and raw MCW5002 test data have up-dated 2nd graph to include 25c result. * http://www.swiftnets.com/products/mc...sp#description Last edited by Les; 09-28-2003 at 07:58 AM. |
|
![]() |
![]() |
![]() |
#120 | |
Cooling Savant
Join Date: Dec 2002
Location: Houston, TX, USA
Posts: 221
|
![]() Quote:
Lowered flowrate results in a COOLER coldplate, as far as i can see. |
|
![]() |
![]() |
![]() |
#121 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
aiiii
I think the words on this page are cavitating sorry but I've not time to catch up "Lowered flowrate results in a COOLER coldplate", are we getting closer ? Les, help me here give me a (frothy ?) verbal description of that second graph (the first I would hazard represents 'reaL world' efficiency, as my uninsulated system was setup) |
![]() |
![]() |
![]() |
#122 | |
Cooling Savant
Join Date: May 2002
Location: Da UP
Posts: 517
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#123 | |
Cooling Savant
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
|
![]() Quote:
The predicted C/Ws are a composite of the calculations posted here: http://forums.procooling.com/vbb/sho...?threadid=6347 . The joined "calculated data points" are at the same flow rate. In that the Temp dependance of the Flomeric and Kryotherm "h" appear to be similar no differentiation is made betweeen wb type.. Your C/Ws simply calculated from "coolant temp", "die temp" and Watts.. Dunno whether your flow rate is constant but would conveniently explain the large discrepancy if was decreasing with coolant Temp. 2) Something like that. Last edited by Les; 09-26-2003 at 04:41 PM. |
|
![]() |
![]() |
![]() |
#124 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
ah so
#2 then is VERY enlightening pHaestus ? BTW, a 25% soln of antifreeze was used |
![]() |
![]() |
![]() |
#125 | |
Thermophile
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
|
![]()
Althornin, I know you understand the following, but I just wanted to expand upon the point you raised, I am not contradicting you.
Quote:
The non-intuitive flip here is that just because the cold-plate/water-block is cooler, this does not necessarily mean that the water will be colder. If the amount of heat being moved is the same, then what happens is just a large temperature differential between the cold-plate and the water. If we keep the cold-plate warmer, the TEC's efficiency picks up, and more heat gets moved from the cold to the hot side. Also, and VERY importantly, for a high flow rate the differential between the water and the cold side is MUCH less than with a low flow rate. Yes, the cold plate is warmer than with a low flow rate, but the water is also THAT much closer to the cold-plate temperature. Rather than mince words like the above description, this is why I tried to keep referring to the wattage moved. Don't think of things as temperatures, think of things as watts moved and then it makes sense when you keep in mind that you can't create/destroy energy. It is true that improving the hot-side efficiency tends to have a greater effect though, but the cold-side efficiency is still important. If you don't believe me, go to Kryotherm and type in some values for the cold-side C/W. The lower the C/W (more efficienct representing a higher flow rate), then the lower the equilibrium cold-chamber temperature, but the higher the cold-plate temperature. |
|
![]() |
![]() |
![]() |