http://www.overclockers.com/articles886/
he tested it with the ehiem 1260 but tested all the others with a 1048. how can you compare the rbx in the same test results as the others when they use differant pumps ?
__________________
Folding , Folding , Folding ! |
![]() |
![]() |
![]() |
#2 |
Pro/Guru - Uber Mod
Join Date: Sep 2002
Location: Indiana
Posts: 834
|
![]()
Well, he does at least provide the pressure drop measured for the different test results.
IF you ignore the heat put into the system by the pump, there is some basis for comparing the numbers. The way I see it, the RBX performs about the same as the Swiftech MCW5002 IF you provide seven times the pressure drop. Not good, especially considering the prevalence of GPU blocks these days. It looks to me like, the RBX is not a contender. |
![]() |
![]() |
![]() |
#3 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]()
My comments copied from the liquidninjas shitstorm thread:
And keep in mind JoeC tested with the LEAST restrictive of the inlet inserts! I wish Joe would have tested out all of the nozzles and with the same pump in all cases. His 1.0GPM starting flow point is in a spot where most waterblock C/W curves are in their "knee" and so a small difference in final flow rate can have a fairly big impact on the C/W. If the RBX only moved say 0.6-0.7 GPM with with the 1048 then it might perform a lot worse.
__________________
Getting paid like a biker with the best crank... -MF DOOM |
![]() |
![]() |
![]() |
#4 | |
Cooling Neophyte
Join Date: Apr 2003
Location: Kingston, ON, Canada
Posts: 31
|
![]() Quote:
__________________
http://www.devhardware.com |
|
![]() |
![]() |
![]() |
#5 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]()
No DMOS. All blocks are tested by adjusting flow rate without the waterblock to 1.0GPM. When the block is added then flow rate decreases at a varying amount (depending upon flow resistance of block). So by using a higher pressure pump (1260) for the RBX it is very difficult for me to wrap my head around how I can compare the data with earlier tests (using 1048). Most of the other blocks have a fairly low decrease in flow anyway; the RBX is much higher even with a higher pressure pump though.
__________________
Getting paid like a biker with the best crank... -MF DOOM |
![]() |
![]() |
![]() |
#6 |
Cooling Savant
Join Date: Mar 2003
Location: notts uk
Posts: 408
|
![]()
it would be ok if he used both pumps to test all blocks as the other blocks tested could give better results on a 1260 limited to 1gpm like the rbx would give very bad results on a 1048.
what we want to see is how a range of blocks work with the same test setup each time. if it's not the same then it make comparing very difficult.
__________________
Folding , Folding , Folding ! |
![]() |
![]() |
![]() |
#7 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]()
What we want to see is EVERYTHING
When we want to see it is NOW What we want it to cost is NOTHING Gotta make some compromises. From the standpoint of reader and interested third party I don't find JoeC's testing completely satisfying. But when wearing the reviewer hat it makes a hell of a lot more sense than what I am doing (I just spent 8 days reviewing a single heatsink).
__________________
Getting paid like a biker with the best crank... -MF DOOM |
![]() |
![]() |
![]() |
#8 |
Cooling Savant
Join Date: Mar 2003
Location: notts uk
Posts: 408
|
![]()
wont the 1260 have more pressure than the 1048 even though it's limited to 1gpm ?
__________________
Folding , Folding , Folding ! |
![]() |
![]() |
![]() |
#9 |
Thermophile
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
|
![]()
I thought that JoeC's results were measured by subtracting the water temperature from the die temperature? The amount of impact that the larger pump would have would then be relative to the secondary heat losses of the system as a result of the warmer water flowing through the loop.
|
![]() |
![]() |
![]() |
#10 | |
Thermophile
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#11 |
Cooling Savant
Join Date: Mar 2003
Location: notts uk
Posts: 408
|
![]()
thats whats throwing me looking at joes results and treating them like the flow vs pressure predictions of BillA's data.
__________________
Folding , Folding , Folding ! |
![]() |
![]() |
![]() |
#12 |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]()
I had a grasp for why JoeC was starting with 1.0GPM sans block and then recording how much flow rate dropped along with performance at the resulting flow rate. It isn't the way I personally do it, but it seemed like a good practical approach to streamlining testing. If a block A drops more in flow rate than block B then it's obviously more restrictive. But introducing another variable (a different pump used now) really makes it difficult for me to follow what JoeC is trying to convey with the results. For example the switch from 1048 to 1260 would have effects on final flow rates for RBX>>PolarFlo>MC5002>Slit Edge. Are these effects enough to shift C/W values? Dunno.
Or am I reading JoeC's tests incorrectly? I am assuming from the tables of data that he begins with a flow rate of 1.00GPM without block and that blocks will reduce flow rates by differing amounts depending upon resistance. Or are these two different tests?
__________________
Getting paid like a biker with the best crank... -MF DOOM |
![]() |
![]() |
![]() |
#13 |
Thermophile
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
|
![]()
The problem with doing what Joe has done is that different pumps obviosuly have different PQ characteristics. How one pump reacts when artificially restricted to 1GPM with a subsequent resistance added is going to be different to how a different pump reacts artificially restricted to 1GPM with the same resistance added.
JoeC needs to settle on either using a fixed pressure drop across the block (ala BillA), a fixed pump (fairly useful to many people with a similar pump - not so useful for flow rate predictions though), or a fixed flow rate and measure the PD at that fixed flow rate. He's created a bit of a mish-mash of data here. The flow-rates are all close enough to be roughly comparable, but Joe seems to be reluctant to settle on any of the above three scenarios, and has instead settled on something weird that sits in-between. Last edited by Cathar; 11-26-2003 at 03:16 PM. |
![]() |
![]() |
![]() |
#14 | |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]() Quote:
__________________
Getting paid like a biker with the best crank... -MF DOOM |
|
![]() |
![]() |
![]() |
#15 |
Cooling Savant
Join Date: Nov 2002
Location: winnipeg
Posts: 129
|
![]()
You could look at the valve been set to 1 gpm as the resistance of an artificial rad. I wonder what pressure drop the valve is equivilent to? Though changing the pump would throw that idea out of wack.
The biggest problem I have with the test is the difference in order between the PolarFlo and the split edge waterblock. On BillA's tests the spilt edge is 2C better than the PolarFlo while Joe's test has the PolarFlo 1C better than the split edge block. If the order of blocks aren't consistant on die simulators, then what chance do they have of being consistant on actual cpu's? If there is no consistancy, then what good is the data? Another problem I have is that the temperature gradient across the surface of the cpu may be alot greater than with a die simulator. It may possibly even change patterns with different load programs. One block could perform better than another with prime95 and perform worse with cpuburn. I haven't seen any data that proves the cpu temp gradient is consistant. |
![]() |
![]() |
![]() |
#16 | ||
Thermophile
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
|
![]() Quote:
Quote:
Unsure of how large such an effect is. I know that Les has made a few efforts of calculating such for different block design types. For now though that's a problem that's probably best left in the "too hard" basket. |
||
![]() |
![]() |
![]() |
#17 | |
Cooling Savant
Join Date: Nov 2002
Location: winnipeg
Posts: 129
|
![]() Quote:
Edit: I just reread BillA's test and it seems to contradict what you just said. Do you have a link to where it was discussed that the block wasn't that flat? Last edited by freeloadingbum; 11-26-2003 at 05:32 PM. |
|
![]() |
![]() |
![]() |
#18 | |
Big PlayerMaking Big Money
Join Date: Aug 2001
Location: irc.lostgeek.com #procooling.com
Posts: 4,782
|
![]() Quote:
And as the main difference between Prime95 and K7Burn is that the first accesses system memory, I doubt that one would result in a different ranking than another on Athlons or P4s. It brings up an interesting point though: How about the integrated memory controller of the A64? How hot does that get, and could whether a program accesses system ram or not make a big difference in temps? Something I hadn't thought of before (wish AMD were as free with tech docs as Intel is).
__________________
Getting paid like a biker with the best crank... -MF DOOM |
|
![]() |
![]() |
![]() |
#19 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
I believe that I tested a version of the PolarFLO prior to the current one
- one would have to ask Steve at Horse of Iron Steve, BTW, is in a class with only N8 as the other member |
![]() |
![]() |
![]() |
#20 | |
Thermophile
Join Date: Sep 2002
Location: Melbourne, Australia
Posts: 2,538
|
![]() Quote:
Compare BillA's MCW5000A picture (somewhat flattish all over), to BillA's PolarFlo (which has a rapidly falling gradient of non-flatness away from the very middle). MCW5000A ![]() PolarFLO ![]() Maybe it's just a matter of personal interpretation. I don't pretend that I can do a whole lot better myself when I lap blocks, but I do believe that this is an area that does need more exploration. Have heard some conflicting points of view on the matter of what's desirable. Some say convex, especially for the IHS chips. Some say very slightly concave for bare-die CPU's as CPU die's are very slightly convex themselves, and some say that as flat as possible is the best tradeoff. I tend to agree with flat as possible, |
|
![]() |
![]() |
![]() |
#21 |
CoolingWorks Tech Guy Formerly "Unregistered"
Join Date: Dec 2000
Location: Posts: 2,371.493,106
Posts: 4,440
|
![]()
the PolarFLO shown is convex, rather much so
but it is only the area in the center that is of interest and if one starts counting fringes the two shown are pretty equal with an IHS, convex will still work - but I too prefer flat |
![]() |
![]() |
![]() |
#22 |
Cooling Savant
Join Date: Nov 2002
Location: winnipeg
Posts: 129
|
![]()
After re-analyzing all the data, it appears that the split edge is the block that's most out of sync with BillA's and Joe's results, not the polarflo. A warped baseplate may be the culprit. Player0's test also seemed to show a poor result for this block.
If the above statement holds true, then I expect the RBX to receive a good asswhooping from the WW by about 1.5C (or more). EDIT: Cancel that perdiction. I just read Joe's update on the RBX. Last edited by freeloadingbum; 11-28-2003 at 10:20 PM. |
![]() |
![]() |
![]() |
#23 |
Cooling Savant
Join Date: Mar 2001
Location: Denver, CO
Posts: 107
|
![]()
I wonder how man blocks DD has put the "accelerator plate" in sideways? http://www.overclockers.com/articles886/ has anyone talked to them about it?
__________________
Folders: I've given up folding ![]() |
![]() |
![]() |
![]() |
#24 |
Cooling Savant
Join Date: Mar 2003
Location: notts uk
Posts: 408
|
![]()
and lets hope he uses the 1048 to test this time.
Thanks BillA ![]()
__________________
Folding , Folding , Folding ! |
![]() |
![]() |
![]() |
#25 |
Cooling Neophyte
Join Date: Jul 2003
Location: singapore
Posts: 39
|
![]()
the test has been updated, puts the RBX at a c/w of 12
![]() |
![]() |
![]() |
![]() |