Unread 10-04-2004, 10:53 PM   #1
MadHacker
Cooling Savant
 
MadHacker's Avatar
 
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
Default Building a RadBox but need a litle bit of help.

I have decided to make an external rad box for my system…
Currently in it is a P4 2.8Ghz o/c to 3.7Ghz

I currently have
D-Tek WW
polarFlo GPU block
DD 875p Chipset block.

And an MCP600 and Fedco#2-148 2 pass heater core.

Was thinking of putting 2 Fedco#2-342 single pass cores..
They are 9.5 x 6.125 x 2”
Hopefully they won’t cost too much…
I also have a spare MCP600 so I was thinking of putting them in series in the rad box…
But there are some things I’m not 100% sure about…
I figure I’ll make it out of 3/4” plywood…

My issues have to think about is fans or blowers? What would be better?
I was originally looking at 172mm Comairrotron fans. 4 of them undervolted would do an excellent job.
But how would I control them?
Right now I control my fans by using Orbital Matrix MX212. it would be nice to come up with some electronic circuit that would be able to adjust the high wattage fans with the lower power MX212. The fans are 1.5 – 2.5 amps each…and I would like to use one of the 1 amp 12 volt outputs to control the fans.

Suggestions for Fans or Blowers as well as ideas on how to control them would be greatly appreciated…
__________________
"Great spirits have always encountered violent
opposition from mediocre minds" - (Einstein)
MadHacker is offline   Reply With Quote
Unread 10-09-2004, 09:48 PM   #2
MadHacker
Cooling Savant
 
MadHacker's Avatar
 
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
Default

well i found out that the Fedco#2-342 heatercores i want will cost me $58.38cdn each. not to bad for a price...
also with help I found the fans I'll be using in the rad box.
I'll be using 4 Papst 6424/2H. 24 vdc running at 12 Volts
it will put out 280CFM at 24V
plan to buy that soon...
will keep yall posted of my progress...
__________________
"Great spirits have always encountered violent
opposition from mediocre minds" - (Einstein)
MadHacker is offline   Reply With Quote
Unread 10-17-2004, 03:21 PM   #3
Seyeklopz
Cooling Neophyte
 
Seyeklopz's Avatar
 
Join Date: Jun 2003
Location: Saint John, New Brunswick, Canada
Posts: 94
Default

Any idea how quiet the papst will be at 12v? It says 61db at 24.

Did you see the falcon? http://www.allelectronics.com/cgi-bi...gi?item=CF-190
Seyeklopz is offline   Reply With Quote
Unread 10-17-2004, 05:03 PM   #4
arterius
Cooling Neophyte
 
Join Date: Aug 2003
Location: europe
Posts: 18
Default

I have very similar fans and found them to be tolerable at 10,8v. specs
At 12v they are still loud and you would need a special fan controller to regulate the voltage because of the high amp draw.
The bearing noise will be your biggest problem after all and I estimate that my fans are in the 35dB range if turned down.
arterius is offline   Reply With Quote
Unread 10-17-2004, 05:15 PM   #5
Seyeklopz
Cooling Neophyte
 
Seyeklopz's Avatar
 
Join Date: Jun 2003
Location: Saint John, New Brunswick, Canada
Posts: 94
Default

I bought a 12VDC 8.5 Amp power supply from the same site. It's an open board, so I'm going to cage it in above the floor vent in my pc case. I'll run my fan and pelt from it.
Seyeklopz is offline   Reply With Quote
Unread 10-17-2004, 08:15 PM   #6
MadHacker
Cooling Savant
 
MadHacker's Avatar
 
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
Default

I just ordered the Pabst fans I have listed above..
I'll let you know how loud they are...
i do have a 4 port fanbus already so i plan to use it for the fans...
and a standard PC powersupply to power them...
__________________
"Great spirits have always encountered violent
opposition from mediocre minds" - (Einstein)
MadHacker is offline   Reply With Quote
Unread 10-17-2004, 08:33 PM   #7
agiacobbi
Cooling Neophyte
 
Join Date: Apr 2004
Location: TN, USA
Posts: 19
Default

Quote:
Originally Posted by Seyeklopz
Any idea how quiet the papst will be at 12v? It says 61db at 24.

Did you see the falcon? http://www.allelectronics.com/cgi-bi...gi?item=CF-190
How about this one, http://www.frozencpu.com/cgi-bin/frozencpu/fan-88.html
agiacobbi is offline   Reply With Quote
Unread 10-17-2004, 09:31 PM   #8
MadHacker
Cooling Savant
 
MadHacker's Avatar
 
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
Default

Quote:
Originally Posted by agiacobbi
but look at the price..
$39.99 for 1... i'll pay $15. for one and run it 1/2 the voltage...
I'd be running the one from frozencpu at 1/2 the voltage anyways...
to loud otherwise...
__________________
"Great spirits have always encountered violent
opposition from mediocre minds" - (Einstein)
MadHacker is offline   Reply With Quote
Unread 10-17-2004, 09:56 PM   #9
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

MH: What Canadian store did you find the 2-342 @ for that price? I imported one from US at $US 29.99 plus shipping but I could use another one...
pHaestus is offline   Reply With Quote
Unread 10-17-2004, 10:53 PM   #10
agiacobbi
Cooling Neophyte
 
Join Date: Apr 2004
Location: TN, USA
Posts: 19
Default

Quote:
Originally Posted by MadHacker
well i found out that the Fedco#2-342 heatercores i want will cost me $58.38cdn each. not to bad for a price...
also with help I found the fans I'll be using in the rad box.
I'll be using 4 Papst 6424/2H. 24 vdc running at 12 Volts
it will put out 280CFM at 24V
plan to buy that soon...
will keep yall posted of my progress...
Better make sure it will run at 12 volts, most 24v fans I have looked at need at least 16v
agiacobbi is offline   Reply With Quote
Unread 10-18-2004, 02:44 PM   #11
MadHacker
Cooling Savant
 
MadHacker's Avatar
 
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
Default

Quote:
Originally Posted by agiacobbi
Better make sure it will run at 12 volts, most 24v fans I have looked at need at least 16v
I considered that.. but the site states "12-28VDC COOLING FAN"
So i'm hoping it will power up ok at 12V... if not...
I will have to find an alternate powersupply...
Which would be unfortunate considering the number of PC power supplies I have at home...
__________________
"Great spirits have always encountered violent
opposition from mediocre minds" - (Einstein)
MadHacker is offline   Reply With Quote
Unread 10-18-2004, 02:49 PM   #12
Seyeklopz
Cooling Neophyte
 
Seyeklopz's Avatar
 
Join Date: Jun 2003
Location: Saint John, New Brunswick, Canada
Posts: 94
Default

You could get a 12v-24v transformer. I've also read that you can use a 5v and 12v line to make 17v. I'm not sure if I remembered that correctly, but a little research will do you good.

Edit: Here's the solution, and a good read. You can get a variety of voltages. 7, 17, 24 and a few others are possible, but you could just do 24, and use a rheo to lower it.

Last edited by Seyeklopz; 10-18-2004 at 02:59 PM.
Seyeklopz is offline   Reply With Quote
Unread 10-18-2004, 03:05 PM   #13
Caeberos
Cooling Neophyte
 
Join Date: Mar 2003
Location: New York
Posts: 32
Default

no, you cannot use a 5v line and a 12v line to create 17v, you can however use those two line to make 7v. That is if you use the 5v as a ground and the 12v as power. If you have a cheap ATX power supply lying around you can create an voltages from 3.3v up to around 24v if you wire it properly.

you can use a -5v line and a 12v line to make 17v. That is probably what Seyeklopz was talking about. I am not sure if my power supply has a -5v line on it, but I am sure it has a -12v line, and alot of other interesting things on the ATX connector. With a litttle creativity you can get all the voltages you need off an ATX supply.

Good Luck
Caeberos is offline   Reply With Quote
Unread 10-18-2004, 03:13 PM   #14
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Quote:
Originally Posted by Caeberos
... With a litttle creativity you can get all the voltages you need off an ATX supply....
...but not necessarily the power: the negative voltage lines are usually rated for 1 amp only.

Also, you'd have to have a load higher up for any of this to work. i.e. the 7 volt trick requires that you have a load on the +5 volt line, because current isn't allowed to flow back into a PSU on any other line than Ground: most PSUs will simply shut down.
bigben2k is offline   Reply With Quote
Unread 10-18-2004, 03:22 PM   #15
MadHacker
Cooling Savant
 
MadHacker's Avatar
 
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
Default

I was thinking the negative voltages would not have enough power...
and these fans seem to suck a lot of power in comparison to other PC fans I have dealt with in the past...
well I'm now in a wait and see mode...
one the fans come in I will hook them up and see if they power up...
if they do.. great.. if not I think i have a small 14 or 16 volt power supply I can test 1 fan on somewhere...
__________________
"Great spirits have always encountered violent
opposition from mediocre minds" - (Einstein)
MadHacker is offline   Reply With Quote
Unread 10-18-2004, 04:02 PM   #16
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

Are You Ignoring My Question Mr Hacker?

//edit: haha Joe disabled "all caps so it made the text look as above when I tried to be angry-faced
pHaestus is offline   Reply With Quote
Unread 10-18-2004, 04:15 PM   #17
arterius
Cooling Neophyte
 
Join Date: Aug 2003
Location: europe
Posts: 18
Default

I don't think that you need a spare psu or transformer at all.
My 8" rotor fans still have enough power to start properly with 11v.
I have also build a special fan controller that will give my fans 12v for a half a second and then reduce the voltage to the desired level.
All I can say is that these fans kick some ass combined with a heatercore.
arterius is offline   Reply With Quote
Unread 10-18-2004, 04:30 PM   #18
Seyeklopz
Cooling Neophyte
 
Seyeklopz's Avatar
 
Join Date: Jun 2003
Location: Saint John, New Brunswick, Canada
Posts: 94
Default

$15 12-28VDC 26 Watt, 6.75" x 2" (172 x 51mm), 133.3 cfm 61dba, Metal housing, 7 Blade fiber-glass reinforced plastic

$14 24 VDC 1.7 Amp, 6.75" x 2.16" (172 x 55mm), 300 cfm @3500 rpm 57 dba, 5 Blade Polycarbonate

Not Canadian, but a good price.

BTW, I LOVE that place, I was adding stuff to my shopping cart for almost 2 hours.
Seyeklopz is offline   Reply With Quote
Unread 10-18-2004, 04:36 PM   #19
MadHacker
Cooling Savant
 
MadHacker's Avatar
 
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
Default

Quote:
Originally Posted by pHaestus
Are You Ignoring My Question Mr Hacker?

//edit: haha Joe disabled "all caps so it made the text look as above when I tried to be angry-faced
I somehow completly missed the question... a little bit rushed in my replies at work...
I plan to buy the heatercores at a car part store called Lordco.
here is a link to their website.
don't know what they have on their site cause i never realy looked...
I found it easier to just go into the store and talk to them myself...

the heatercore they can get it itno their store in a few hours time... but i havn't purchased them yet so i'm not shure if they are copper yet...
they did mention that a lot of them are being made out of alluminum...
I'm just waiting on some $$$ so i can take a look at them before I purchase them...
__________________
"Great spirits have always encountered violent
opposition from mediocre minds" - (Einstein)
MadHacker is offline   Reply With Quote
Unread 10-18-2004, 04:49 PM   #20
MadHacker
Cooling Savant
 
MadHacker's Avatar
 
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
Default

Quote:
Originally Posted by Seyeklopz
the 133.3 cfm 61dba, Metal housing fan is the one i ordered. (4 of them)
but the listed specs are listed wrong on the site...
280CFM at 24V is what they will do...
Just curious what they will do at 12V how loud and how much CFM?
__________________
"Great spirits have always encountered violent
opposition from mediocre minds" - (Einstein)
MadHacker is offline   Reply With Quote
Unread 10-18-2004, 05:33 PM   #21
Big Player
Cooling Neophyte
 
Join Date: Sep 2004
Location: eff that
Posts: 16
Default

Quote:
Originally Posted by Seyeklopz
Not Canadian, but a good price.

BTW, I LOVE that place, I was adding stuff to my shopping cart for almost 2 hours.
Just had a browse through there...does indeed look like a useful place. I'd heard of it before, but never checked it out.
__________________
'Iron rusts from disuse;
stagnant water loses its purity
and in cold weather becomes frozen;
even so does inaction sap the
vigour of the mind.'
- Leonardo da Vinci
Big Player is offline   Reply With Quote
Unread 10-19-2004, 09:01 PM   #22
Seyeklopz
Cooling Neophyte
 
Seyeklopz's Avatar
 
Join Date: Jun 2003
Location: Saint John, New Brunswick, Canada
Posts: 94
Default

Damn, if I had known it did 280 cfm, i would have got it! Got the other one, and i will need to trim the edges to fit in the top of my case... damn lian-li and their internal structure
Seyeklopz is offline   Reply With Quote
Unread 02-13-2005, 04:48 PM   #23
MadHacker
Cooling Savant
 
MadHacker's Avatar
 
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
Default Building a RadBox (update)

Well I got some work done on my radbox.
here are some pictures
I got the 4 fans mounted as well as the heatercores.
I set up the box so that the top and the one side is removable for easy maintance.


Front filters are easy to remove for cleaning. dishwasher safe too


Top removed... lots of space to work in. but once I get all the stuf in it will be a little bit crowded.


with side removed as well... lots of space to work...


I was thinking of using mCubed T-Ballancer as a fan controller since it can be used as a stand alone system link here
the reviews seem to be good.

also going to do the MCP600 R.P.M Signal Mod so I can better monitor the flow.

// edited to fix image links
__________________
"Great spirits have always encountered violent
opposition from mediocre minds" - (Einstein)

Last edited by MadHacker; 03-13-2005 at 04:15 AM.
MadHacker is offline   Reply With Quote
Unread 02-13-2005, 05:04 PM   #24
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Holy moley. That's just a little bit of fannage there.

Y'know, with all that radiator frontal area it would actually be pretty easy to achieve a very effective 100CFM using just a pair of very quiet fans, but hey, I'm a noise-nut.
Cathar is offline   Reply With Quote
Unread 02-13-2005, 05:52 PM   #25
MadHacker
Cooling Savant
 
MadHacker's Avatar
 
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
Default

Quote:
Originally Posted by Cathar
Holy moley. That's just a little bit of fannage there.

Y'know, with all that radiator frontal area it would actually be pretty easy to achieve a very effective 100CFM using just a pair of very quiet fans, but hey, I'm a noise-nut.
Actualy at 6 volts they make no noise what so ever...
none that I can hear...
and that is whith my ear 1 foot away...
and it still moves some air...

my last heatercore was 10"x6"x2.5" cooled pretty good untill I put a prescot CPU in.
Then my water temp went up 5 deg and that was with 4 120mm(evercool) fans running at 100%(push pull)
With overkill maybe I can get my water temp closer to ambient
__________________
"Great spirits have always encountered violent
opposition from mediocre minds" - (Einstein)
MadHacker is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 05:14 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...