![]() | ||
|
|
Testing and Benchmarking Discuss, design, and debate ways to evaluate the performace of he goods out there. |
![]() |
Thread Tools |
![]() |
#1 |
Cooling Neophyte
Join Date: Sep 2001
Location: High Altitude Lab
Posts: 94
|
![]()
at the prodding of BillA Im starting a workblog of sorts
this was for [H]ardOCP's [H]igh Altitude Lab ![]() Objective: Thermodynamic and Power Testing the construction of an automated test platform and environmental test chamber Phase One Research components (complete more or less, thanx BillA and the rest of these forums) Phase Two Acquistion (partially complete) To Date here is an acquired equipment list (updated as of the last editing timestamp below) Interface National Instruments PCI-GPIB\LP NI-488.2 and cable National Instruments PCI-DIO-96 w\ 2m 100 pin cable (class status: need PIO breakout box) Software LABview 7.0 MATLAB & Simulink DegreeC AccuTRAC Keithley Runtime Environment Autotest APG for Windows (3.0) (class status: need to upgrade APG and like to add CFD modeling, need to get a grip on LABview and MATLAB so I can integrate all this together) Measurment Hardware Keithley 2700 Digital Multimeter & Data Aquisition System Keithley 7701 32 channel Differential Multiplexer Module Keithley 7708 40 channel Diff Mux Module w/ Automatic Cold Junction Compensation Ametek 0-1000A Digital Recording Ammeter (AC) Fluke 2176A 10 Channel Digital Thermometer w/ RTD Digitec HT 5810 Thermometer 2 x Digidoc5 (hardware fan monitoring) and rheobus fan controls (Class Status: more or less complete, need more Rheobus controls, adding another dedicated HP 34401A DMM for the UTS-325) Sensors 10 J Type Thermocouples with shielded extention grade wire 10 T Type surface mount Thermocouples 2x 4 wire RTDs Contact Temperature Probe (front panel of DMM) mystery tool being shipped 50x Thermistors (various makes and models) 10 calibrated J type panel connectors and plugs w\ strain relief in 2 handmade sheilded quickswap modular panels 27 x IHA-25 F.W. Bell Current Sensors EESIFLO Sonic Low Flow, Mass flowmeter (pre-production prototype, temperature immune) being fabricated Endress+ Hauser M-Point Massflow Meter Setra 230 Wet/Wet Differential Pressure Transducer w/3-Valve Manifold Keithley HA5050 50 Amp Shunt Sensor American Aerospace Controls DC Current Sensor 913B-10-B Micro Control Technology Calibration Module (Class Status: need more RTDs and panel connectors, PCI\PCIe & AGP riser cards for the power consumption suite, need triple point cells (Hg \ H2O \ Ga) for in-lab calibration, need to have sensors professionally calibrated and their error curves plotted) Electronic Enclosure Airflow and Temperature Test Suite DegreeC Cambridge AccuSense ATM-24 24 x CAFS-220 sensors AccuTRAC Software suite (Class Status: Part one Complete on delivery, maybe get a dedicated RS232 card, part two build airflow resistance flowbench\wind tunnel to measure fans, as well as radiator and case resistance) Power Supply Testing Hardware Panasonic VP 5720A Oscilliscope (GPIB w\ digital storage) Ithaco Lock On Amplifier Autotest UTS-325 PSU ATE w\ 5 x 150W programmable DC load modules (1A /uSec slew rate for transient step mode) a total of 900 Watts test capacity 2.1 KVA Programmable Variac, Differential wideband peak detector, 12 position, 4 wire switching matrix, line source measurement, load current measurement, universal timer counter and software suite. (Class Status:The Autotest UTS-325 is a completely integrated automatic test system, The test suite includes: AC Line Current, AC Inrush, DC Line Current, DC Inrush, DC Line Step, Efficiency, Vout Setpoint, Voltage, Frequency, Sequencing, Rise/Fall Time, Time Interval, Over/Under Shoot, Regulation Line, Regulation Line Frequency, Regulation Load, Cross Regulation, Regulation 2 Corner, Regulation 4 Corner, Regulation Dynamic, Dynamic Transient Response, Noise & Ripple, OverLoad Constant Current, OverLoad Constant Voltage, OverLoad Short Circuit, Short Circuit Recovery and Over Voltage Protection tests. Need to upgrade the EPROM and software, need dedicated DMM) Sound Testing Hardware Bruel & Kjaer 2203 Sound Level Meter with 1613 Octave Filter Set Bruel & Kjaer 4131 condenser microphone Manfrotto Tripod Adapter (Class Staus: need to build sound chamber) Environmental Test Chamber Control & Measurement PCon Multiloop PID control software National Instruments PCI-DIO-96 w\ 2m 100 pin cable (listed above) Omega CN77342-C2 Autotune PID Temperature Controller RS232 Rotronic HC321A Humidity & Temperature dewpoint Computer w\ Hygrometer Kikusui PIA3200 GPIB Power Supply Control Aquafine SP-1 UV Water Treatment Unit 100' 3\8" Anaconda Sealtite Isolated Ground Conduit Aluminum Insulated Refrigerator door 3 Air conditioners various blowers, pumps, insulation, sheet metal, metal stock, hardware, lumber and plumbing (Class Status: need solid state relays, power supplies, UV replacement bulb, incremental improvements will be made as time allows and need dictates, increasing cooling capacity ect. Phase2 of the chamber calls for tight humdity and temperature control based on Saturation Thermodynamics) Infrastructure 2 computers for DAQ and Control w\ 2U rackmount Cases Dual Opteron Workstation for MATLAB\CFD Modeling (244's\K8W\FX3000\4GB) 3 pair Heavy Duty Rackrails (had others) Bud Industries Rackmount 30U Enclosure 5 surge proctetors Olympus E20N Lowel Tota halogen lights Manfrotto 3251 heavy duty tripod and 3047 head Welch Duo-Seal High Vacuum Pump Model 1400 CONDOR Linear DC Power Supply 5V@12A ±15V@3A 12V-15VDC largely inaccurate mail scale (up to 75lbs) ton of GPIB and RS232 cables (Class Status: need centralized Online UPS approx 5KVA perferably Liebert, third computer for UTS-325, fabricate vacumm chamber for thermal isolation, fabricate Calorimetry Tank) Immediate Cash Expenditure.........................$8457 plus some supplies\equipment\software previously acquired Approx List .......................................... $50,000 > $60,000 plus odds and ends ![]() Phase Three Integration & Construction step one first single thermocouple logged +8 hour run on the DAQ w\7708 and attached to the Monitoring boxen (Celeron 700MHZ some Shuttle antique in a 2U rackmount case) Keithley runtime on W2K ![]()
__________________
LurkyLoo Last edited by Ice Czar; 04-27-2006 at 01:53 PM. |
![]() |
![]() |
![]() |
#2 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
aiiii
I'm a dinosaur, great stuff IC |
![]() |
![]() |
![]() |
#3 |
Pro/Staff
Join Date: Oct 2001
Location: Klamath Falls, OR
Posts: 1,439
|
![]()
Excellent! Look forward to seeing this produce results and evolve.
|
![]() |
![]() |
![]() |
#4 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]()
Someone's got money...
Looking forward to see it run! |
![]() |
![]() |
![]() |
#5 | |
Cooling Neophyte
Join Date: Sep 2001
Location: High Altitude Lab
Posts: 94
|
![]()
Thank you
And Bill, if your a dinosuar your a damn smart one ![]() Without your guidance and advise Id still be in phase one and have wasted three times the money on antiques as I did before you started to clue me in ![]() Quote:
![]() (passing up far more lucrative but irregular freelance) only when you factor in the buying power on ebay did it make any sense whatsoever ![]() and bigben2K thank you as well, your posts here where vary helpful ![]()
__________________
LurkyLoo Last edited by Ice Czar; 03-01-2006 at 07:14 PM. |
|
![]() |
![]() |
![]() |
#6 |
Cooling Savant
Join Date: Apr 2004
Location: Canada
Posts: 219
|
![]()
Are you doing testing for HardOCP?
Rattle FrgMstr's coiffers. |
![]() |
![]() |
![]() |
#7 | |
Pro/Staff
Join Date: Oct 2001
Location: Klamath Falls, OR
Posts: 1,439
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#8 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
yup, experience is the accumulation of errors
but a point of semantics (wonderful stuff, almost as good as philosophy) 'smart', if we use the IQ version, relates directly to the rate at which info can be 'absorbed' from written text (well documented, don't argue) - so I am very smart; YET yesterday, having the same source data as TM, I was unable to follow simple instructions - so I do not break my arm patting myself on the back, plenty dumb with even simple instructions smart in my book is learning from someone else's errors; here again I'm not too sharp, I have to make the (obvious) errors myself to 'internalize' them [also just what children do to the dismay of parents, "experience does not transfer"] re the subject at hand - testing, I have bought SO MUCH CRAP over the last 6 years it is incredible; inadequate, obsolete, unsuited, broken, whatever - no free lessons, particularly for the self-tutored; now I know professionals in the field I can querry, so my errors are fewer and smaller in scope so yes Brian, for us 'smart' kind of equates to experience + comprehension for 'stupid' examples speak more loudly than words; consider politics and religions - but note they both are stupid only for the masses, the leaders live quite well Thank You |
![]() |
![]() |
![]() |
#9 | |
Cooling Savant
Join Date: Nov 2002
Location: Portugal, Europe
Posts: 870
|
![]() Quote:
looking forward for your cal runs. side note: - the keithley DAQ cards have a larger latency than the NI's that can limit fast aquisition. a friend of mine picked that up while trying to make a control system for an inverted pendulum. not really that relevant as the rate required is not very high, but just a heads up. given the choice, go NI. - the Fluke (damn that's ancient) is not loggable, however, you could "hack into it" and output the signal to the display. Or use a webcam and a visual aquisition ![]()
__________________
"we need more cowbell." |
|
![]() |
![]() |
![]() |
#10 |
Cooling Neophyte
Join Date: Sep 2001
Location: High Altitude Lab
Posts: 94
|
![]()
well the switch speed for the 2700\7708 is 3ms which is fine for the measurements Im looking at logging,
Ive actually got the scans set at 1 sec, and its internal memory buffer will do 55,000 readings of course with the computer I can poll it and write to disk indefinately on the control side I was going to use the NI PCI-DIO-96 ![]() I bought that Fluke before I knew what the hell I was doing, but its reasonably useful as its own "remote" unit step 2 wire up and log multiple thermocouples ![]() cant seem to get the ExcelLINX plugin working properly, its hardcoded to GPIB1 or 2 and my DMM is on GPIB0 so I keep getting a configuration error (the above is again the Keithley runtime only from the scanning side) scale is C with a little lighter and water bath action Time to wade into the IVI and VISA configuration documentation for configurations....again ![]()
__________________
LurkyLoo Last edited by Ice Czar; 03-04-2006 at 08:08 AM. |
![]() |
![]() |
![]() |
#11 |
Cooling Neophyte
Join Date: Sep 2001
Location: High Altitude Lab
Posts: 94
|
![]()
update: was canned by Kyle when I couldn't get repeatable results, at issue was having the thermocouples directly wired into the the DMM, making it impossible to swap out components on the case without seriously moving the sensors, also was doing "whole room" gradient heating putting all the equipment through the same stress testing.
been working on the test chamber, and rounding out the other test suites, just landed a DegreeC ATM-24 and this time the test chamber is up as well as having a sheilded and "pluggable" interface between the DMM and DUT. I'll be "mapping" the "test case" (likely one of many platforms I'll eventually have,this one a Chenbro XspyderIII) for a proof of concept and to solicit other case and turnkey cooling solution reviews now aligned with TechPowerUp and W1zzard
__________________
LurkyLoo |
![]() |
![]() |
![]() |
#12 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]()
Too bad ya'll couldn't work it out.
Let me know if you'd like to have your own forum on the WBTA, to present your testbench. Open or read-only, your choice. PM me for details. |
![]() |
![]() |
![]() |
#13 |
Cooling Neophyte
Join Date: Sep 2001
Location: High Altitude Lab
Posts: 94
|
![]()
actually working with W1zzard has some distinct advantages
![]() we are currently working on putting together an underwriter program for the lab. I have to round up the sponsors, but he sees the value of that. I would like to post a worklog over there if you don't mind thanx ![]()
__________________
LurkyLoo |
![]() |
![]() |
![]() |
#14 |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]()
You're all set:
http://wbta.us/forums/index.php?board=37.0 Yeah, I need sponsors too. NordicHardware has no budget, and they're in Sweden... |
![]() |
![]() |
![]() |
#15 |
Cooling Neophyte
Join Date: Sep 2001
Location: High Altitude Lab
Posts: 94
|
![]()
thanx ben I'll start with mirroring my TechPowerUp worklog
![]()
__________________
LurkyLoo |
![]() |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
|
|