Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]()
Take the 0.5" ID data:
total head loss = loss from tube's length + loss from tube's bend so ht = hb + hL ht = Kbv2/g + f(L/D)v2/g Kb = 42f (tabulated in Crane r/d = 8/0.5 or 16) L/D = 18/0.5 or 36 ht = 42(v2/g) + f(36)(v2/g) ht and v are known as is g. Just a matter of plug into spreadsheet and get units right at that point, right? |
![]() |
![]() |
![]() |
#27 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
well, anything can be back-calculated - but I'm not too comfy with 2 aspects:
- the length is quite short relative to the magnitude of the effect/difference, and - the effect of 'rounding' errors at the low drops is rather large NOTE: the 3/8 hose is clear vinyl, while the 1/2 and 5/8 are silicone needed is data from a 10' straight length - but I did not setup to do this -> my intent was only to provide WCers with some 'plug in' values, since most hose is actually used in short pieces to make a 90 these curves were generated as an adjunct to my running 'calibration' tests to establish the correction factors for different sized hose connections to the cross used to take the temp and pressure taps I could back out some connection values also; but as I use Cu thin wall pipe, the numbers would not be too useful |
![]() |
![]() |
![]() |
#28 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]()
All good points. Just looking at the graphs then for most users (1/2" ID and under 2gpm) the contribution is pretty minor anyway.
|
![]() |
![]() |
![]() |
#29 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
yup
but the 3 and 4gpm 'dreamers' need to get REALLY serious about each little thing - or get a nice BIG pump |
![]() |
![]() |
![]() |
#30 | |
Responsible for 2%
of all the posts here. Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
|
![]() Quote:
![]() So what do you estimate the friction factor to be? |
|
![]() |
![]() |
![]() |
#31 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
I think pHaestus does have a job, academic welfare makework - something like that.
|
![]() |
![]() |
![]() |
#32 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]()
It's cheaper to give me a little research money and salary than to turn me loose on society.
![]() |
![]() |
![]() |
![]() |
#33 |
Thermophile
Join Date: Oct 2002
Location: U.S.A = Michigan
Posts: 1,243
|
![]()
BillA,
Thank you very much for that graph, that is just the sort of info I was hope'n for. I have no doubt I'm one of your "dreamers", but am trying to get a idea of just how large a pump is needed and the head loss that will have to be overcome. Thanks again. BE |
![]() |
![]() |
![]() |