Default WOOT! I got me a flowmeter!

Check it out!

"BLUE WHITE" Flometer
model#: F-44500LH-8
Flow range: 0.5 to 5.0 gpm

(It's my first flowmeter, pardon the excitement! )
bigben2k is offline   Reply With Quote
Unread 04-16-2003, 09:00 PM   #2
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

ah Null-A Ben, welcome
your first flowmeter lesson

it is interesting (distressing ?) that their instructions do not give the device's head loss curve, but they no doubt have one if you request it

also they do not specify the straight pipe length required on the inlet and discharge side
(Brooks recommended 1.5' inlet and 1' for the discharge for the unit I had)

yes Null-A Ben, that is where I started too (oh so long ago it seems)

report back, eh ?
BillA is offline   Reply With Quote
Unread 04-16-2003, 09:23 PM   #3
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Duly noted, kind sir! (I'll certainly read over the installation manual very carefully)

When I saw the relatively small size of the marker, and considering that the connections are 1/2 NPT, I assumed that the headloss through it wouldn't be too great. The entrance is pretty narrow, but it is short.

The website was quite useless:
http://www.cie-inc.com/Manufacturers...f440_specs.htm

I found most of the info here:
http://www.kingsolar.com/catalog/mfg...f44500lh8.html
(note how the picture is incorrect)

This 1 page PDF confirmed the flow range for me:
http://www.fabcoplastics.com/catalog/section4/4-15.pdf

as did this page:
http://www.burtprocess.com/phplus/pr...m&series=F-440

and this 3 page PDF:
http://www.harringtonplastics.com/Ca...n5/5_43-45.pdf


Either way, at $6.50 (+$7.50 s&h), I think I'm off to a good start.
bigben2k is offline   Reply With Quote
Unread 04-16-2003, 09:35 PM   #4
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Ah! I found a good reference: the original Blue-White website

The dimensions

The specs

The manual

(still nothing about pressure drop, and installation details, but I will certainly contact tech support, thanks Bill!)
bigben2k is offline   Reply With Quote
Unread 04-21-2003, 11:24 PM   #5
Blackeagle
Thermophile
 
Join Date: Oct 2002
Location: U.S.A = Michigan
Posts: 1,243
Default

I posted in the rad thread, but here again.

Blue-White shows a max pressure drop of 2psi for your flow meter Ben. Found it by going through the differant steps as if I were ordering one. You'll come to a data page.

Does not say at what flow rate the 2psi head loss will happen at. Hhhmmmmmmmmmm.
Blackeagle is offline   Reply With Quote
Unread 04-21-2003, 11:30 PM   #6
Blackeagle
Thermophile
 
Join Date: Oct 2002
Location: U.S.A = Michigan
Posts: 1,243
Default

pH or BillA,

As you have and have used one of these, why are they so restrictive & just how restrictive are they?

On a small pump many use I can understand 2psi being pretty notable. But I thought both of you have larger pumps, wrong again?
Blackeagle is offline   Reply With Quote
Unread 04-22-2003, 01:00 AM   #7
Skulemate
Cooling Savant
 
Skulemate's Avatar
 
Join Date: Jul 2002
Location: Toronto, Canada
Posts: 381
Default

Well, seems reasonable to me that the max pressure drop will occur at the maximum rated flow (I'd assume that the meter is only calibrated to read to a certain value). Given that it's a "variable area" flow meter, I would assume it's some sort of a constriction (i.e. a Venturi Meter) that uses two pressure readings and the energy equation to solve for flow.
__________________
Michael E. Robbins
M.A.Sc. Candidate, University of Toronto

12.1 GHz of AMD's finest (17.7 GHz total) crunching proudly for the AMDMB.com Killer Frogs
SETI BOINC: Dual Opteron 246s (Iwill DK8N) | XP2800+ (Shuttle SN41G2) | 3x XP2400+ (ASUS A7N266-vm)
SETI BOINC: 2x P4 2.8E (ASUS P4R800-vm) | Crunching 24/7
Skulemate is offline   Reply With Quote
Unread 04-22-2003, 01:32 AM   #8
BillA
CoolingWorks Tech Guy
Formerly "Unregistered"
 
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
Default

no, the flow rises vertically and 'supports' a slug
5 % ?
that is a sad joke
the slug bobbles around like Janet Reno's hand

and look at the divisons
do I see a tick at each 0.5 gal ?
if so,
that is what can BE READ, interpolations are just to amuse

my old rad data was run with a spring loaded "variable area" flow meter with a magnetic sensor giving 0 - 5 VDC output
- I worked my butt off 'calibrating' it, then later had to revise all the data

I still have a couple of them, $20 ea + shipping

N.B. a magnetic flowmeter at $300 is a MUCH better deal

EDIT: gd qwerty keyboard

Last edited by BillA; 04-22-2003 at 01:37 AM.
BillA is offline   Reply With Quote
Unread 04-22-2003, 01:36 AM   #9
Alchemy
Cooling Savant
 
Join Date: Oct 2002
Location: Boston
Posts: 238
Default

Quote:
Originally posted by Skulemate
Well, seems reasonable to me that the max pressure drop will occur at the maximum rated flow (I'd assume that the meter is only calibrated to read to a certain value). Given that it's a "variable area" flow meter, I would assume it's some sort of a constriction (i.e. a Venturi Meter) that uses two pressure readings and the energy equation to solve for flow.
It's clearly a rotameter.

Ben, you do realize this must be mounted perfectly vertical? And you're sure the rotameter is calibrated for water?

Alchemy
Alchemy is offline   Reply With Quote
Unread 04-22-2003, 07:04 AM   #10
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Yes, I understand the requirement. I'm still waiting for a reply from tech support on the leading and trailing straight pipe length.

2 psi is correct, but I would suspect that that could be above 5 gpm.
bigben2k is offline   Reply With Quote
Unread 04-22-2003, 11:09 AM   #11
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

2PSI eh? The conversion is (I think) 0.433 PSI per ftH2O so

~4.6 ft H2O pressure drop. What's your pump rated at again? Most of the ones I use in my system's cooling loop can't push the little bell up far above 1.2 GPM...
pHaestus is offline   Reply With Quote
Unread 04-22-2003, 11:17 AM   #12
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Yep, 2.0 psi is 55.36" of water, or 4.6 feet. ( www.convert-me.com )

My pump can do max 14.6 feet of head. At 2 psi, it would flow 440 gph, or 7.3 gpm (assuming that there are no other restrictions).

If I can get a couple of pressure gauges, or slap together a manometer, I should easily be able to take some flow measurements of a heatercore.

Hummmm ...manometer...
bigben2k is offline   Reply With Quote
Unread 04-22-2003, 11:43 AM   #13
BrianH
Cooling Savant
 
Join Date: May 2002
Location: Ottawa, Ont, Canada
Posts: 115
Default

Work any of these work with little loss?
BrianH is offline   Reply With Quote
Unread 04-22-2003, 12:06 PM   #14
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

LOL! the pressure drop chart is there, but no units are specified!

Assuming it's in psi, you'd want to stick with the 1/2 NPT connections.

The turbine wheels have a huge drop.
bigben2k is offline   Reply With Quote
Unread 04-22-2003, 12:46 PM   #15
BrianH
Cooling Savant
 
Join Date: May 2002
Location: Ottawa, Ont, Canada
Posts: 115
Default

Yes, I would also assume PSI also

For the 1/2" low flow units, the pressure drop for 3 GPM (180GPH) rate is very low (ie almost zero)

Most of us are lucky to get more that 90 GPH (1.5GPM) flow thru our systems.

But I see now that they only go down to 1.5GPM. Oh well, you guys with higher flow rates might want to look at this
BrianH is offline   Reply With Quote
Unread 04-22-2003, 01:13 PM   #16
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

There's one that'll take measurements between 0.5 and 5 gpm.

Either way, pHaestus is right, I can't use my flow meter permanently in a loop, at least not until I get rid of the core, for the #rotor chiller, and even then...

EBay alert setup...
bigben2k is offline   Reply With Quote
Unread 04-22-2003, 01:48 PM   #17
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Quote:
Originally posted by BrianH
Yes, I would also assume PSI also

For the 1/2" low flow units, the pressure drop for 3 GPM (180GPH) rate is very low (ie almost zero)

Most of us are lucky to get more that 90 GPH (1.5GPM) flow thru our systems.

But I see now that they only go down to 1.5GPM. Oh well, you guys with higher flow rates might want to look at this
It's no good.

The flow range from 0.5 to 5 gpm is only for the 1/4" port, which drops 3 psi at 3 gpm. The units with the 1/2" ports start measuring flow at 4gpm.

Oh well.
bigben2k is offline   Reply With Quote
Unread 04-22-2003, 01:54 PM   #18
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

Which takes us back to the idea of just using a differential pressure transmitter on inlet and outlet of radiator and choosing a rad that BillA had tested. You measure deltaP and then can calculate Q. Simple enough and no added restriction.

I have a GPI paddle-wheel type for my test system, but I don't see the need for flowmeters in cooling loops I am actually using. The deltaP measurement I could go for, however
pHaestus is offline   Reply With Quote
Unread 04-22-2003, 02:00 PM   #19
BrianH
Cooling Savant
 
Join Date: May 2002
Location: Ottawa, Ont, Canada
Posts: 115
Default

Quote:
Oh well.
My feelings exactly
BrianH is offline   Reply With Quote
Unread 04-22-2003, 02:22 PM   #20
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Quote:
Originally posted by pHaestus
Which takes us back to the idea of just using a differential pressure transmitter on inlet and outlet of radiator and choosing a rad that BillA had tested. You measure deltaP and then can calculate Q. Simple enough and no added restriction.

I have a GPI paddle-wheel type for my test system, but I don't see the need for flowmeters in cooling loops I am actually using. The deltaP measurement I could go for, however
Or simply, I could build a manometer, and use the flowmeter to measure individual components. Whoever said that all I want to measure is the dP through a heatercore?

But I still need a cheap build guide for a manometer. Google time. The pressure gauges are starting to look better.
bigben2k is offline   Reply With Quote
Unread 04-22-2003, 03:07 PM   #21
Blackeagle
Thermophile
 
Join Date: Oct 2002
Location: U.S.A = Michigan
Posts: 1,243
Default

pHaestus,

So if I wanted to get a rough estimate of a whole systems flow, I would need a pressure gauge near the pumps outlet and another near the intake. Then the differance between the two gauges in psi can be converted to head loss, correct?

Thank you,

BE
Blackeagle is offline   Reply With Quote
Unread 04-22-2003, 03:11 PM   #22
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

If you know the pump's curve, yes, with a tiny bit of error, but "good enough".
bigben2k is offline   Reply With Quote
Unread 04-22-2003, 03:29 PM   #23
Blackeagle
Thermophile
 
Join Date: Oct 2002
Location: U.S.A = Michigan
Posts: 1,243
Default

Been doing some more looking around at Blue-White. The digital flow meter data sheet shows 0 pressure drop. But just the fact of adding in a T fixture has a head loss, so what is up with that?

Also looked at more flow meter data. Of the 4 I checked all have a max. head loss of 2 psi. Accuracy levels do change, ones I looked at were from 2% to 5%.
Blackeagle is offline   Reply With Quote
Unread 04-22-2003, 03:35 PM   #24
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Nice Digital meter. Zero head indeed: it's probably a paddle type (not paddlewheel) meter.

Also costs <$400.00
bigben2k is offline   Reply With Quote
Unread 04-22-2003, 03:48 PM   #25
pHaestus
Big Player
Making Big Money
 
pHaestus's Avatar
 
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
Default

You must consider the application of the equipment FIRST.

Look for spec sheets and prices and such when you know what is required to answer a question. Otherwise you either get sold something much more expensive than needed, or you buy junk that doesn't work.

This is about the sum of the lessons I can provide; still sorting out the good stuff from the junk at my house
pHaestus is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 05:37 PM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...