Consider the following.

Qmax = 226W
Vmax = 15.2V
Imax = 24A
Pmax = 364.8W

Qmax = 320W Th = 50C
Qmax = 243.5W Th = 26.8C
Vmax = 15.4V
Imax = 26A
Pmax = 400.4

If one believes the 226W and 320W related parameters above are factual and you compare the differences between the 226W and alleged 320W device, then for a 35.6W difference in input power you get a 94W maximum increase in cooling power from the 320W device.

How about this, for a 35.6W increase in input power you get an 18W maximum increase in cooling power from a 244W device.

Which scenario is believable?
DNA is offline   Reply With Quote
Unread 11-28-2005, 12:01 PM   #2
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default Re: Thermal Enterprises 245/320W Peltier

I don't see how anyone's going to get a 26.8 deg C temp differential (temp between the hot and cold sides); is there a magical recipe? An insane clamping pressure?
bigben2k is offline   Reply With Quote
Unread 11-28-2005, 04:20 PM   #3
ricecrispi
Cooling Savant
 
Join Date: Jul 2005
Location: california
Posts: 429
Default Re: Thermal Enterprises 245/320W Peltier

I doubt that too and same for 320 watts and 50 C delta but these are theorectical values.

More important question is with only 30 more watts input over the 226 pelt will you 90 watt improvement seen in the 320 watt pelt.

IMO, NO! But I'm still learning about pelts

The bigger question is..... are people buying what they believe is 320 watt pelt when it's only 243 watts? Are people getting fooled into buying a 320 watt pelt that is vaguely stated to use about 320 watts but cools only 243 watts?
ricecrispi is offline   Reply With Quote
Unread 11-29-2005, 11:31 PM   #4
Revivalist
Cooling Neophyte
 
Join Date: Oct 2005
Location: Fresno, CA, USA
Posts: 16
Default Re: Thermal Enterprises 245/320W Peltier

Quote:
Originally Posted by ricecrispi
I doubt that too and same for 320 watts and 50 C delta but these are theorectical values.

More important question is with only 30 more watts input over the 226 pelt will you 90 watt improvement seen in the 320 watt pelt.

IMO, NO! But I'm still learning about pelts

The bigger question is..... are people buying what they believe is 320 watt pelt when it's only 243 watts? Are people getting fooled into buying a 320 watt pelt that is vaguely stated to use about 320 watts but cools only 243 watts?
Probably so unfortunately. I'll admit that I was one. But I'm still happy with the purchase since it's still the most powerful 50mm pelt out there.
__________________
AMD 64 3400+ Newcastle 2.2GHz @ 2.70GHz --- ASUS A8V @ 270MHz HTT
1GB dual OCZ @ DDR530, 2.5-3-3-8 --- MSI 6600GT @ 600 GPU, 1.30GHz RAM
2x80GB Hitachi RAID 0 on VIA --- Aspire 500W & Vigor 400W dual power supplies
Cooling: Maze4-1 CPU block with 245/320 TEC, chrome Maze4 GPU block, BIX III, MCP655 pump, 1/2" tubing
Revivalist is offline   Reply With Quote
Unread 11-29-2005, 11:51 PM   #5
Joe
The Pro/Life Support System
 
Joe's Avatar
 
Join Date: Dec 1999
Location: Denver, CO
Posts: 4,041
Default Re: Thermal Enterprises 245/320W Peltier

Quote:
Originally Posted by ricecrispi
I doubt that too and same for 320 watts and 50 C delta but these are theorectical values.

More important question is with only 30 more watts input over the 226 pelt will you 90 watt improvement seen in the 320 watt pelt.

IMO, NO! But I'm still learning about pelts

The bigger question is..... are people buying what they believe is 320 watt pelt when it's only 243 watts? Are people getting fooled into buying a 320 watt pelt that is vaguely stated to use about 320 watts but cools only 243 watts?

You know there is an article on the site breaking down how pelts work, curves, etc... . Check the articles area, RichW did it back in 2000 I think.
__________________
Joe - I only take this hat off for one thing...

ProCooling archive curator and dusty skeleton.
Joe is offline   Reply With Quote
Unread 11-29-2005, 11:52 PM   #6
Joe
The Pro/Life Support System
 
Joe's Avatar
 
Join Date: Dec 1999
Location: Denver, CO
Posts: 4,041
Default Re: Thermal Enterprises 245/320W Peltier

Here it is

http://www.procooling.com/index.php?...ticles&disp=43
__________________
Joe - I only take this hat off for one thing...

ProCooling archive curator and dusty skeleton.
Joe is offline   Reply With Quote
Unread 12-02-2005, 11:30 PM   #7
DNA
Cooling Neophyte
 
Join Date: Feb 2005
Location: USA
Posts: 71
Default Re: Thermal Enterprises 245/320W Peltier

Quote:
Originally Posted by ricecrispi
I doubt that too and same for 320 watts and 50 C delta but these are theorectical values.

More important question is with only 30 more watts input over the 226 pelt will you 90 watt improvement seen in the 320 watt pelt.

IMO, NO! But I'm still learning about pelts

The bigger question is..... are people buying what they believe is 320 watt pelt when it's only 243 watts? Are people getting fooled into buying a 320 watt pelt that is vaguely stated to use about 320 watts but cools only 243 watts?
I emailed Thermal Enterprises and posed the following question.
"Your ebay advertisement refers to the device as 245-320w. Your specs clearly state that the maximum Qc of the device is 243.5w . Why do you use the 320w reference in your advertisement? It's misleading to the public".

Their response was as follows.
"We simply follow the same common practice as most other TEC manufactures, we establish the watt rating of our devices under two different operating conditions. The lower wattage rating is established with hot side temperature at 27 deg C. The higher wattage rating is established with hot side temperature at 50 deg C".

After researching the peltier rating subject, I have to agree with Thermal Enterprises response. It is up to the end-user to determine which set of peltier parameters would be most applicable for their operating conditions.

In summary, when peltier maximum cooling power wattage ratings (Qcmax) are expressed by two values as is the case with Thermal Enterprises devices, the lower rating equates to a Th = 27C ambient condition and the higher rating to a Th = 50C. In any well planned CPU peltier/water-cooled system, the Qcmax that would be most representative of their system's cooling performance would be the vaule at Th = 27C.
DNA is offline   Reply With Quote
Unread 12-03-2005, 12:08 AM   #8
ricecrispi
Cooling Savant
 
Join Date: Jul 2005
Location: california
Posts: 429
Default Re: Thermal Enterprises 245/320W Peltier

Thanks for the link Joe. I'm gonna read it and get the program.

UPDATE: I seen kryptherm before. Not the most user friendly and intuitive program but i'm getting a better handle on it this time.
Anyone know how to edit the module list or add new modules?


I brought up the fact orignally in Revivalist's post on his pelt setup. DNA made this post on it to resolve the issue. I was going to buy the 320 watt and realized in the charts not going to get 320 watts.

I learned how to read the tables sent to me from this link. http://overclockers.com/tips45/
Took a while to find good pelt info. I got a collection of links i got to catch up own over the winter

UPDATE: I asked Thermal Enterprise a while back if it was a 240 watt pelt and 320 watt pelt. Of course I said I didn't know a lot about pelts and I wanted to use it to cool my cpu. I asked for some advice and input. They told me go learn some more about pelts. Not bad advice. I asked for clarifications about the pelts after learning some more about pelts and they sent me a chart instead of answers. Maybe it was my approach?

Last edited by ricecrispi; 12-03-2005 at 02:55 AM.
ricecrispi is offline   Reply With Quote
Unread 12-03-2005, 03:32 AM   #9
WeaselBlade
Cooling Neophyte
 
Join Date: Jul 2004
Location: BC, Canada
Posts: 15
Default Re: Thermal Enterprises 245/320W Peltier

So, what hotside temp does the standard 226w peltier need for 226w Qmax? Anyone have a datasheet/know where one is?
WeaselBlade is offline   Reply With Quote
Unread 12-03-2005, 04:36 AM   #10
DNA
Cooling Neophyte
 
Join Date: Feb 2005
Location: USA
Posts: 71
Default Re: Thermal Enterprises 245/320W Peltier

Quote:
Originally Posted by WeaselBlade
So, what hotside temp does the standard 226w peltier need for 226w Qmax? Anyone have a datasheet/know where one is?
Although I have not been able to confirm it, I believe the 226W rating is at a Th = 27C ambient. Its Pcmax value also supports that Qcmax rating.
DNA is offline   Reply With Quote
Unread 12-03-2005, 03:27 PM   #11
ricecrispi
Cooling Savant
 
Join Date: Jul 2005
Location: california
Posts: 429
Default Re: Thermal Enterprises 245/320W Peltier

In general, most of the pelts WCing people see on DD or other sites are rated Qmax at ambient temps.

I'm not going to say Thermal Enterprise is decieving people. They have the info posted on the description but they are definitely not straightforward about clarify the issue and supplying a simple answer.....

The fact the fooled many people into believing it's a 320 watt pelt is a testiment to that.
ricecrispi is offline   Reply With Quote
Unread 12-04-2005, 02:25 AM   #12
ricecrispi
Cooling Savant
 
Join Date: Jul 2005
Location: california
Posts: 429
Default Re: Thermal Enterprises 245/320W Peltier

http://img233.imageshack.us/img233/8...attpelt7tz.jpg

This is what' i've learned.

Qc is 100W (should be 90 W)
Find the point were Qc @100W crosses various current rating lines at bottom of the graph.

Draw a vertical line up to the same current rate line above. This gives voltage the pelt draws to get that DT
for 12.3 V=Dt is 34 C
Cpu temp =Th- DT

TH = 25 C degrees (is the hot side of the pelt at Q total of 346 W. TH varies depending on how good your setup is)


25-34= -9 C

Last edited by ricecrispi; 12-04-2005 at 02:33 AM.
ricecrispi is offline   Reply With Quote
Unread 12-04-2005, 03:04 AM   #13
DNA
Cooling Neophyte
 
Join Date: Feb 2005
Location: USA
Posts: 71
Default Re: Thermal Enterprises 245/320W Peltier

Quote:
Originally Posted by ricecrispi
http://img233.imageshack.us/img233/8...attpelt7tz.jpg

This is what' i've learned.

Qc is 100W (should be 90 W)
Find the point were Qc @100W crosses various current rating lines at bottom of the graph.

Draw a vertical line up to the same current rate line above. This gives voltage the pelt draws to get that DT
for 12.3 V=Dt is 34 C
Cpu temp =Th- DT

TH = 25 C degrees (is the hot side of the pelt at Q total of 346 W. TH varies depending on how good your setup is)


25-34= -9 C
cpuT is not equal to Th - dT. Tc = Th - dT; Th is ~ equal to coolant temperature.

cpuT > Tc; under maximum thermal load, it may be greater by as much as 10°C to 20°C.

Th varies as a function of Ta, V, I, Q and RQ.

The hot side temperature (Th) will be equal to the ambient temperature (Ta) plus the rise in temperature across the heat sink from dissipating the heat load (Q) and the peltier input power (V x I) multiplied by the heat sink thermal resistance characteristics (RQ).

Th = Ta + (V x I + Q) RQ

RQ = thermal resistance of heat sink in C° temperature rise per Watt dissipated.
Using known values for Th, Ta, V, I, and Q, one can solve for RQ.

RQ = (Th - Ta)/(V x I +Q)

Last edited by DNA; 12-04-2005 at 04:57 PM.
DNA is offline   Reply With Quote
Unread 10-25-2008, 06:21 PM   #14
fizicsphosyl'41
Cooling Neophyte
 
Join Date: Oct 2008
Location: AUSTRALIA
Posts: 2
Default Re: Thermal Enterprises 245/320W Peltier

Hi Everyone,
Introducing a fizicsphosyl of seriously ancient proportions. Havn't yet read enough of your disscussion regarding the apparent anomoly.however there is a funcion of DELTA TEMP. to be considerred at the point of calculation. NO argument, just for consideration.
Thanks,Rob.
fizicsphosyl'41 is offline   Reply With Quote
Unread 10-26-2008, 05:11 PM   #15
billbartuska
Cooling Savant
 
Join Date: Jun 2005
Location: Skokie, Illinois
Posts: 322
Default Re: Thermal Enterprises 245/320W Peltier

Quote:
Originally Posted by fizicsphosyl'41 View Post
Hi Everyone,
Introducing a fizicsphosyl of seriously ancient proportions. Havn't yet read enough of your disscussion regarding the apparent anomoly.however there is a funcion of DELTA TEMP. to be considerred at the point of calculation. NO argument, just for consideration.
Thanks,Rob.

Hey! This thread is over three years old.
__________________
My new rig....
Intel SE440BX-3, PIII 550 (@ 680)
MX440 275/332 (@ 350/400) and 3DFX Voodo 5 5500 160/160 (@180/180)
Two Opticals and 120 gigs (w/28gigs in RAID0) on 4 Maxstors
billbartuska is offline   Reply With Quote
Unread 10-26-2008, 05:27 PM   #16
fizicsphosyl'41
Cooling Neophyte
 
Join Date: Oct 2008
Location: AUSTRALIA
Posts: 2
Default Re: Thermal Enterprises 245/320W Peltier

Quote:
Originally Posted by billbartuska View Post
Hey! This thread is over three years old.

Oh Yes!
Please forgive me!!!!

.......Laughed my 'freakin' head off for hours when WE realized it!! Red
Face!(Could freedrink on that one for a month.)
Go's nicely with my well matured age....'1941.
Thanks for the reply as well. shows someone is still alive there!
Regards,
Rob. Page....fizicsphosyl'41......AU...(we are light years behind the 8
ball!)
fizicsphosyl'41 is offline   Reply With Quote
Unread 10-27-2008, 06:27 AM   #17
billbartuska
Cooling Savant
 
Join Date: Jun 2005
Location: Skokie, Illinois
Posts: 322
Default Re: Thermal Enterprises 245/320W Peltier

Quote:
Originally Posted by fizicsphosyl'41 View Post
Oh Yes!
This place used to be THE PLACE for cooling info. But. alas. that's all gone now, though it's still the best place in our galaxy for getting basic cooling information.

Check out these:Reviews and Articles
See also, Overclockers.com (watercooling)

And there is a peltier thread plodding along here
__________________
My new rig....
Intel SE440BX-3, PIII 550 (@ 680)
MX440 275/332 (@ 350/400) and 3DFX Voodo 5 5500 160/160 (@180/180)
Two Opticals and 120 gigs (w/28gigs in RAID0) on 4 Maxstors
billbartuska is offline   Reply With Quote
Unread 10-27-2008, 01:51 PM   #18
ben333
Uber Pro/Mods
 
ben333's Avatar
 
Join Date: Aug 2007
Location: New Hampshire (USA) Posts: Two hundred somethin
Posts: 432
Default Re: Thermal Enterprises 245/320W Peltier

Bill, thats amazing... you've managed to find overclockers.com without it looking like crap!! How long will this old site be up? I checked archives for days and couldn't find some articles from before the "upgrade", thank you for posting this link.
__________________
Pro Slacker
ben333 is offline   Reply With Quote
Unread 10-27-2008, 04:37 PM   #19
billbartuska
Cooling Savant
 
Join Date: Jun 2005
Location: Skokie, Illinois
Posts: 322
Default Re: Thermal Enterprises 245/320W Peltier

Quote:
Originally Posted by ben333 View Post
Bill, thats amazing... you've managed to find overclockers.com
Without knowing what I was looking for I'd never have been able to find it. It was deep down in Google.
__________________
My new rig....
Intel SE440BX-3, PIII 550 (@ 680)
MX440 275/332 (@ 350/400) and 3DFX Voodo 5 5500 160/160 (@180/180)
Two Opticals and 120 gigs (w/28gigs in RAID0) on 4 Maxstors
billbartuska is offline   Reply With Quote
Unread 03-08-2011, 11:47 PM   #20
jonusb5
Banned
 
Join Date: Mar 2011
Location: canada
Posts: 9
Default Re: Thermal Enterprises 245/320W Peltier

After having thoroughly San Jose Asian Escort discussed the fine line San Jose Asian Escorts between escort services and prostitution, there is no San Jose Escort denying that there is a huge possibility this single line will be crossed every now and then.After having San Jose Escorts thoroughly discussed the fine line between escort services and prostitution,
jonusb5 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 04:14 PM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...