Unread 11-17-2004, 07:12 PM   #176
Uncle`BuZZ
Cooling Neophyte
 
Join Date: Oct 2004
Location: France
Posts: 28
Default

Quote:
Originally Posted by Cathar
While we're also discussing pressure drops and their impact on flow rates (/me cheers as this is really what all this stuff is about), we also need to consider that radiators are not static with respect to varying flow rates too.

Throw in a super restrictive block and peg the flow rates back by 20-30%, and if you're already operating just below the 1gpm mark, this will make a significant difference in the performance of heater-core style radiators:

http://thermal-management-testing.com/Thermo12.gif

Ideally we don't want to be falling much below 0.70gpm/2.5LPM if we can help it, even for a weak pump like an Eheim 1046.
The graph you put here isn't an evidence of your argument : the constant in the test is the coolant/air differential, so when you put more water into the radiator, you put more heat, so it is evident that radiator dissipated more heat. It doesn't mean than the radiator has a better efficiency with more flow !

We need same graph but with a constant power as a CPU will put the same power in water in a high or a flow rate. So the coolant/air differential will increase when flow decrease...

And the EHEIM1048 and 1046 are used for low flow since they are quiet and resistant, but their PQ curve aren't really good for high pressure. Try the same test with the Laing DDC and D4 (maybe results will be the same, but I dont think EHEIM are representative of good pumps for high drop pressure)

EDIT: sorry if this point was already discussed, I realize I havent read half of the topic yet !

EDIT2 : IMO, most users mix "low flow" with "µchannel". In commercial blocks which use "µchannel", the pressure drop is very high so the "low flow" is a direct effect. But it's not the "low flow" which is efficient but the "µchannel". As you all know, same block will always be more efficient with higher flow (without dealing with the pump and his power). If you look at the tests of roscal's blocks (named "proto") you can see an example of a real "µchannel" (0.3 mm) whith a PQ curve very different of all other µchannel blocks ( http://www.cooling-masters.com/image...pdc_blocs1.png )

To my mind, the good way is in this direction : µchannel to increase the exchange surface and decrease the layer (in a 0.3mm channel, the layer can't be more than 0.15 mm ) but without adding restriction like the nexxos or 1a blocks with "stupid" way for water.

Last edited by Uncle`BuZZ; 11-17-2004 at 07:44 PM.
Uncle`BuZZ is offline   Reply With Quote
Unread 11-17-2004, 11:17 PM   #177
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Quote:
Originally Posted by Uncle`BuZZ
The graph you put here isn't an evidence of your argument : the constant in the test is the coolant/air differential, so when you put more water into the radiator, you put more heat, so it is evident that radiator dissipated more heat. It doesn't mean than the radiator has a better efficiency with more flow !
I think you need to read the source article: http://thermal-management-testing.com/ThermoChill.htm

Radiators do improve in efficiency with increasing flow rates.

This fact invalidates the following section of your response.

Quote:
We need same graph but with a constant power as a CPU will put the same power in water in a high or a flow rate. So the coolant/air differential will increase when flow decrease...

And the EHEIM1048 and 1046 are used for low flow since they are quiet and resistant, but their PQ curve aren't really good for high pressure. Try the same test with the Laing DDC and D4 (maybe results will be the same, but I dont think EHEIM are representative of good pumps for high drop pressure)

EDIT: sorry if this point was already discussed, I realize I havent read half of the topic yet !
Cathar is offline   Reply With Quote
Unread 11-18-2004, 03:20 AM   #178
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

The pink line on BillA's graph gives you this, if you keep power constant:



btw, would really like to see pHaestus test the 0.3mm proto
lolito_fr is offline   Reply With Quote
Unread 11-18-2004, 04:56 AM   #179
Incoherent
Cooling Savant
 
Join Date: Sep 2003
Location: Vallentuna, Sweden
Posts: 410
Default

Quote:
Originally Posted by Cathar
Radiators do improve in efficiency with increasing flow rates.

Undoubtedly...

Why?

Muse...

...ignore me.
Incoherent is offline   Reply With Quote
Unread 11-18-2004, 05:42 AM   #180
Uncle`BuZZ
Cooling Neophyte
 
Join Date: Oct 2004
Location: France
Posts: 28
Default

Quote:
Originally Posted by Cathar
I think you need to read the source article: http://thermal-management-testing.com/ThermoChill.htm

Radiators do improve in efficiency with increasing flow rates.

This fact invalidates the following section of your response.
Maybe I missed something, and I believe that radiator are more efficient with more flow... but the graph you put isn't an asnwer. The answer is given by the graph posted by lolito_fr.

All graphs on the HE 120 series test page are based on a 5°C coolant/air differential.

As input is equal to coolant/air differential * specific heat capacity of coolant * mass flow rate when you modify the flow with a constant coolant/air differential you modify the input, so with more flow you introduce more heat in the rad, so the results is evident : rad dissipated more heat, but it doesnt mean than a rad with the same input but with more flow will disspated more heat (this appears to be right as shown by the graph dt vs flow at 71 W)

1 Watt = 1 J/s
cp = 4185 J/kg/°C (depends of temperature, but very few changes)

lpm/60 gives liters per second
1 liter of water is about 1 kg

so lpm/60 * cp * delta T gives kg/s * J/kg/°C * °C = J/s = W

On the graph you posted :

at 2 lpm, you have 2/60 * 4185 * 5 = 697.5 W in input
at 10 lpm, you have 10/60 * 4185 * 5 = 3487.5 W in input

(hum, it's amazing, maybe i missed something because they are great values, am I wrong ?)

Ok, I got it , I keep my wrong reasoning to show you how I am stupid and to let you understand what I meant. After reading of the article, the delta T isn't between inlet air and inlet coolant but between inlet air and the average temp of coolant resulting of dissipation, so it doesn't mean the input is directly proportional to flow as I believed.

But I dont understand your quote : my sentence "We need same graph but with a constant power as a CPU will put the same power in water in a high or a flow rate. So the coolant/air differential will increase when flow decrease..." is true to my mind, and it's exactly the graph posted above. The answer is evident on this graph, not on your where we don't know nothing about input.
Uncle`BuZZ is offline   Reply With Quote
Unread 11-18-2004, 05:49 AM   #181
Uncle`BuZZ
Cooling Neophyte
 
Join Date: Oct 2004
Location: France
Posts: 28
Default

Quote:
Originally Posted by lolito_fr
btw, would really like to see pHaestus test the 0.3mm proto
Me too , but I don't think rosco will never let someone doing some tests on his block if he isn't in same room, and I think the cost for posting a block with a rosco in the same packet to pH is too much for what pH could receive by paypal
Uncle`BuZZ is offline   Reply With Quote
Unread 11-18-2004, 06:12 AM   #182
Cathar
Thermophile
 
Cathar's Avatar
 
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
Default

Quote:
Originally Posted by Uncle`BuZZ
The answer is evident on this graph, not on your where we don't know nothing about input.
Don't know input? Huh?

The graph shows exactly what the input is to sustain the 5C air-water temperature delta at equilibrium.

All the information that is on the graph that I presented from BillA's excellent article is enough to formulate a C/W graph for the radiator's performance with respect to flow rate - simply divide 5C by the input power (watts) shown to arrive at the C/W for that flow rate.

Multiple the resulting C/W axis by the CPU watts (71W) and you would arrive at the exact same graph as lolito_fr presented above.

I don't believe you are stupid. I am glad that you are thinking about it deep enough to get yourself perhaps a little confused, but that's a good thing. A least you're thinking!
Cathar is offline   Reply With Quote
Unread 11-18-2004, 06:31 AM   #183
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

Buzz, not sure who is more confused after reading your post- you or me?
You cannot say that Bills' (not Cathars) graph is wrong and mine is correct - as my graph is just a different interpretation of this one:
http://thermal-management-testing.com/Thermo12.gif

Saying that BillA or Cathar is incorrect is heresy - you had better have some concrete evidence if you were to make such a claim, lol.

edit: too slow. Cathar, thx for explaining the math for me
lolito_fr is offline   Reply With Quote
Unread 11-18-2004, 07:02 AM   #184
Uncle`BuZZ
Cooling Neophyte
 
Join Date: Oct 2004
Location: France
Posts: 28
Default

Quote:
Originally Posted by lolito_fr
You cannot say that Bills' (not Cathars) graph is wrong and mine is correct
I didnt say the figures or the graph are wrong, I said I don't see on the graph posted by cathar what he said : radiators are more efficient with more flow, because in reality, we have the same input and the difference between high and low flow is only the flow and not the power to dissipate.

What I don't see is how the average temp of coolant is representative of the input... I don't see the input in the graph.

It's the average term who confuses me... I dont see what it represents... the temp on outlet coolant is talking to me, as the delta T between inlet and outlet, but not the average... because you can have the same average with 10 and 4 °C and 8 and 6°C

inlet coolant temp and flow give the input, delta T between inlet and oultlet with flow give the power dissipated, but I dont see what represents the average temp...
Uncle`BuZZ is offline   Reply With Quote
Unread 11-18-2004, 10:34 AM   #185
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

Hmmmm. I think I see now...

I think you were saying that it looked as though the increased power at higher flow rates was because the liquid was not cooling down as much, so the average fluid temp was higher?

So the increased rad efficiency as flow increases would be clearer if the difference between the inlet and outlet fluid temp was very small (ie negligeable)?

Edit: Oops. The fact that the average fluid temp is higher for increased flow rates is one reason why the rad is more efficient. Bleh.



So my question now: how does Bill regulate the average fluid temp in the rad?

Last edited by lolito_fr; 11-18-2004 at 11:20 AM.
lolito_fr is offline   Reply With Quote
Unread 11-18-2004, 12:26 PM   #186
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

avg temp NOT regulated
the 5°C deltaT is air inlet -> coolant inlet
the LMTD (Tm) is calculated per the std eq
BillA is offline   Reply With Quote
Unread 11-18-2004, 01:09 PM   #187
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

ok, that makes sense.
It does now make me wonder if we're using your graphs correctly to predict overall system temps, seeing as the liquid side dT across the rad will be adding to the rad dT ??

maybe I'm just looking too close...
lolito_fr is offline   Reply With Quote
Unread 11-18-2004, 02:38 PM   #188
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

all my testing prior to Swiftech was the bench testing of components, and my focus was on identifying a procedure that would distinguish the capability differences

the data is adaptable to system's characterization, but may need some adjustment

I must admit to not spending any time on systems performance prediction, I just test the components together to arrive at a system C/W
N.B. systems C/Ws must be measured at the max heat load

when you fellows think that you have a viable prediction scheme
-> work out what the number might be for a Swiftech kit;
then you can compare to the measured value on the site

this should be fun
BTW, I have values for both the MCW650 and the other unannounced pump so this pump heat business can be objectively assessed
- and I'm not adverse to helping Bruce, I could test the MCP600 if needed
BillA is offline   Reply With Quote
Unread 11-18-2004, 02:44 PM   #189
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

Quote:
Originally Posted by lolito_fr
ok, that makes sense.
It does now make me wonder if we're using your graphs correctly to predict overall system temps, seeing as the liquid side dT across the rad will be adding to the rad dT ??

maybe I'm just looking too close...
The equation I would use, for total dT of the system with respect to " inlet air", is :
dT(cpu-air) = dT(cpu-water) + W(wb+pump)x"C/W"(rad) - W(wb+pump)/(69.5466x flow(lpm))

Bloody hard work using the beermat method.

Edit: Changed + for - sign to account for direction of heat flow.

Last edited by Les; 11-18-2004 at 03:46 PM.
Les is offline   Reply With Quote
Unread 11-18-2004, 02:56 PM   #190
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

Bill, that sounds like fun indeed. Nice little homework project
Les, thats not what I wanted to hear (the W(wb+pump)/(69.5466x flow(lpm)) bit)
I was thinking that the 2 LMTD's (rad & waterblock) "cancelled" each other out. (lets just forget pump heat here for a minute!)
I will draw a diagram



I must be missing something!!

edit: just using simplified LMTDs for the example
edit2: replaced "LMTD" by "average". suspect this has something to do with it(?)

Last edited by lolito_fr; 11-18-2004 at 03:21 PM.
lolito_fr is offline   Reply With Quote
Unread 11-18-2004, 03:37 PM   #191
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

Thanks for diagram; have changed a "+" for a "- " sign

Last edited by Les; 11-18-2004 at 03:54 PM.
Les is offline   Reply With Quote
Unread 11-18-2004, 03:47 PM   #192
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

Is W*wb/(69.5466x flow(lpm)) not already accounted for in the dT(cpu-water) ?

Edit: No, because pH gives the dT between CPU and water inlet
Damn. so my graphs are wrong.

Last edited by lolito_fr; 11-18-2004 at 03:58 PM.
lolito_fr is offline   Reply With Quote
Unread 11-18-2004, 03:59 PM   #193
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

Do not think so.
All Bill's "C/W"s are with respect to inlet temperature.
pHaestus's dTs are with respect to inlet temperature.
Will have a rethink(easy to get confused), but think I am right

Edit: Yes; I think your edit is correct

Last edited by Les; 11-18-2004 at 04:05 PM.
Les is offline   Reply With Quote
Unread 11-18-2004, 04:07 PM   #194
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

I can provide water avgs (or LMTD) if needed.
pHaestus is offline   Reply With Quote
Unread 11-18-2004, 04:10 PM   #195
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

All Bill's "C/W"s are with respect to inlet temperature.

Now I am confused. "the LMTD (Tm) is calculated per the std eq" Does this not mean the graph is corrected for 5°C LMTD?

pH, Thx but I think we can manage as long as we know exactly what is measured/reported
lolito_fr is offline   Reply With Quote
Unread 11-18-2004, 04:17 PM   #196
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

Quote:
Originally Posted by pHaestus
I can provide water avgs (or LMTD) if needed.
I think the equation
dT(cpu-air) = dT(cpu-water) + W(wb+pump)x"C/W"(rad) - W(wb+pump)/(69.5466x flow(lpm))
gives system dT from the existing data.
However. with my continual insistence of complicating, I am not happy with using a constant "wb extracted" heat or pump heat.
Still believe "wb extracted heat" changes with "C/W" - something like one of these curves image

Last edited by Les; 11-18-2004 at 04:23 PM.
Les is offline   Reply With Quote
Unread 11-18-2004, 04:30 PM   #197
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

ugh. I think the pump heat thing we can just about cope with (input power vs flow?) but the cpu secondary losses...

edit: the cpu is not part of the cooling system - the system C/W is independent.

Last edited by lolito_fr; 11-19-2004 at 03:45 AM. Reason: meant cpu not wb secondary losses
lolito_fr is offline   Reply With Quote
Unread 11-18-2004, 04:34 PM   #198
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

I am just being awkward
Les is offline   Reply With Quote
Unread 11-18-2004, 04:39 PM   #199
Uncle`BuZZ
Cooling Neophyte
 
Join Date: Oct 2004
Location: France
Posts: 28
Default

the zern PQ+ could be a good target for a futur test to see a µchannel block without useless drop pressure.
Uncle`BuZZ is offline   Reply With Quote
Unread 11-19-2004, 06:47 AM   #200
lolito_fr
Cooling Savant
 
Join Date: Dec 2003
Location: France
Posts: 291
Default

yep. pity that Rosco and pH only have 2 hands

Quote:
when you fellows think that you have a viable prediction scheme
-> work out what the number might be for a Swiftech kit;
then you can compare to the measured value on the site
Have we got figures for the rads used in those kits?

the 676 looks like a stretched Miracle Midget Wonder (on this page)

the MCR120 looks like a BIX, but thinner?
lolito_fr is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 01:38 PM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...