Go Back   Pro/Forums > ProCooling Technical Discussions > General Liquid/Water Cooling Discussion
Password
Register FAQ Members List Calendar Chat

General Liquid/Water Cooling Discussion For discussion about Full Cooling System kits, or general cooling topics. Keep specific cooling items like pumps, radiators, etc... in their specific forums.

Reply
Thread Tools
Unread 08-08-2003, 02:33 AM   #1
Gooserider
Cooling Savant
 
Gooserider's Avatar
 
Join Date: Jun 2003
Location: North Billerica, MA, USA
Posts: 451
Am I estimating my airflow needs right?

I have been working on figuring out the cooling reqirements for the system I'm working on, and want to see if there are any obvious problems with the way I'm doing it.

I am water cooling the all the major heat producers in the system. The radiator will be mounted in the front of the case, with the fans behind it sucking through the radiator, and dumping into the case. The air will then pass through the case and exit out the back. To control the airflow and contain the noise, I intend to seal all case openings other than the radiator and the 3 fan outlets on the back of the case.

Some of the 'radical coolers' I've talked to don't think sending the air from the rad through the case is a good idea, but I don't think it will hurt anything since the figures I've seen say air only gets warmed 2-3*C max on its way through a WC rad. I don't see that as a significant diference from ambient.

For the purposes of making my estimate, I am trying to be very conservative. I think it is better to estimate to high and have to turn fans down / off, rather than not having enough cooling power available when it's needed.

I am making two assumptions, 1. That all the heat to be dissipated will be coming out of the radiator (I know it's false, but it makes the numbers much easier...) 2. That my maximum allowed temperature rise in the rad is 10*C. (I probably could get away with a bigger Delta-T, but that's part of being conservative

My heat budget is as follows:

2 X CPU @ 100W = 200W
1 X pump @ 50W = 50W
4 X HDD @ 18W = 64W
1 X FGF @ 100W = 100W (FGF = Fudge and Growth Factor :wink: )
----------------------
Total Heat out = 414 W

According to the NMB website, to calculate required air flow, one uses the following formula

required CFM = (1.7 X Watts) / max allowed Delta-T *C

or

required CFM = 1.7 X 414 / 10 = 72.4 CFM

Does this seem like a valid figure?

Gooserider
__________________
Designing system, will have Tyan S2468UGN Dual Athlon MOBO, SCSI HDDS, other goodies. Will run LINUX only. Want to have silent running, minimal fans, and water cooled. Probably not OC'c
Gooserider is offline   Reply With Quote
Unread 08-13-2003, 10:17 AM   #2
bigben2k
Responsible for 2%
of all the posts here.
 
bigben2k's Avatar
 
Join Date: May 2002
Location: Texas, U.S.A.
Posts: 8,302
Default

Got a link?

The formulae can only apply to a specific model of core, no?
bigben2k is offline   Reply With Quote
Unread 08-13-2003, 11:38 AM   #3
Since87
Pro/Guru - Uber Mod
 
Join Date: Sep 2002
Location: Indiana
Posts: 834
Default Re: Am I estimating my airflow needs right?

Quote:
Originally posted by Gooserider


According to the NMB website, to calculate required air flow, one uses the following formula

required CFM = (1.7 X Watts) / max allowed Delta-T *C

or

required CFM = 1.7 X 414 / 10 = 72.4 CFM

Does this seem like a valid figure?
I suspect (haven't worked it out) that the equation from the NMB website refers to the Delta-T between incoming air temperature and outgoing air temperature.

My impression is that you might be treating that Delta-T as if it is the differential between the water temperature and the air temperature.

These are significantly different issues. The water temperature will be somewhat higher than the temperature of the air exiting the rad.
Since87 is offline   Reply With Quote
Unread 08-18-2003, 11:20 AM   #4
CoolROD
Cooling Savant
 
CoolROD's Avatar
 
Join Date: Mar 2003
Location: North Carolina, USA
Posts: 225
Default

If you put 414W into your rad and 72.4 cfm air at 100 kPa 22Deg. C

Your exit air temp will be 32.2 deg C or 90 Deg F

I will be glad to discuss this.

The delta T (air temp) was 10.2 deg. C

My assumption was the same as Since87's so I checked it...
__________________
Jack of all Trades, Master of None.
CoolROD is offline   Reply With Quote
Unread 08-18-2003, 01:51 PM   #5
Gooserider
Cooling Savant
 
Gooserider's Avatar
 
Join Date: Jun 2003
Location: North Billerica, MA, USA
Posts: 451
Default Hmmm... Interesting!

There was an article either here or on Overclockers that said the temp change for air going through a WC rad would be 2-3* C max, based both on math and actual measurments.
I believe the reasoning was based at least in part on the idea that thermal transfer takes time, and the air wouldn't be spending long enough passing through the rad to do the complete heat transfer.

The article was by BillA, or one of the other senior cooling gurus, so I'm inclined to believe he knows what he's talking about...

One of the ideas I've had, is that since I'm using a single pass rad (FedCo 2-342) there will be a significant temp. gradient between the inlet at the bottom, and the outlet at the top. Per heat xfer laws, the greater the temp difference, the more heat will be transferred. Since I'll be using two fans in parallel, the lower fan will get hotter air than the top fan, so why not duct it out the bottom of the case? This would keep the worst of the heat load from getting blown back through the case.

Gooserider
__________________
Designing system, will have Tyan S2468UGN Dual Athlon MOBO, SCSI HDDS, other goodies. Will run LINUX only. Want to have silent running, minimal fans, and water cooled. Probably not OC'c
Gooserider is offline   Reply With Quote
Unread 08-18-2003, 02:55 PM   #6
t00lb0x
Cooling Savant
 
t00lb0x's Avatar
 
Join Date: May 2003
Location: In a box
Posts: 221
Default

Quote:
Originally posted by CoolROD
If you put 414W into your rad and 72.4 cfm air at 100 kPa 22Deg. C

Your exit air temp will be 32.2 deg C or 90 Deg F

I will be glad to discuss this.

The delta T (air temp) was 10.2 deg. C

My assumption was the same as Since87's so I checked it...
Would you please elaborate on this forumla. Or at least show the formula. That would be really, really helpful.
__________________
"If you can't dazzle them with brilliance, baffle them with bullshit"
t00lb0x is offline   Reply With Quote
Unread 08-18-2003, 02:59 PM   #7
CoolROD
Cooling Savant
 
CoolROD's Avatar
 
Join Date: Mar 2003
Location: North Carolina, USA
Posts: 225
Default

Sure, I will post a spreadsheet tonight that anyone can use.
Do you have Excel?
__________________
Jack of all Trades, Master of None.
CoolROD is offline   Reply With Quote
Unread 08-18-2003, 03:01 PM   #8
Since87
Pro/Guru - Uber Mod
 
Join Date: Sep 2002
Location: Indiana
Posts: 834
Default Re: Hmmm... Interesting!

Quote:
Originally posted by Gooserider
There was an article either here or on Overclockers that said the temp change for air going through a WC rad would be 2-3* C max, based both on math and actual measurments.
I believe the reasoning was based at least in part on the idea that thermal transfer takes time, and the air wouldn't be spending long enough passing through the rad to do the complete heat transfer.
Find the article and see what heatload that 2-3°C figure was based on.

I'll bet it wasn't 414 Watts.
Since87 is offline   Reply With Quote
Unread 08-18-2003, 03:03 PM   #9
t00lb0x
Cooling Savant
 
t00lb0x's Avatar
 
Join Date: May 2003
Location: In a box
Posts: 221
Default

Quote:
Originally posted by CoolROD
Sure, I will post a spreadsheet tonight that anyone can use.
Do you have Excel?
Yes I do, could you please post it. Thanks a lot (i'll have to save it because its helpful.)
__________________
"If you can't dazzle them with brilliance, baffle them with bullshit"
t00lb0x is offline   Reply With Quote
Unread 08-18-2003, 03:04 PM   #10
Since87
Pro/Guru - Uber Mod
 
Join Date: Sep 2002
Location: Indiana
Posts: 834
Default

Quote:
Originally posted by CoolROD
Sure, I will post a spreadsheet tonight that anyone can use.
That would be great. I tend to avoid doing these calculations because of all the conversions that need to be looked up.
Since87 is offline   Reply With Quote
Unread 08-18-2003, 03:48 PM   #11
t00lb0x
Cooling Savant
 
t00lb0x's Avatar
 
Join Date: May 2003
Location: In a box
Posts: 221
Default

Yeah but it would be good just to know it in the first place. Formulas are always helpful, wait, they should have a thread of all the equations that could be used. Like C/W, airflow, and stuff like that.
__________________
"If you can't dazzle them with brilliance, baffle them with bullshit"
t00lb0x is offline   Reply With Quote
Unread 08-18-2003, 03:59 PM   #12
CoolROD
Cooling Savant
 
CoolROD's Avatar
 
Join Date: Mar 2003
Location: North Carolina, USA
Posts: 225
Default

I am starting a new one tonight. The first post will relate total watts dissipated from the radiator, cfm, and the temperature change of the air through the radiator. Keep in mind that this has all been covered before, but is burried in the forum.
__________________
Jack of all Trades, Master of None.
CoolROD is offline   Reply With Quote
Unread 08-18-2003, 03:59 PM   #13
t00lb0x
Cooling Savant
 
t00lb0x's Avatar
 
Join Date: May 2003
Location: In a box
Posts: 221
Default

Yeah but having it in one place would be helpful to noobs like me.
__________________
"If you can't dazzle them with brilliance, baffle them with bullshit"
t00lb0x is offline   Reply With Quote
Unread 08-18-2003, 04:07 PM   #14
Zhentar
Cooling Savant
 
Join Date: Apr 2003
Location: Madison, WI
Posts: 225
Default

There's a flaw in your heat calcs- the pump/HDs will not make 114 watts of heat. Most of this energy is converted to kinetic energy moving either the water or platters.

I'm guessing 250W would be much more realistic, and thats including growth factor.
Zhentar is offline   Reply With Quote
Unread 08-19-2003, 12:12 AM   #15
CoolROD
Cooling Savant
 
CoolROD's Avatar
 
Join Date: Mar 2003
Location: North Carolina, USA
Posts: 225
Default

I have uploaded the work that relates airflow to temperature rise through a radiator. Since I have to host the information, I am going to hold off on creating a new thread for formulas and spreadsheets until I complete more of them.

This example assumes no pressure drop across the radiator. This is not true, but the pressure difference is insignificant and I will do the thermo the hard way to prove it. I am doing this for myself anyway, b/c I want to model my whole system.

Here is an example of the work. You can launch the excel spreadsheet from the link at the top of the page -or- click here.

edit: let me know if that is what you wanted.
The variables are kind of messy b/c I haven't found the right ones in Excel yet.
__________________
Jack of all Trades, Master of None.

Last edited by CoolROD; 08-27-2003 at 07:15 PM.
CoolROD is offline   Reply With Quote
Unread 08-19-2003, 12:14 AM   #16
t00lb0x
Cooling Savant
 
t00lb0x's Avatar
 
Join Date: May 2003
Location: In a box
Posts: 221
Default

Thanks man! I've been waiting for this.
__________________
"If you can't dazzle them with brilliance, baffle them with bullshit"
t00lb0x is offline   Reply With Quote
Unread 08-19-2003, 12:21 AM   #17
CoolROD
Cooling Savant
 
CoolROD's Avatar
 
Join Date: Mar 2003
Location: North Carolina, USA
Posts: 225
Default

No problem -That was an instant response! I hope it is not too messy. I am sure it will look terrible when I critique it tomorrow!
__________________
Jack of all Trades, Master of None.
CoolROD is offline   Reply With Quote
Unread 08-19-2003, 12:22 AM   #18
t00lb0x
Cooling Savant
 
t00lb0x's Avatar
 
Join Date: May 2003
Location: In a box
Posts: 221
Default

Yeah, it was quick, I have been waiting for this almost all day (sad...) That looks pretty good and it makes sense. So if you can improve on that, that is pretty impressive.
__________________
"If you can't dazzle them with brilliance, baffle them with bullshit"
t00lb0x is offline   Reply With Quote
Unread 08-19-2003, 02:16 AM   #19
Solarian League
Cooling Neophyte
 
Solarian League's Avatar
 
Join Date: Jun 2003
Location: Solarian League
Posts: 66
Default

ouch! i'm looking at 10-15 degree increase in my delta

enter temp is 22c and my watt load is about 660 which yields an exit temp of about 35c

ouch
Solarian League is offline   Reply With Quote
Unread 08-19-2003, 03:00 AM   #20
Les
Cooling Savant
 
Join Date: Oct 2001
Location: Wigan UK
Posts: 929
Default

Some sums previously shown in a "Water Cooling Simulator Discussion" thread http://forums.procooling.com/vbb/sho...5&pagenumber=4

Les is offline   Reply With Quote
Unread 08-19-2003, 03:15 AM   #21
Gooserider
Cooling Savant
 
Gooserider's Avatar
 
Join Date: Jun 2003
Location: North Billerica, MA, USA
Posts: 451
Default Some reference stuff...

Quote:
Since87: quote: Originally posted by Gooserider "There was an article ... that said the temp change for air going through a WC rad would be 2-3* C max..." Since87: Find the article and see what heatload that 2-3°C figure was based on. I'll bet it wasn't 414 Watts.
Well, I've been searching, haven't found it yet, but here are some other things I found on Overclockers that appear relevant...

"Radiator System Resistance" This is the source for my assumption of 50% of rated fan performance.

"Pump-Off"
Commentary on the influence of system resistance on waterflow from pumps. (Note that I'm designing for a comparatively high flow volume.)

"Waterblock Bench Testing Results"
Discussion of waterblock testing.

"Water Cooling Flow Rate and Heat Transfer"
Zhentar, see the bottom part of this one, it addresses your comment about pump heat. (sorry, you got it wrong...)

"Measuring Airflow Resistance"
An interesting background peice on how airflow resistance is measured.

"Radiator Heat Dissipation Testing"
This is a primary info source, though a bit dated. It does it's measurements in BTU's, and I forget offhand how they xlate into Watts, but an interesting read. In terms of the rad that I'm using vs. this article; my rad is bigger than either the Serck or the Big Momma. It is the same type of construction as the BM, but is a single pass design which gives it low flow resistance like the Serck. Some crude testing w/ just the rad shows my pump can push about 6GPM through it, showing ~6' of head loss, out of a rated 14' head and 8 GPM flow )

It might also be worth reviewing the Water Cooling Simulator Discussion message area here on Pro-Cooling, there is alot of good info there.

Gooserider
__________________
Designing system, will have Tyan S2468UGN Dual Athlon MOBO, SCSI HDDS, other goodies. Will run LINUX only. Want to have silent running, minimal fans, and water cooled. Probably not OC'c
Gooserider is offline   Reply With Quote
Unread 08-19-2003, 06:21 AM   #22
Since87
Pro/Guru - Uber Mod
 
Join Date: Sep 2002
Location: Indiana
Posts: 834
Default

Quote:
Originally posted by CoolROD

This example assumes no pressure drop across the radiator. This is not true, but the pressure difference is insignificant and I will do the thermo the hard way to prove it. I am doing this for myself anyway, b/c I want to model my whole system.
In what sense is pressure drop across the radiator insignificant? (In terms of power dissipated due to the flow through it?)

I haven't had a chance to look at the spreadsheet. (Computer is under construction and doesn't have Excel ATM. Will take a look when I get to work.)

How about posting your simulation work in the Water Cooling Simulator Discussion forum? It will make it easier to find at a later date. BTW, you can attach small files to your post, (like a zipped spreadsheet) if long term hosting is problematic.
Since87 is offline   Reply With Quote
Unread 08-19-2003, 06:42 AM   #23
Since87
Pro/Guru - Uber Mod
 
Join Date: Sep 2002
Location: Indiana
Posts: 834
Default Re: Some reference stuff...

Quote:
Originally posted by Gooserider

"Water Cooling Flow Rate and Heat Transfer"
Zhentar, see the bottom part of this one, it addresses your comment about pump heat. (sorry, you got it wrong...)
Yes, all the power going into the pump in a closed loop system exits the pump as heat. (The proportion that exits through the pump casing and through the water will vary depending on the system.) Only in a system where water is pumped from one location to another, is power exiting 'the system' in the form of kinetic energy.
Since87 is offline   Reply With Quote
Unread 08-19-2003, 07:09 AM   #24
CoolROD
Cooling Savant
 
CoolROD's Avatar
 
Join Date: Mar 2003
Location: North Carolina, USA
Posts: 225
Default

Quote:
Originally posted by Since87:

In what sense is pressure drop across the radiator insignificant? (In terms of power dissipated due to the flow through it?)
The maximum pressure generated by the fan is only around 1" W.C. or .036 PSI. For comparison: the atmosphere we are working in is 407" W.C. or 14.7 PSI. In this context, the temperature change of the air due to the change in it's internal pressure is small. I said that I am going to figure this the hard way (which includes the air's internal pressure drop) to validate this. I am trying to make the math easier...

This is actually irrelevant -What is important is that I am assuming "Constant Specific Heats" for air at room temperature. This is acceptable for the range of -20 to 70 Deg C with an error of less then 1/2 a percent.

edit:
Quote:
Originally posted by Since87:

(In terms of power dissipated due to the flow through it?)
This is a little vague...please take a look at my post when you get your computer running...and tell me what you are asking.
__________________
Jack of all Trades, Master of None.

Last edited by CoolROD; 08-20-2003 at 10:24 PM.
CoolROD is offline   Reply With Quote
Unread 08-19-2003, 07:16 AM   #25
CoolROD
Cooling Savant
 
CoolROD's Avatar
 
Join Date: Mar 2003
Location: North Carolina, USA
Posts: 225
Default

I might post in the "Water Cooling Simulator Discussion" when I get some more significant relations completed. This is toy stuff and probably the easiest model in thermodynamics (Constant Pressure, Ideal Gas, etc.) Some people here wanted to use it -so I put it here.

Now I have to figure out this "attachment thing" with a post...
__________________
Jack of all Trades, Master of None.
CoolROD is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 06:50 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
(C) 2005 ProCooling.com
If we in some way offend you, insult you or your people, screw your mom, beat up your dad, or poop on your porch... we're sorry... we were probably really drunk...
Oh and dont steal our content bitches! Don't give us a reason to pee in your open car window this summer...