Default Coolant

Thanks to all those members in the forum talking about coolants! You got me sparked to write a quick article on coolant selection and maintenance. Now, I just need to make sure that it is well proof-read by some other staff members and that it gets approved and posted by Joe.
Brians256 is offline   Reply With Quote
Unread 09-17-2002, 09:32 AM   #2
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

It would be nice if you could clear up the "unknowns".

You state to check the pH level of antifreeze. Do you have an easy suggestion for checking that pH?

Otherwise, you did a great job, and answered some of my questions. Thanks!
bigben2k is offline   Reply With Quote
Unread 09-17-2002, 12:20 PM   #3
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

red cabbage makes a tolerable indicator:

http://www.cchem.berkeley.edu/demola.../CabbIndic.htm

You can make your own pH meter but I bet its costly and a pain to calibrate. I think some saltwater aquarium users have them, and you can probably get litmus paper at the pet store too.

the pKa of ethylene glycol is 14.22, so it is basically completely present as C2H4(OH)2
(my weird notation to show that the OH on the alcohol groups are present and not O-)

Can just calculate pH using henderson-hasselbalch eqn:

pH = pKa + log (A-/HA )

oops too many unknowns; better just measure
pHaestus is offline   Reply With Quote
Unread 09-17-2002, 12:30 PM   #4
Brians256
Pro/Staff
 
Brians256's Avatar
 
Join Date: Oct 2001
Location: Klamath Falls, OR
Posts: 1,439
Default

How would I measure the pH? I'd just go to the local store and get some litmus paper, to be honest. They have it in the gardening section of the local megastore (Fred Meyers) to measure soil pH. Or, I'd get it from a hobby store or from an online chem supply house.

The pH that I'd want to maintain would be above 9.0 for antifreeze. As for the pH of water wetter coolants, I don't know for sure what the initial pH of a 1:32 (water:ww) liquid is. I also don't know for sure if there are any buffering chemicals in WW. That being said, my first guess is to keep it at pH 9.0 or above.

Being lazy, I plan on changing the coolant fairly frequently (about every 4 months). That's probably MUCH more than I need, but it really isn't that expensive to do a coolant flush. I do have an "inspection port" to monitor the color and transparency, too. If the coolant becomes cloudy or discolored, it'd be an immediate alarm bell to do a flush. I'll also do a quick inspection of the heater core and waterblock when I do my flushes. That way I can increase or decrease the frequency of my changes if things look good.

Besides, this way the feral cats and possums get a quick waterdish treat every 4 months! Keeps their population down.

P.S. Just kidding about the waterdish, but it is a tempting thought.

Last edited by Brians256; 09-17-2002 at 12:36 PM.
Brians256 is offline   Reply With Quote
Unread 09-17-2002, 01:34 PM   #5
Bignuts
Cooling Savant
 
Bignuts's Avatar
 
Join Date: Mar 2001
Posts: 155
Default the swimming pool guys have pH down to a science

You can get multiple indicators for a wide range of pH at any swimming pool supplier, and they dont require you to buy in bulk.

Also, you can use a multimeter to check for pH:

http://www.venturers.org/NextGenTech/pages/Coolant.html

down near the bottom of that page.
Bignuts is offline   Reply With Quote
Unread 09-17-2002, 01:52 PM   #6
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Nice link!

Here's the relevant info:
You can also use an ordinary digital volt meter for the same purpose. With the engine off, touch the voltmeter positive test lead to the radiator or engine (making sure you get good metal-to-metal contact). Then open the radiator cap and insert the negative test lead into the coolant. A reading of up to 0.2 volts is considered acceptable and indicates the presence of reserve alkalinity in the coolant. If the coolant reads 0.3 to 0.6 volts, it is borderline and should be recycled or replaced. A reading of 0.7 volts or more would tell you the coolant is overdue for a change.

Based on this, I might be able to build a monitoring ciruit...

I can't help but wonder where this voltage comes from though. Anyone?
bigben2k is offline   Reply With Quote
Unread 09-17-2002, 04:02 PM   #7
Brians256
Pro/Staff
 
Brians256's Avatar
 
Join Date: Oct 2001
Location: Klamath Falls, OR
Posts: 1,439
Default

Where does the voltage come from? Good question! My first thought was that it came from the ongoing galvanic corrosion. The voltage you got was because the dissimilar metals were forming a nice battery effect, and the effect became more pronounced as more charge carriers became available. But, I'm not sure of that. Wouldn't the electrical potential be there even if the solution had no charge carriers?

BTW: the chelating agent should trap the charge carriers. That's what it is for.
Brians256 is offline   Reply With Quote
Unread 09-17-2002, 04:18 PM   #8
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

I guess...

If it is a galvanic induced voltage, then I may not want to build a circuit that induces a voltage, which may accelerate the process. I could build something with a needle indicator, stuck to a 5 1/4 plate, with a push button to check the pH.

All we'd have to do, is press the button once in a while, to check the pH. It could be PSU or battery powered. It could be built around a 1/2 inch copper tee, like the overclocker flow sensor (without the cork plug, thank you!).
bigben2k is offline   Reply With Quote
Unread 09-17-2002, 04:23 PM   #9
Brians256
Pro/Staff
 
Brians256's Avatar
 
Join Date: Oct 2001
Location: Klamath Falls, OR
Posts: 1,439
Default

A voltmeter circuit wouldn't induce voltage, though. It measures voltage by involving a high-impedance parallel circuit that reponds to the existing voltage.
Brians256 is offline   Reply With Quote
Unread 09-17-2002, 04:51 PM   #10
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

True, but I need to amplify this reading so that it'll show up on the needle indicator. I'll give it a whirl, and see what happens.
bigben2k is offline   Reply With Quote
Unread 10-16-2002, 01:37 PM   #11
utabintarbo
Cooling Savant
 
utabintarbo's Avatar
 
Join Date: Jul 2002
Location: Sterling Hts., MI
Posts: 496
Default bump

Any progress?
__________________
Sarcasm is yet another of the free services we offer!
utabintarbo is offline   Reply With Quote
Unread 10-16-2002, 02:18 PM   #12
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

LOL! no, I ordered the wrong parts. This is going to have to wait until my next order, but thanks for the reminder!
bigben2k is offline   Reply With Quote
Unread 10-30-2002, 02:05 AM   #13
Alchemy
Cooling Savant
 
Join Date: Oct 2002
Location: Boston
Posts: 238
Default

Quote:
Originally posted by pHaestus
the pKa of ethylene glycol is 14.22, so it is basically completely present as C2H4(OH)2
(my weird notation to show that the OH on the alcohol groups are present and not O-)

Can just calculate pH using henderson-hasselbalch eqn:

pH = pKa + log (A-/HA )

oops too many unknowns; better just measure
It's not difficult to solve.

Assuming you use a 50% volumetric solution of ethylene glycol and water, and assuming volumetric additivity [edit-spelling] (probably off by 5-10% right there) you'd have a solution of 0.0180 molar ethylene glycol.

If the pKa is 14.22

Ka = 10^-14.22 = 6.0256 x 10^-15

Ka = [OH]*[C2H40H] / [C2H4(OH)2]

The concentrations of C2H4OH and OH- are equal and the concentration of C2H4(OH)2 doesn't change, so you can solve for them given the inital concentration of C2H4(OH)2.

6.0256 x 10^-15 ~ [OH-]^2 / 0.0180

Solving for the concentration of OH- gives 1.04 x 10^-8.

pOH = - log (1.04 x 10^-8) = 7.98

pH = 14-7.98 = 6.01

So if you have a 50% ethlyene glycol solution in water, you should have a pH of approximately 6.0.

If, after mixing the additives, you still have a pH below what you want, you might be able to add base to boost the pH, checking periodically with litmus paper.

If one of those additives is a buffer, though, you're doing your coolant a disservice.

Alchemy

Last edited by Alchemy; 10-30-2002 at 02:28 AM.
Alchemy is offline   Reply With Quote
Unread 10-30-2002, 03:54 AM   #14
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

So you just added something strongly basic to water (pK = 14), and the pH dropped? Reasonableness?

(I think you want to remove a proton when writing a reaction for the dissociation and not release an OH-)

HOC2H40H <--> -OC2H4OH + H+ (logKa1 = -14)

Not so simple in real world though.

Consider the equilibrium between copper ions and aluminum ions and the glycol as well (that will affect the speciation of the glycol). I dont have stability constants for such at fingertips; dont know what concentrations for metals is "normal".

Another complication with neutral/alkaline pH:

Don't forget to consider the solubility of CO2.

CO2(g) <-->CO2(l)
CO2(l) + H2O <--> H2CO3*
H2CO3* <--> H+ + HCO3^- (logKa1 = -6.3)
HCO3- <--> H+ + CO3^2- (log Ka2 = -10.3)

You'll find quite a lot of total dissolved CO2 (H2CO3* + HCO3- + CO3^2-) at pH 8 or higher. You can solve the above by considering that the relationship between CO2(g) and CO2(l) is related to Pco2 and the Henry's Law constant for CO2.

Not going to be able to solve this without an iterative approach. Mineql is a free download and not too bad (DOS but works mostly in XP/2k)
pHaestus is offline   Reply With Quote
Unread 11-13-2002, 03:20 PM   #15
EagleShadow
Cooling Neophyte
 
EagleShadow's Avatar
 
Join Date: Nov 2002
Location: Portland OR
Posts: 3
Default

Quote:
Originally posted by Brians256
Where does the voltage come from? Good question! My first thought was that it came from the ongoing galvanic corrosion. The voltage you got was because the dissimilar metals were forming a nice battery effect, and the effect became more pronounced as more charge carriers became available. But, I'm not sure of that. Wouldn't the electrical potential be there even if the solution had no charge carriers?

BTW: the chelating agent should trap the charge carriers. That's what it is for.
Guess they never did the water in a beaker with Iron and copper rods with ya in science class eh.

When you take Basic water and place it in a beaker. Take Iron Rod on 1 side. Copper on other. You can actually create electricity.

It boils down to the atomic substructure of one metal to the other. The water just acts like a bridge.

Put simply. Water and metals always makes battery's. Just most cases it's just not enough electric value to be of any problem.
( Been a while since I was in that class so pardon me for not remember'n all the details. ) " I just had my 10 year Reunion "
__________________
EagleShadow
EagleShadow is offline   Reply With Quote
Unread 11-14-2002, 03:11 PM   #16
Brians256
Pro/Staff
 
Brians256's Avatar
 
Join Date: Oct 2001
Location: Klamath Falls, OR
Posts: 1,439
Default

Unfortunately, my High School chemistry class was a total joke. The chemistry that I did learn (outside of class) was in the field of applied energetic exothermic reactions. I made fun stuff like black gunpowder, nitrocellulose, Cupric Azide, thermite, Nitrogen Tri-iodide, and basic coloring agents (such as magnesium for white and strontium for red).

Now, if the teacher had possessed some modicum of enthusiasm and/or the students were actually interested and motivated to learn (you can't just blame it on the teacher).... who knows what we could have learned?

Public school stinks because it's just a sad application of the lowest-common-denominator principle. Take the laziest and least talented person in the room (sometimes, although rarely, it's the teacher), and move the class at that person's speed.
Brians256 is offline   Reply With Quote
Unread 11-27-2002, 01:07 AM   #17
punish3r
Cooling Neophyte
 
punish3r's Avatar
 
Join Date: Nov 2002
Location: Colorado
Posts: 34
Default Ph Meter

Hi all, I know I'm new here, but thought I might be able to help with your Ph predicament. I've been working on a computer for the last three weeks or so that I'm turning into an electronics workstation, currently I've got an oscilloscope (Dave Jones' DSO Mk3) a DMM (PCMCIA card Ines i218) a frequency counter, a function generator and, the reason I'm posting this here, a home built Ph meter.

The meter is actually designed to plug into the DMM and provide a voltage reading (0.01v = 1pH @ 24 deg C) with about a 0.1 +/- pH accuracy. The whole setup cost me about $70 US, but fifty of that was the probe itself. The other twenty was wrapped up in casing the main circuit, buying more etchant, buying the PCB materials, and actual component cost. All in all a cheap beastie considering that pH add-on probes for Fluke DMM's start at one hundred US and go up from there. But I digress.

I'm using a Cole-Parmer U-59001-65 General Purpose pH electrode. Mainly because it's no maintenance, has a top reading of 80 deg C, is designed for permanent/semi-permanent submersion, and looks pretty cool I haven't bought a digital camera yet, so if you want to see the probe, go to
Cole-Parmer's Website

The circuit itself is actually a very simple design.



This was built with exacting measurements in mind, so the calibration is a bit long, but I'll put it here in case anyone is interested. Anyway. As far a design, it's basically an electronic representation of a mathematic equation. At 24 deg C, the equation for the slope is Y=-0.017X+7 so, to obtain the output in tenths of volts (just for a cleaner reading from the A/D DMM) the equation would be 10Y=-0.17X+70

The first chip (LM351) turns the probe output into a high impedance signal, the second chip (First half of LM353) controls the slope by taking the LM351 output and multiplies it by -0.17, and the third chip (second half of the LM353) while acting as a summing amplifier, controls the Y-intercept by adding 70mV to the signal.

Like I said before, the calibration is long, but makes sense as long as you understand the math. Start by shorting the inputs together, and adjust the offest on the LM351 to read 0mV at its output. Now, unshort the inputs, connect the probe, and place your probe in a pH standard, and measure the voltage at the output of the LM351. Multiply this voltage by 0.17, and now measure the voltage at the output of the first half of the LM353. Adjust the slope pot until you get the voltage (0.17 * X) INVERTED. i.e. if your reading at the first chip was Z adjust until you get -Z at the second chip. Finally, check the final output and adjust the Y-intercept pot until your voltage reading and the pH of the solution are matched. Remember, the way this circuit works (1pH = 0.01v) so if your standard is 10.1 pH your voltage reading will be 0.101v
Finally, check the meter by using it in other liquids that you know the pH of, just to verify proper calibration.
A few notes on the components used. The key on this circuit is accuracy. That's why the slope and y-intercept pots are both 15 turn. Yes, you can use a normal 3/4 or 1 turn, but I would recommend against it. Even with the x10 boost in voltage, the amounts we're dealing with are still so tiny, that a slight bump on the board might change the value of the pots enough to mess up your reading. On the chips, it's what I had on hand. If you can conceive of a better opamp to use, by all means do. The 351 and 353 are not application specific, so I'm sure there is a more 'refined' chip out there for this circuit.

As an afterthought, I have found digital pH meters around the net for about $60 US. The reasons I spent more than that are that one, I like building this stuff, and two, with a homebuilt design like this, you can build a second circuit to read the voltage, make it out of any kind of readout you want (LED, LCD, LPT input, etc) and get it that much more custom/closer to the way you like displays to be. Anyway. I know this was a bit long of a post, but I hope it helps.

The PÜNiSH3R
__________________
Fix reason firmly in her seat, and call on her tribunal for every fact, every opinion. Question with boldness even the existence of a God; because, if there be one, he must more approve of the homage of reason than that of blindfolded fear.
-Thomas Jefferson

Last edited by punish3r; 11-27-2002 at 05:36 AM.
punish3r is offline   Reply With Quote
Unread 11-27-2002, 08:24 AM   #18
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

Nice post Punisher!

Try www.labx.com for pH electrodes. There is a complete Corning pH meter/electrode setup for $27 on their auction list at the moment, and similar will always be around.
pHaestus is offline   Reply With Quote
Unread 12-01-2002, 12:48 AM   #19
Brians256
Pro/Staff
 
Brians256's Avatar
 
Join Date: Oct 2001
Location: Klamath Falls, OR
Posts: 1,439
Default

Nice! Real component analog work is uncommon these days.
Brians256 is offline   Reply With Quote
Unread 12-01-2002, 09:28 PM   #20
punish3r
Cooling Neophyte
 
punish3r's Avatar
 
Join Date: Nov 2002
Location: Colorado
Posts: 34
Default

I just figure what's the point in having to manually program a PIC to do something that two IC's that cost less than a dollar can do without an A/D conversion? Anyway, I suck at high-level programming. Lots better with hardware than I am with software. That's why I used to be Automatic_Jack. Anyway, getting off subject here.
__________________
Fix reason firmly in her seat, and call on her tribunal for every fact, every opinion. Question with boldness even the existence of a God; because, if there be one, he must more approve of the homage of reason than that of blindfolded fear.
-Thomas Jefferson
punish3r is offline   Reply With Quote
Unread 08-12-2007, 04:25 PM   #21
Uncle_Dave
Cooling Neophyte
 
Join Date: Aug 2007
Location: Boston MA
Posts: 2
Default Re: Coolant

The red cabbage caught my eye.


How did the PH meter work out?
Uncle_Dave is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 10:56 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...