Go Back   Pro/Forums > ProCooling Technical Discussions > General Liquid/Water Cooling Discussion
Password
Register FAQ Members List Calendar Chat

General Liquid/Water Cooling Discussion For discussion about Full Cooling System kits, or general cooling topics. Keep specific cooling items like pumps, radiators, etc... in their specific forums.

Reply
Thread Tools
Unread 11-16-2003, 10:12 AM   #1
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default Must read info on Swiftech MCP600 pumps

I want to make sure everyone is aware of an issue that has cropped up recently where some MCP600 pumps are dying after a few weeks of use. I have seen a quote directly from Bill Adams at Swiftech on this issue:

“The problem affecting 2-3% of the pumps has been identified as a failure of the thrust bearing (a Ryton washer) between the impeller and the front shaft support hub (the pump motors are fine)
- the hub is being redesigned to utilize a ceramic bearing face

In the meantime, failed pumps are being replaced with a new pump head assembly having a slightly reduced diameter impeller
- this reduces the deadhead pressure capability ~0.5m, the actual effect on the CPU temp will not be noticeable in most systems.

when the revised pump heads are available they will be provided to all who wish them w/o charge of course.”

from here


So at this moment performance of the MCP600 may be slightly less than the pump that I have been testing. If so, though, you will be able to eventually get a new pump head from Swiftech at no charge that will return your pump to its rated performance.

I still am recommending this pump (and in fact I am running the MCP600 in my main PC), but I recommend that you ask retailers whether the pump is the original version, the temporary fix version, or the redesigned ceramic bearing face version. You want one of the latter two.

I can't fault Swiftech for the way they've handled this issue though. Bill actually even did a tolerable job of customer service (someone check the thermostat in Hades, please).
pHaestus is offline   Reply With Quote
Unread 11-16-2003, 11:10 AM   #2
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

unfortunately there is no way that a retailer can identify the original pumps from those with the 'temporary fix' as the pump heads look quite the same

all pumps shipped from Nov. 10 have the cut down impeller, and this will continue for some time
these pumps will not fail

for any RMAed pumps we are mailing a replacement pump head, no need to return the motor (zero failures)

the conversion of the thrust bearing to ceramic is rather involved and because of the tooling will not occur for some weeks
- when these pump heads are available they will be sent to all purchasers who wish them

on a positive note, the changes implemented a month ago to reduce the motor noise have been VERY effective, the pump now compares quite well to an Eheim 1048, and better than a 1250

please pHaestus, we always do well at customer service
but not at kissing butt when the problem is of the customer's creation
the thread here was nothing, you should see the rabid crowd at hardocp
BillA is offline   Reply With Quote
Unread 11-16-2003, 11:22 AM   #3
Mindflux
Cooling Neophyte
 
Join Date: Nov 2003
Location: Texas
Posts: 15
Default

Craaap I just ordered one of these... but I guess since it's after Nov 10 I should be ok.
Mindflux is offline   Reply With Quote
Unread 11-16-2003, 11:56 AM   #4
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

Wasn't questioning the quality of Swiftech's customer service. I was referring specifically to your bedside manner
pHaestus is offline   Reply With Quote
Unread 11-16-2003, 12:15 PM   #5
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

I presume you saw the 'title' the mods over there gave me ?
- for meritorious service I presume
kinda like JoeK's here

hi ho
BillA is offline   Reply With Quote
Unread 11-16-2003, 12:24 PM   #6
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

heh I considered changing your title to Swiftech CSR, but I figured that 90% of the time your posts did not represent the official stance of Swiftech, Inc
pHaestus is offline   Reply With Quote
Unread 11-16-2003, 12:29 PM   #7
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

for sure, Gabe is generally quite dismayed
often with good reason
but life is for living, eh ?
BillA is offline   Reply With Quote
Unread 11-16-2003, 12:30 PM   #8
Aardil
Cooling Savant
 
Join Date: Oct 2002
Location: Louisiana
Posts: 174
Default

Billa,
If I understand correctly ( I get things wrong alot) Swiftech is gonna offer the replacement head to anyone that has an original 600 pump free of charge?

My question is this, do the bad pumps need to be RMAed and sent in for repair or is it something we could get sent to the customer and the customer change himself?

Both my 600's are fine so far but I dont have 10 hours running time on either, just some testing time as the rest of the project parts are supposed to be in next week.
Aardil
Aardil is offline   Reply With Quote
Unread 11-16-2003, 12:37 PM   #9
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

yes, replacement heads at no cost (once we have the ones with ceramic thrust bearings)

in the meantime if you have a problem (less than 2%); get an RMA # (after talking with me), and we will send just the pump head
no, you can change out, 4 Phillips head ss screws
BillA is offline   Reply With Quote
Unread 11-16-2003, 12:43 PM   #10
jaydee
Put up or Shut Up
 
jaydee's Avatar
 
Join Date: Dec 2001
Location: Spokane WA
Posts: 6,506
Default

Is there going to be any cost hike for the revised pumps when they are released?
jaydee is offline   Reply With Quote
Unread 11-16-2003, 01:08 PM   #11
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

we don't know at this time, and would inform our distributors before the public in any case

we look forward to the change as it will greatly enhance the yet to be determined MTBF value,
but it is difficult to 'sell' longevity in a price conscious market
- the MCP600 will remain a 'high end' product
BillA is offline   Reply With Quote
Unread 01-31-2004, 01:15 PM   #12
satanicoo
Cooling Savant
 
satanicoo's Avatar
 
Join Date: Nov 2002
Location: portugal
Posts: 635
Default

*Bump*

It isnt revised yet?
__________________
back.
satanicoo is offline   Reply With Quote
Unread 01-31-2004, 02:53 PM   #13
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

well, we know some things - but not others
the final re-design is completed, tested, and now shipping (for some time),
and the pump price did go up $5

what we do not yet know is a real shipping schedule for the replacement heads in quantity;
when we have them it will be announced

in the meantime anyone whose MCW600 pump fails should contact us
(562) 595-8009
BillA is offline   Reply With Quote
Unread 01-31-2004, 05:21 PM   #14
pauldenton
Cooling Savant
 
Join Date: Jan 2004
Location: london, england
Posts: 416
Default

Quote:
Originally Posted by unregistered
well, we know some things - but not others
the final re-design is completed, tested, and now shipping (for some time),
and the pump price did go up $5

what we do not yet know is a real shipping schedule for the replacement heads in quantity;
when we have them it will be announced

in the meantime anyone whose MCW600 pump fails should contact us
(562) 595-8009
BillA, spotted this on a vendor's site (http://www.sidewindercomputers.com./pumps.html)
The new revision (rev 2) of the MCP600 is now shipping. The new pumps can be distinguished from the previous by the serial number on the label; the revised series have a serial number beginning with "S".
can you confirm this method works? thanks.
pauldenton is offline   Reply With Quote
Unread 01-31-2004, 05:30 PM   #15
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

Quote:
Originally Posted by pauldenton
BillA, spotted this on a vendor's site (http://www.sidewindercomputers.com./pumps.html)
The new revision (rev 2) of the MCP600 is now shipping. The new pumps can be distinguished from the previous by the serial number on the label; the revised series have a serial number beginning with "S".
can you confirm this method works? thanks.
yup
not too enthused about calling it Rev.2 as the specs are exactly the same as initially described,
but the serial # starting with an 'S' will identify those with the new pump heads
BillA is offline   Reply With Quote
Unread 01-31-2004, 05:56 PM   #16
pauldenton
Cooling Savant
 
Join Date: Jan 2004
Location: london, england
Posts: 416
Default

Quote:
Originally Posted by unregistered
yup
not too enthused about calling it Rev.2 as the specs are exactly the same as initially described,
but the serial # starting with an 'S' will identify those with the new pump heads
yes i thought it was a bit odd too...

cheers
pauldenton is offline   Reply With Quote
Unread 02-01-2004, 06:25 AM   #17
flacowboy
Cooling Neophyte
 
flacowboy's Avatar
 
Join Date: Dec 2003
Location: gulf coast of fla
Posts: 10
Default

hey i havea mp600 that died and have to admit that swiftech did a awsome job with my rma had a new head with in 3 days and was not questioned at all just for that alone i will will stick with swiftech they are a awsome company to deal with wish all companies were that forthright thanks for all the work u do billa
flacowboy is offline   Reply With Quote
Unread 04-27-2005, 12:03 PM   #18
DJ_MIX
Cooling Neophyte
 
Join Date: Apr 2005
Location: NJ
Posts: 8
Default

Can someone help me out I have the MCP600 Early ones and my pump will work fine for 30 mins then die and my temps shoot up.

I CONTACTED SWIFTECH BY EMAIL
AND CONFIMED NEED NEW REPLACEMENT HEAD
THEY SAID NO REPLACEMENT HEAD WITHOUT RECEIPT ALSO.

I bought this pump over 1 year ago and don't have the receipt I supply them with my
pumps serial and they refuse to send out a new replacement..


ANYONE HELP ME !! Get a new head or can I fix it mySELF
Don't plain on shelling out $20 more since it's a deisgn flaw on their part..
If I HAVE to get a new pump IT won't be a swiftech product.
DJ_MIX is offline   Reply With Quote
Unread 04-27-2005, 12:22 PM   #19
JamesAvery22
Cooling Savant
 
Join Date: May 2004
Location: Northern VA
Posts: 383
Default

Quote:
Originally Posted by DJ_MIX
Can someone help me out I have the MCP600 Early ones and my pump will work fine for 30 mins then die and my temps shoot up.

I CONTACTED SWIFTECH BY EMAIL
AND CONFIMED NEED NEW REPLACEMENT HEAD
THEY SAID NO REPLACEMENT HEAD WITHOUT RECEIPT ALSO.

I bought this pump over 1 year ago and don't have the receipt I supply them with my
pumps serial and they refuse to send out a new replacement..


ANYONE HELP ME !! Get a new head or can I fix it mySELF
Don't plain on shelling out $20 more since it's a deisgn flaw on their part..
If I HAVE to get a new pump IT won't be a swiftech product.
Should have saved the receipt. I bought mine from frozencpu.com and I just had to print out the invoice from their webpage when I had to get a new head for my mcp600. Thats your fault for not saving it. Blaming a company for not RMAing a product that you have no proof of purchase for is pretty f'ing stupid. Name a company or store that will take a product back if you cannot prove that you bought it!
__________________
Stabbing.
My Heatware
JamesAvery22 is offline   Reply With Quote
Unread 04-27-2005, 12:49 PM   #20
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

http://www.ocforums.com/showthread.php?t=382840
BillA is offline   Reply With Quote
Unread 04-27-2005, 01:30 PM   #21
satanicoo
Cooling Savant
 
satanicoo's Avatar
 
Join Date: Nov 2002
Location: portugal
Posts: 635
Default

Billa 1 - 0 DJ_MIX
__________________
back.
satanicoo is offline   Reply With Quote
Unread 04-27-2005, 01:37 PM   #22
MadHacker
Cooling Savant
 
MadHacker's Avatar
 
Join Date: May 2003
Location: Okotoks, A.B. Canada
Posts: 726
Default

Quote:
Originally Posted by JamesAvery22
Name a company or store that will take a product back if you cannot prove that you bought it!
let see... Asus, Abit, Maxtor, Western Digital to name a few.
all of which i have RMA'd to in the past and not once have they asked for a reciept or any proof of purchase...
Sell it to your self and give yourself a reciept...
that is a proof of purchase... Legal.. yes...
moral... probobly not...
__________________
"Great spirits have always encountered violent
opposition from mediocre minds" - (Einstein)
MadHacker is offline   Reply With Quote
Unread 04-27-2005, 02:25 PM   #23
freeloadingbum
Cooling Savant
 
Join Date: Nov 2002
Location: winnipeg
Posts: 129
Default

Did the pump fail because DJ_MIX lied about how he purchased it or did it fail because of the faulty design? Is it possible for the pump to be past it's two year warranty?

As the legal owner of a swiftech product, DJ_MIX is still a swiftech customer, regardless of buying the pump on the forum. Unless it's swiftech's policy that all second hand swiftech parts should be considered junk and that no one should ever buy one.
freeloadingbum is offline   Reply With Quote
Unread 04-27-2005, 02:45 PM   #24
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

Warranty
Our products are guaranteed for 12 months from the date of delivery to the final user against defects in materials or workmanship. During this period, they will be repaired or have parts replaced provided that: (I) the product is returned to the agent from which it was purchased; (II) the product has been purchased by the end user and not used for hire purposes; (III) the product has not been misused, handled carelessly, or other than in accordance with any instructions provided with respect to its use.

dj has no warranty rights as he did not purchase the pump from Swiftech or a distributor,
and I will not reward a 'customer' jerking around with the RMA system

people who buy used parts should expect a used part, no more
BillA is offline   Reply With Quote
Unread 04-27-2005, 03:07 PM   #25
freeloadingbum
Cooling Savant
 
Join Date: Nov 2002
Location: winnipeg
Posts: 129
Default

Quote:
Originally Posted by unregistered
dj has no warranty rights as he did not purchase the pump from Swiftech or a distributor,
and I will not reward a 'customer' jerking around with the RMA system
None of this has anything to do with why the part failed. The fact that the warranty is not transferable is "BULLSHIT". The fact that alot of companies hide behind this kind of bullshit doesn't make it right. Did the act of buying the pump on the forum cause it to fail? The early version of the pump has a known design flaw and therefore should be repaired regardless of warranty. At least that's what a company that stands behind their products would do.
freeloadingbum is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 03:40 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com